Ground Mount cable run questions!

NikoV6
Posts: 218
Joined: Thu Aug 11, 2022 6:42 am

Re: Ground Mount cable run questions!

#21

Post by NikoV6 »

nowty wrote: Wed Aug 17, 2022 9:44 am
NikoV6 wrote: Wed Aug 17, 2022 6:07 am Thanks everybody for the replies, very helpful!

I should clarify, the AC from the inverter will be going to Tesla gateway.

Interesting about the voltage Nowty, my inverter has three inputs, I think I should reconfigure my panels for three string

https://www.segen.co.uk/product/solis-8 ... e-with-dc/

This is my wiring diagram, thoughts please

Image
Nice picture. :mrgreen:

Regarding the input for 3 strings, there are only two MPPTs, so if doing 3 strings, the two going into the larger MPPT should be identically sized. I note the installation manual does not specifically say this.

So the panel configuration would need to be something like 8 + 8 / 6 or 7 + 7 / 8 configuration.
Best PowerPoint skilzzz!!

Cheers, the question about the strings into the MPPT was on my list!

Do you know if the DNO will be OK with a CT restricting export of the solars?
14Kw Mitsubishi Ecodan ASHP
22 x JA Solar 455W Mono Perc Half Cell Silvers
Solis 8.0Kw 5G Dual MPPT Inverter
13.5Kw Tesla Powerwall
Zappi 2 Charger
iBoost
User avatar
Stinsy
Posts: 2861
Joined: Wed Jun 02, 2021 1:09 pm

Re: Ground Mount cable run questions!

#22

Post by Stinsy »

NikoV6 wrote: Wed Aug 17, 2022 10:59 am Do you know if the DNO will be OK with a CT restricting export of the solars?
They should be if your setup is G100 complaint.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
NikoV6
Posts: 218
Joined: Thu Aug 11, 2022 6:42 am

Re: Ground Mount cable run questions!

#23

Post by NikoV6 »

Stinsy wrote: Wed Aug 17, 2022 11:49 am
NikoV6 wrote: Wed Aug 17, 2022 10:59 am Do you know if the DNO will be OK with a CT restricting export of the solars?
They should be if your setup is G100 complaint.
The inverter has a failsafe function that can be turned on to stop generation and sound alarm if CT/meter connection is lost, specifically to comply with UK G100 regulations. I am hopeful the DNO will recognise this!
14Kw Mitsubishi Ecodan ASHP
22 x JA Solar 455W Mono Perc Half Cell Silvers
Solis 8.0Kw 5G Dual MPPT Inverter
13.5Kw Tesla Powerwall
Zappi 2 Charger
iBoost
User avatar
nowty
Posts: 5797
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Ground Mount cable run questions!

#24

Post by nowty »

Another thing I've noticed is that although the MPPT range is 90V to 520V (that's the working voltage Vmp range), its rated at 330V DC, so your better off doing it in 3 strings for max inverter efficiency and extended life of the inverter.

330V at Vmp is about 8 panels worth.
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
NikoV6
Posts: 218
Joined: Thu Aug 11, 2022 6:42 am

Re: Ground Mount cable run questions!

#25

Post by NikoV6 »

nowty wrote: Wed Aug 17, 2022 12:12 pm Another thing I've noticed is that although the MPPT range is 90V to 520V (that's the working voltage Vmp range), its rated at 330V DC, so your better off doing it in 3 strings for max inverter efficiency and extended life of the inverter.

330V at Vmp is about 8 panels worth.
7 + 7 and 8 it is then!
14Kw Mitsubishi Ecodan ASHP
22 x JA Solar 455W Mono Perc Half Cell Silvers
Solis 8.0Kw 5G Dual MPPT Inverter
13.5Kw Tesla Powerwall
Zappi 2 Charger
iBoost