Experimental PV calculator

sharpener
Posts: 430
Joined: Fri May 20, 2022 10:42 am

Re: Experimental PV calculator

#11

Post by sharpener »

richbee wrote: Thu May 11, 2023 9:23 am My feeling is about the same, based on 6 months of having only 1x 5kWh battery with Solar PV. There is a lot of time where the battery is full and exporting, but then the battery is empty the following morning. Also the discharge rate of 2.5kW is not enough to run things like a kettle fully.

I have now fitted a 2nd 5kWh battery and it seems to have made a huge difference - in May so far I have inly imported <10kWh and usage is well over 90%, even though we have had less PV generation on average compared to April.
FWIW our experience is much the same. Originally fitted 7.1 kW, charging this from PV was fine but not leaving enough for the immersion diverter. Also not enough storage to run the electric cooker at breakfast time without cheap rate top-up.

So added nearly as much PV again, also added third battery module to make the figures below. Would agree this is a sweet spot; is enough to keep the lights on all evening in winter with a bit to spare and in summer to survive on PV alone. Won't increase capacity any further, heat pump will have to fend for itself, though I am contemplating 200 litre thermal store to charge up from E7 before the heat demand begins in the morning. Subjec to what I can get an installer to agree to, may have to DIY or retrofit.
16 x 230W Upsolar panels S Devon, 4kW Steca, 3.9 MWh FITs/yr
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP
LesNewell
Posts: 8
Joined: Wed May 10, 2023 6:48 pm

Re: Experimental PV calculator

#12

Post by LesNewell »

sharpener wrote: Sun May 14, 2023 7:30 pm Won't increase capacity any further, heat pump will have to fend for itself, though I am contemplating 200 litre thermal store to charge up from E7 before the heat demand begins in the morning.
Would you be better off charging the battery a bit from E7 then using that to run the heat pump instead of adding a thermal store? That's assuming you are running an air to water heat pump.
Just out of interest, what sort of export tariff are you on?
sharpener
Posts: 430
Joined: Fri May 20, 2022 10:42 am

Re: Experimental PV calculator

#13

Post by sharpener »

LesNewell wrote: Sun May 14, 2023 8:07 pm
sharpener wrote: Sun May 14, 2023 7:30 pm Won't increase capacity any further, heat pump will have to fend for itself, though I am contemplating 200 litre thermal store to charge up from E7 before the heat demand begins in the morning.
Would you be better off charging the battery a bit from E7 then using that to run the heat pump instead of adding a thermal store? That's assuming you are running an air to water heat pump.
Will do both if I can. If I need a buffer tank anyway then marginal cost/kWh of increasing it to 200 l is quite small, also there is a physical limitation on height of battery stack where it is atm.
LesNewell wrote: Sun May 14, 2023 8:07 pmJust out of interest, what sort of export tariff are you on?
Original FIT dating from Dec 2011 just before it was cut. CBA to sort out separate SEG for 2022 panels, metering difficult as they are on DC side, and would need a smart meter in addition which SP say cannot be made to work in our location.
16 x 230W Upsolar panels S Devon, 4kW Steca, 3.9 MWh FITs/yr
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP
openspaceman
Posts: 662
Joined: Mon Mar 21, 2022 7:37 pm

Re: Experimental PV calculator

#14

Post by openspaceman »

sharpener wrote: Sun May 14, 2023 10:14 pm
Original FIT dating from Dec 2011 just before it was cut. CBA to sort out separate SEG for 2022 panels, metering difficult as they are on DC side, and would need a smart meter in addition which SP say cannot be made to work in our location.
Same here but I am just considering getting off the deemed export register and moving to Octopus for a higher SEG, has anyone here successfully managed this without compromising the original FIT? How difficult was it?
Morso S11
FIT
16 Sharp PV panels facing WSW 4kW
Solarmax 4200S inverter
Non FIT
3 Canadian solar DC coupled 1.75kW facing SSE
Storage
Growatt SPA3000TL BL inverter ac coupled
Growatt GBLI6532 6.5kWh lithium phosphate battery
User avatar
Fintray
Posts: 1558
Joined: Mon May 31, 2021 6:37 pm
Location: Aberdeenshire

Re: Experimental PV calculator

#15

Post by Fintray »

openspaceman wrote: Wed May 17, 2023 2:31 pm
sharpener wrote: Sun May 14, 2023 10:14 pm
Original FIT dating from Dec 2011 just before it was cut. CBA to sort out separate SEG for 2022 panels, metering difficult as they are on DC side, and would need a smart meter in addition which SP say cannot be made to work in our location.
Same here but I am just considering getting off the deemed export register and moving to Octopus for a higher SEG, has anyone here successfully managed this without compromising the original FIT? How difficult was it?
I was already an Octopus customer but my FIT was with SSE, I contacted Octopus to get my export swapped over to them (FIT payments are still with SSE now OVO) to get the better SEG payments and it was very quick and simple.
3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
sharpener
Posts: 430
Joined: Fri May 20, 2022 10:42 am

Re: Experimental PV calculator

#16

Post by sharpener »

Fintray wrote: Wed May 17, 2023 2:38 pm
openspaceman wrote: Wed May 17, 2023 2:31 pm
sharpener wrote: Sun May 14, 2023 10:14 pm
Original FIT dating from Dec 2011 just before it was cut. CBA to sort out separate SEG for 2022 panels, metering difficult as they are on DC side, and would need a smart meter in addition which SP say cannot be made to work in our location.
Same here but I am just considering getting off the deemed export register and moving to Octopus for a higher SEG, has anyone here successfully managed this without compromising the original FIT? How difficult was it?
I was already an Octopus customer but my FIT was with SSE, I contacted Octopus to get my export swapped over to them (FIT payments are still with SSE now OVO) to get the better SEG payments and it was very quick and simple.
How is your metering arranged? If you have a FIT meter does that power also get counted by the smart meter and then have to be subtracted again, as I posted here https://camelot-forum.co.uk/phpBB3/view ... 757#p32757. [Mods please delete one if you wish.]
Last edited by sharpener on Wed May 17, 2023 5:07 pm, edited 1 time in total.
16 x 230W Upsolar panels S Devon, 4kW Steca, 3.9 MWh FITs/yr
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP
User avatar
Fintray
Posts: 1558
Joined: Mon May 31, 2021 6:37 pm
Location: Aberdeenshire

Re: Experimental PV calculator

#17

Post by Fintray »

The power from both my systems goes through the smart meter and all export (and import) is currently on the Flux tariff, there is no deduction of the readings from the FIT's generation meter.
3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
sharpener
Posts: 430
Joined: Fri May 20, 2022 10:42 am

Re: Experimental PV calculator

#18

Post by sharpener »

Fintray wrote: Wed May 17, 2023 3:38 pm The power from both my systems goes through the smart meter and all export (and import) is currently on the Flux tariff, there is no deduction of the readings from the FIT's generation meter.
Thanks. So you now get SEG payments from Octopus for all exports, and FIT generation payments - but not export payments - from Ovo/SSE for the original FIT system, is that how it works?

How do they know you are no longer entitled to the export portion, deemed or otherwise?

What I was told about difficulty in metering the export from DC-connected generation appears to have been wrong then.
16 x 230W Upsolar panels S Devon, 4kW Steca, 3.9 MWh FITs/yr
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP
openspaceman
Posts: 662
Joined: Mon Mar 21, 2022 7:37 pm

Re: Experimental PV calculator

#19

Post by openspaceman »

Fintray wrote: Wed May 17, 2023 3:38 pm The power from both my systems goes through the smart meter and all export (and import) is currently on the Flux tariff, there is no deduction of the readings from the FIT's generation meter.

Presumably 3p gets deducted from the 50% that would have been deemed export?
Morso S11
FIT
16 Sharp PV panels facing WSW 4kW
Solarmax 4200S inverter
Non FIT
3 Canadian solar DC coupled 1.75kW facing SSE
Storage
Growatt SPA3000TL BL inverter ac coupled
Growatt GBLI6532 6.5kWh lithium phosphate battery
User avatar
Fintray
Posts: 1558
Joined: Mon May 31, 2021 6:37 pm
Location: Aberdeenshire

Re: Experimental PV calculator

#20

Post by Fintray »

sharpener wrote: Wed May 17, 2023 5:17 pm
Fintray wrote: Wed May 17, 2023 3:38 pm The power from both my systems goes through the smart meter and all export (and import) is currently on the Flux tariff, there is no deduction of the readings from the FIT's generation meter.
1. Thanks. So you now get SEG payments from Octopus for all exports, and FIT generation payments - but not export payments - from Ovo/SSE for the original FIT system, is that how it works?

2. How do they know you are no longer entitled to the export portion, deemed or otherwise?

3. What I was told about difficulty in metering the export from DC-connected generation appears to have been wrong then.
1. Yes, that is correct.
2. Octopus contacted SSE and told them I was moving my export to them.
3. Both my systems are AC connected, so I don't know about how DC generation would be counted.