Spoke too soon!!

richbee
Posts: 604
Joined: Tue Apr 19, 2022 3:39 pm
Location: Northumberland

Re: Spoke too soon!!

#21

Post by richbee »

Somehow the inverter has to detect the balance between PV, battery, load and grid incoming/export, to decide when to drain the battery.
The only thing the CT clamp can detect is the flow in or out from the grid.

If I've understood correctly, If the load is 1kW, and the PV produces 1kW, the CT should detect 0.
So how does the inverter know what the load is? I assume it does a sum - CT = 0, PV = 1kW, Battery = 0 in/out, therefore load must be 1kW to complete the sum.
Solar PV since July '22:
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W
User avatar
nowty
Posts: 5797
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Spoke too soon!!

#22

Post by nowty »

richbee wrote: Fri Jul 29, 2022 10:30 am Somehow the inverter has to detect the balance between PV, battery, load and grid incoming/export, to decide when to drain the battery.
The only thing the CT clamp can detect is the flow in or out from the grid.

If I've understood correctly, If the load is 1kW, and the PV produces 1kW, the CT should detect 0.
So how does the inverter know what the load is? I assume it does a sum - CT = 0, PV = 1kW, Battery = 0 in/out, therefore load must be 1kW to complete the sum.
Yes that’s how it works.
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
richbee
Posts: 604
Joined: Tue Apr 19, 2022 3:39 pm
Location: Northumberland

Re: Spoke too soon!!

#23

Post by richbee »

After some weeks waiting for the installers to contact sunsynk technical, they asked to check the ct connection at the inverter end. Installer still didn't understand and asked me for another photo of the ct clamp!
I took the front off the inverter and sent them a photo - looks like the ct was connected to the wrong pins!
Well done to those who correctly predicted a ct issue😁
Now waitibg for them to arrange to come out & put it right.
I'm sure I could do it, but I'd rather they did it from a warranty point of view - although with their record so far maybe not😜
Also had a smart meter fitted today, so we can now get paid for our surplus - once the installers sort out the DNO application (not holding breath)
Solar PV since July '22:
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W
richbee
Posts: 604
Joined: Tue Apr 19, 2022 3:39 pm
Location: Northumberland

Re: Spoke too soon!!

#24

Post by richbee »

Resurrecting this fossilised thread to report that the inverter CT connection has finally been sorted out....by me.
After 3 further cancellations of their electrician coming out to sort it - I finally lost my patience with them and did it myself - dead easy job in 5 minutes, with everything turned off and isolated.
Now seems to be working properly - only 2 months since the install - 3.5 months since they were supposed to do the install - safe to say I won't be recommending the company - they still haven't managed to fix the broken roof slates or gutter clip - or take away their left over rubbish in the garden - if anyone wants any rails or mounting brackets.......
Solar PV since July '22:
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W
pudding
Posts: 98
Joined: Sat Mar 26, 2022 7:01 pm
Location: Cornwall

Re: Spoke too soon!!

#25

Post by pudding »

Glad you got it all sorted! I completely forgot about this thread unfortunately. I had my Sunsynk inverter installed in mid-August, and I was there helping the guys who hadn't installed one before so I was able to set it all up and help. I fitted the CT CAT 6 extension cable to the inverter, and the pins from the manual were the wrong ones, and I had to change from 3/4 to 5/6 or vice versa, which I luckily remembered reading about somewhere. I'm guessing that's what you needed to do? Seems there are a few different models with a slightly different circuit board for this connection, but the manuals are all the same!
4kW array w/Fronius | 3.51kW & 3.28kW arrays w/Sunsynk 3.6kW hybrid | 6 x Pylon US3000C
8kW GSHP/MVHR/5kW A2A HP/ Ripple- KH & DW & P4 on the way :D
richbee
Posts: 604
Joined: Tue Apr 19, 2022 3:39 pm
Location: Northumberland

Re: Spoke too soon!!

#26

Post by richbee »

pudding wrote: Tue Sep 20, 2022 2:29 pm Glad you got it all sorted! I completely forgot about this thread unfortunately. I had my Sunsynk inverter installed in mid-August, and I was there helping the guys who hadn't installed one before so I was able to set it all up and help. I fitted the CT CAT 6 extension cable to the inverter, and the pins from the manual were the wrong ones, and I had to change from 3/4 to 5/6 or vice versa, which I luckily remembered reading about somewhere. I'm guessing that's what you needed to do? Seems there are a few different models with a slightly different circuit board for this connection, but the manuals are all the same!
Yes, exactly - swap from 5&6 to 3&4 - manual says 5&6 but the circuit board says 3&4. All works beautifully now it's connected correctly :D
Solar PV since July '22:
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W