Can you boil a kettle direct from a PV panel.

Posted: Mon Nov 21, 2022 7:22 pm
by nowty
This is a resurrection of a lost experiment from the old place. There was talk many times in the past of directly connecting solar panels to an immersion heater or storage heater without any use of inverters. There were arguments for and against it and some didn’t think it would work at all.

The biggest issue of using DC direct from panels is the acing and welding together of thermostats and switches. But irrespective of that a few summers ago I had a go at connecting two solar panels directly to a kettle to see if it would boil.

I cut the plug off a socket extension lead and connected the live and neutral to a pair of MC4 solar connectors so I could directly connect to a pair of solar panels.

The pair of solar panels were 325W Panasonic with a Vmp of 59V and Imp of 5.5A. So a pair of them in series would give 118V with a current of 5.5A in full summer sun.
Image


Without using an MPPT, the trick is to find a resistive load to best match the generating panels of 118V at 5.5A. Using Ohms law the resistance required to match the pair my panels was a resistance of 21.5 ohms. If I used NOCT parameters for the panels (more typical) the resistance works out at a little higher at 25 ohms.

My 220V 1.85kW kettle has a resistance of 26.1 ohms so should be a good candidate for the experiment. One problem is that the on/off switch of the kettle electrically latches on which would not work with DC so I had to tape the switch down.

My health and safety manager gave it a final check and made a comment that I had cut the earth wire off the extension lead, but I ignored that.
Image


On load voltage was nearly 116V.
Image


Onload current was 4.9A.
Image


1 litre of water was boiling away nicely in 15 minutes.
Image

Re: Can you boil a kettle direct from a PV panel.

Posted: Mon Nov 21, 2022 7:45 pm
by Stinsy
Would 4x panels have worked better? 230V 5.5A?

What about 8x panels in a 4s2p arrangement? 230V 11A?

Re: Can you boil a kettle direct from a PV panel.

Posted: Mon Nov 21, 2022 7:56 pm
by nowty
Stinsy wrote: Mon Nov 21, 2022 7:45 pm Would 4x panels have worked better? 230V 5.5A?

What about 8x panels in a 4s2p arrangement? 230V 11A?
For 4 panels in series, the resistance would need to be around 40 ohms for max power transfer. The kettle would boil faster but less than twice the speed. The on load voltage would be lower than 230V and the current higher than 5.5A.

The 8 panels arrangement of in a 4s2P would be a good match and boil at a similar speed to plugging it into the mains.

Re: Can you boil a kettle direct from a PV panel.

Posted: Mon Nov 21, 2022 9:07 pm
by Mr Gus
Faster than Ivan's Toob solar curry.