Swap Sofar charger for Sofar hybrid inverter to add more

Post Reply
JC_UK
Posts: 46
Joined: Fri Feb 11, 2022 4:28 pm

Swap Sofar charger for Sofar hybrid inverter to add more

#1

Post by JC_UK »

Hi,

We have a SMA inverter with 16 panels connected and on FIT.
We have added a Sofar ME3000SP charger and pylontech batteries.

The DNO say we can add another 3kw of generation to the system.

I am thinking of a swapping the 3KW Sofar charger for a 6kw Sofar Hybrid inverter and connect the battery storage to the hybrid inverter.
This will allow a further 6kw of generation, over the 3kw that the DNO will allow with the sofar charger in the system.

Does anyone know if the Sofar Hybrid inverter will direct all surplus power to the connected batteries or only surplus power from the connected solar panels?

Many thanks
JC

16x 245W Pan Solar panels - 3.92kW - 2015
SMA SB 3600TL-21 inverter - 2015
Solar iBoost+ Controller - 2015
9x 2.4kWh Pylontech batts 21.6 kWh - 2022/24
Solax X1 SK_SU3000 Hybrid inverter - 2024

TBD
12x 260W REC Solar panels 3.12kW
1GB B4RN Internet
Tinbum
Posts: 1117
Joined: Mon May 31, 2021 9:55 pm

Re: Swap Sofar charger for Sofar hybrid inverter to add more

#2

Post by Tinbum »

Not sure but if it doesn't you can always leave the ME3000 in as well but that would require some thinking about 2 chargers on 1 pack.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
User avatar
nowty
Posts: 5787
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Swap Sofar charger for Sofar hybrid inverter to add more

#3

Post by nowty »

I have a ME3000SP in my system which I have used as a dumb battery charger in timed mode, in winter, set at an extra 50A of battery charging on top of the 120A I get from my SMA sunny Island battery inverter. I do however, have a battery bank size, cables, fuses and isolators capable of such power and it is set to charge to a lower voltage so it drops out at around 70% SOC. :mrgreen:

I love copper and bolt down fuses. 8-)
Image

On the Octopus Intelligent tariff I get 6 hours of off peak charging so I don't actually need or use the ME3000SP anymore. But if I had to go back to Octopus Go on a 4 hour slot, then I need the extra charging power for the shorter slot time. :twisted:
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Ken
Posts: 511
Joined: Mon Jul 26, 2021 10:07 am

Re: Swap Sofar charger for Sofar hybrid inverter to add more

#4

Post by Ken »

So you are thinking to feed the new panels to the hybrid inverter and then to the batts. If you remove the Sofar charger where/how would you connect the SMA inverter output to the batts ? The hybrid inverter is fed with DC current and you cannot attach the output of the SMA which is AC directly to the batts without a charger.

So the question is can one have 2 chargers supplying one batt bank. I dont know but it seems doubtful ??
User avatar
nowty
Posts: 5787
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Swap Sofar charger for Sofar hybrid inverter to add more

#5

Post by nowty »

Ken wrote: Wed Sep 28, 2022 9:31 am So the question is can one have 2 chargers supplying one batt bank. I dont know but it seems doubtful ??
Yes you can but the stats on the inverter(s) will be all over the place and at least one will have to run in dumb mode (no BMS connection) unless you utilise some fancy comms.

Its quite common use a DC charge controller to connect a second charging source to a battery stack, but less so using a second grid tie battery inverter unless they are set up as a master / slave configuration with comms between the two.

As Tinbum has pointed out, you have to know what you are doing and be careful not to exceed charge and voltage limits of your system, like batteries, cables and isolators.
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Tinbum
Posts: 1117
Joined: Mon May 31, 2021 9:55 pm

Re: Swap Sofar charger for Sofar hybrid inverter to add more

#6

Post by Tinbum »

Ken wrote: Wed Sep 28, 2022 9:31 am So the question is can one have 2 chargers supplying one batt bank. I dont know but it seems doubtful ??
Yes you can. Some inverters are designed for it and have a communication cable between them to control the charging / discharge. My 3 SMA sunny islands are linked like this.

You can just use a junction box on the CAN cable so it has 3 plugs, turn off the CAN resistor in the Pylon Battery DIP switch settings and that should work but current (A) settings will be incorrect. If you have a really large battery pack it probably wouldn't be a problem but certainly not recommended for small packs. Say you had 3 x US3000c the max current that can accept is 111A (37A x 3), now if your inverters were 3KW each they could push out 120A (60A x 2). I know people will say that, for example, the current will taper off anyway, but that's only when nearing fully charged. I work on the principle that the battery pack manufactures put a max charge current in for a reason, and im sure they could see if you had exceeded it if it came to a warranty claim.

I have a very large pack but I still alter the CAN settings so I can't possibly overcharge. The SMA inverters are really good in that they report, over CAN, the current they put out, my Eltek chargers do the same but the Sofar inverters don't so I also have to use RS485 communication with them to get that data. (Sofar do actually transmit on the CAN id but they populate it with 0x00 's and despite asking they won't add the data even though I'm certain it would only require a slight firmware update).
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW