Comparing solar immersion heater diverters (water heating).
Re: Comparing solar immersion heater diverters (water heating).
Don't know enough about how they all work to comment on why, but I did have "conflict" issues between a solic and an iboost. In theory the 200W export threshold of the iboost (older version) should give priority to the zero export solic. And it did, most if the time but occasionally got the wrong way round. However, putting more distance between the CTs seems to have stabilised them.
Another thing ice remembered; you can extend the wire of an iboost (and maybe others?) by about 20-30m. Much longer than this and nothing happens. Add on a similar range for the wireless part and you've a very useful ~50m+ range. Although chews through the batteries a bit and not as reliable as one where wireless unit is right next to the iboost.
Another thing ice remembered; you can extend the wire of an iboost (and maybe others?) by about 20-30m. Much longer than this and nothing happens. Add on a similar range for the wireless part and you've a very useful ~50m+ range. Although chews through the batteries a bit and not as reliable as one where wireless unit is right next to the iboost.
-
- Posts: 1873
- Joined: Thu Sep 09, 2021 3:42 pm
- Location: North East Dorset
Re: Comparing solar immersion heater diverters (water heating).
But surely, "before", in terms of any spacial position on the same cable, makes zero practical difference, because distance is always proportional to time on any cable (due to the cable velocity factor) for any step function and that cable time difference is so minute as to make zero practical difference, because it's completely swamped by massively larger response time delays in the devices.
I still maintain that the (very real) race condition that determines which device takes priority has nothing at all to do with where along a cable run a measurement happens, and is solely down to how fast each device responds to the change.
I still maintain that the (very real) race condition that determines which device takes priority has nothing at all to do with where along a cable run a measurement happens, and is solely down to how fast each device responds to the change.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
Re: Comparing solar immersion heater diverters (water heating).
I agree that the position up/downstream can't make a difference. But apparently, they can be too close to one another.Oldgreybeard wrote: ↑Wed Nov 23, 2022 6:13 pm But surely, "before", in terms of any spacial position on the same cable, makes zero practical difference, because distance is always proportional to time on any cable (due to the cable velocity factor) for any step function and that cable time difference is so minute as to make zero practical difference, because it's completely swamped by massively larger response time delays in the devices.
I still maintain that the (very real) race condition that determines which device takes priority has nothing at all to do with where along a cable run a measurement happens, and is solely down to how fast each device responds to the change.
-
- Posts: 1873
- Joined: Thu Sep 09, 2021 3:42 pm
- Location: North East Dorset
Re: Comparing solar immersion heater diverters (water heating).
They can, as the magnetic field leakage from one can mutually interfere with another ones that is very close to it, I believe. IIRC, there's a recommendation I read somewhere that says they need to be at least something like 20mm apart, to reduce the risk of this.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
Re: Comparing solar immersion heater diverters (water heating).
But they are not on the same cable. It's a question of whether the topology isOldgreybeard wrote: ↑Wed Nov 23, 2022 6:13 pm But surely, "before", in terms of any spacial position on the same cable, makes zero practical difference, because distance is always proportional to time on any cable (due to the cable velocity factor) for any step function and that cable time difference is so minute as to make zero practical difference, because it's completely swamped by massively larger response time delays in the devices.
I still maintain that the (very real) race condition that determines which device takes priority has nothing at all to do with where along a cable run a measurement happens, and is solely down to how fast each device responds to the change.
A) (my arrangement - battery priority): Grid - Diverter CT - [AC-In -Victron ESS- AC-Out] - tee off to PV inverter - CU - Diverter - Immersion circuit
or B) (hot water priority): Grid - [AC-In -Victron ESS- AC-Out] - Diverter CT - tee off to PV inverter - CU - Diverter - Immersion circuit
These configurations are deterministic, that is they do not rely on propagation delays/race timings to work correctly, they depend only on which current flow the diverter views as being "surplus".
16 x 230W Upsolar panels S Devon, 4kW Steca, 3.9 MWh FITs/yr
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP
Re: Comparing solar immersion heater diverters (water heating).
I self installed an Eddi just over a year ago together with a Harvi and hub. After a couple of hours getting my head round where to place the CTs and which settings to use I got it working and talking to the app. Since then its worked without any problems at all. I had an Zappi fitted in June and I got that to integrate with the eddi and app too. In the 12 months to 31st Oct I generated 2384 kwhs, and my export total was only 77kwhs.
I paid £566 for the Eddi, hub, and harvi.
I have a 3kwp pv system.
In the first 12 months of use I diverted a total of 661.3kwhs into my immersion tanks (I have two of them). At 33p a unit that's a saving of £218, so in another 18 months it will have paid for itself. I'm well happy with that.
The units look solid, and well made. The myenergi forum seems busy with lots of helpful types on there. I'm confident if I neede tech support I'd be able to get it from there.
I'd recommend them.
I paid £566 for the Eddi, hub, and harvi.
I have a 3kwp pv system.
In the first 12 months of use I diverted a total of 661.3kwhs into my immersion tanks (I have two of them). At 33p a unit that's a saving of £218, so in another 18 months it will have paid for itself. I'm well happy with that.
The units look solid, and well made. The myenergi forum seems busy with lots of helpful types on there. I'm confident if I neede tech support I'd be able to get it from there.
I'd recommend them.
11.205kW (2023) PV + 3kW (2013 FIT) PV
12.4kwH Solax Battery
Eddi diverter to 2 HW cylinders
Zappi EV charger
MG4 64kw EV
Rainwater harvesting
Part Sedum roof
12.4kwH Solax Battery
Eddi diverter to 2 HW cylinders
Zappi EV charger
MG4 64kw EV
Rainwater harvesting
Part Sedum roof
Re: Comparing solar immersion heater diverters (water heating).
@Woodyeyes, (and others if its not in your sig) how big (in litres) are your two water tanks ?
And what EV have you got or what is the battery size ?
PM me if you like.
And what EV have you got or what is the battery size ?
PM me if you like.
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Re: Comparing solar immersion heater diverters (water heating).
145L each tank.
I ordered a mg ZS LR EV on 6th Dec 2021 as a lease deal with Vanarama. I’m still waiting! Latest estimated delivery date they gave me is April 2023.
Last month I popped into my local mg dealer and ordered a mg 4 instead. They quoted 8-16 weeks. I’m buying the mg4.
We’ll see which one turns up first and cancel the one that doesn’t.
The mg4 has a 64kw battery.
I ordered a mg ZS LR EV on 6th Dec 2021 as a lease deal with Vanarama. I’m still waiting! Latest estimated delivery date they gave me is April 2023.
Last month I popped into my local mg dealer and ordered a mg 4 instead. They quoted 8-16 weeks. I’m buying the mg4.
We’ll see which one turns up first and cancel the one that doesn’t.
The mg4 has a 64kw battery.
11.205kW (2023) PV + 3kW (2013 FIT) PV
12.4kwH Solax Battery
Eddi diverter to 2 HW cylinders
Zappi EV charger
MG4 64kw EV
Rainwater harvesting
Part Sedum roof
12.4kwH Solax Battery
Eddi diverter to 2 HW cylinders
Zappi EV charger
MG4 64kw EV
Rainwater harvesting
Part Sedum roof
Re: Comparing solar immersion heater diverters (water heating).
If its ordered its going on the secret list.Woodyeyes wrote: ↑Tue Nov 29, 2022 1:03 am 145L each tank.
I ordered a mg ZS LR EV on 6th Dec 2021 as a lease deal with Vanarama. I’m still waiting! Latest estimated delivery date they gave me is April 2023.
Last month I popped into my local mg dealer and ordered a mg 4 instead. They quoted 8-16 weeks. I’m buying the mg4.
We’ll see which one turns up first and cancel the one that doesn’t.
The mg4 has a 64kw battery.
https://camelot-forum.co.uk/phpBB3/view ... 120#p22664
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Re: Comparing solar immersion heater diverters (water heating).
I have a Solar Immersion to divert PV export to my 170ltr Megaflo.
Performed faultlessly since a DIY install in 2013.
I am currently boosting it during the Octopus Go 4 hr window as solar is not sufficient in winter and I reckon electricity at 7.5p is better than gas at @ 10p per kWh.
Performed faultlessly since a DIY install in 2013.
I am currently boosting it during the Octopus Go 4 hr window as solar is not sufficient in winter and I reckon electricity at 7.5p is better than gas at @ 10p per kWh.