Search found 603 matches

by marshman
Wed Mar 27, 2024 10:15 pm
Forum: Photovoltaic
Topic: Solis Cloud App - utter misery
Replies: 7
Views: 640

Re: Solis Cloud App - utter misery

Mine has been working fine, both Android app and on the web. I was "offered" an update but refused, "if it ain't broke don"t fix it"

Screenshot from today.


Image
by marshman
Thu Feb 15, 2024 8:39 pm
Forum: Energy storage, batteries, energy tariffs
Topic: Solax sk-su3000e - Pylontech us2000c Battery BMS and CT Clamps - start again
Replies: 8
Views: 727

Re: Solax sk-su3000e - Pylontech us2000c Battery BMS and CT Clamps - start again

Think you are on a hiding to nothing trying to get the Solax inverter to communicate with the Pylontech batteries. There are numerous pleas for help on t'interweb on other forums and there is a long thread on this forum - none have a conclusion. This is the thread on this forum: (worth a read as at ...
by marshman
Mon Feb 05, 2024 10:14 am
Forum: Energy storage, batteries, energy tariffs
Topic: Solax sk-su3000e - Pylontech us2000c Battery BMS and CT Clamps - start again
Replies: 8
Views: 727

Re: Solax sk-su3000e - Pylontech us2000c Battery BMS and CT Clamps - start again

As kommando says, seems like the BMS link is not working. Ideally this should use the CAN bus . Most common reason - assuming you have the correct battery selected on the inverter, is the cable is wrong. CAN bus only uses 2 wires - similar to RS485 - They need to be a "twisted pair". As fa...
by marshman
Thu Jan 25, 2024 8:43 pm
Forum: Photovoltaic
Topic: Solis Hybrid Inverter No Battery alarm
Replies: 10
Views: 1143

Re: Solis Hybrid Inverter No Battery alarm

Yes, setting the charge current on the time of use page only sets the charge current for those times you want it to charge. Force charging has its own setting for SOC to start and max grid power (i.e. charge current). I think you have been lucky the fuse survived this long. It probably has not gone ...
by marshman
Thu Jan 25, 2024 7:38 pm
Forum: Photovoltaic
Topic: Solis Hybrid Inverter No Battery alarm
Replies: 10
Views: 1143

Re: Solis Hybrid Inverter No Battery alarm

The fuse carries current both ways, charge and discharge. 50A is too small for a 3.6kW inverter. If the inverter is supplying a house load at its full capacity - 3.6kW then it will be drawing 70A from the battery and through the fuse, 1.5 times its rated current. The fuse will survive quite a long t...
by marshman
Wed Jan 24, 2024 4:24 pm
Forum: Energy storage, batteries, energy tariffs
Topic: Monitoring Battery Capacity
Replies: 10
Views: 911

Re: Monitoring Battery Capacity

151Ah @ a nominal 50V = 7550Wh or 7.55kWh

Only real way is to "coulomb count" or fully charge and then measure how much energy you can extract when discharging form full charge to your lower limit.
by marshman
Mon Jan 15, 2024 9:55 pm
Forum: Energy storage, batteries, energy tariffs
Topic: Solax sk-su3000e OFF MODE following install
Replies: 8
Views: 704

Re: Solax sk-su3000e OFF MODE following install

Just press and hold the "ENTER" button for 5 seconds to clear OFF MODE. It is mentioned in section 6.8 (page 30) of this manual.

https://www.solaxpower.com/uploads/file ... ual-en.pdf

Hope that helps.