Grounding ground mount panels

Post Reply
NikoV6
Posts: 218
Joined: Thu Aug 11, 2022 6:42 am

Grounding ground mount panels

#1

Post by NikoV6 »

I have mounted my panels on a timber framed steel clad "shed" . Do I need to ground the shed using an earth spike please. UK install

Thanks
14Kw Mitsubishi Ecodan ASHP
22 x JA Solar 455W Mono Perc Half Cell Silvers
Solis 8.0Kw 5G Dual MPPT Inverter
13.5Kw Tesla Powerwall
Zappi 2 Charger
iBoost
User avatar
Stinsy
Posts: 2861
Joined: Wed Jun 02, 2021 1:09 pm

Re: Grounding ground mount panels

#2

Post by Stinsy »

Opinions vary. There is no consensus, additionally the prevalence of RCDs has reduced earthing requirements in many situations. Some countries specifically require solar panel frames to be bonded to the property's main earth connection, the UK is not one of them.

You should exercise common sense. Current from the solar panels cannot flow to earth because the DC side is functionally isolated from Earth so there is no risk of electric shock between the DC side and Earth. The cladding would need to be earthed only if it is considered an "Exposed conductive part" (irrelevant of the solar system). Is there anywhere where single-insulated cables could come in contact with the cladding?
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
NikoV6
Posts: 218
Joined: Thu Aug 11, 2022 6:42 am

Re: Grounding ground mount panels

#3

Post by NikoV6 »

Stinsy wrote: Wed Sep 07, 2022 2:45 pm Opinions vary. There is no consensus, additionally the prevalence of RCDs has reduced earthing requirements in many situations. Some countries specifically require solar panel frames to be bonded to the property's main earth connection, the UK is not one of them.

You should exercise common sense. Current from the solar panels cannot flow to earth because the DC side is functionally isolated from Earth so there is no risk of electric shock between the DC side and Earth. The cladding would need to be earthed only if it is considered an "Exposed conductive part" (irrelevant of the solar system). Is there anywhere where single-insulated cables could come in contact with the cladding?
The DC cables run across the roof but I believe these are double insulated?

I am having 6mm armoured AC power run from the house, but this will be on its own RCD as a new circuit (lights and twin socket for the new shed)
14Kw Mitsubishi Ecodan ASHP
22 x JA Solar 455W Mono Perc Half Cell Silvers
Solis 8.0Kw 5G Dual MPPT Inverter
13.5Kw Tesla Powerwall
Zappi 2 Charger
iBoost
User avatar
Stinsy
Posts: 2861
Joined: Wed Jun 02, 2021 1:09 pm

Re: Grounding ground mount panels

#4

Post by Stinsy »

NikoV6 wrote: Wed Sep 07, 2022 3:35 pm
Stinsy wrote: Wed Sep 07, 2022 2:45 pm Opinions vary. There is no consensus, additionally the prevalence of RCDs has reduced earthing requirements in many situations. Some countries specifically require solar panel frames to be bonded to the property's main earth connection, the UK is not one of them.

You should exercise common sense. Current from the solar panels cannot flow to earth because the DC side is functionally isolated from Earth so there is no risk of electric shock between the DC side and Earth. The cladding would need to be earthed only if it is considered an "Exposed conductive part" (irrelevant of the solar system). Is there anywhere where single-insulated cables could come in contact with the cladding?
The DC cables run across the roof but I believe these are double insulated?

I am having 6mm armoured AC power run from the house, but this will be on its own RCD as a new circuit (lights and twin socket for the new shed)
You don't have to worry about the DC because it is functionally isolated from Earth.
So long as no single-isolated cables can com in contact with the cladding then you don't have to worry about the AC side either.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger