SMA SunnyBoy 3.0 and SOFAR ME3000SP
Posted: Mon Nov 28, 2022 12:22 pm
Hi again,
I already have a SOFAR ME3000SP and batteries, and a SMA Sunnyboy 3600TL21 and 16 solar panels.
The SOFAR ME3000SP CT clamps monitor the solar generation from the solar installation and grid import export etc.
The CT Clamp is around the +ve cable from the Sunnyboy 3600TL21 to the CU.
I now want to add a SMA SunnyBoy 3.0 to my home installation.
I have 12 Solar panels each rated @ 260w == 3120w – max rating.
I would like to connect the panels as a set/string of 4 facing approx. East (approx. 1040w) and a set/string of 8 facing approx. South (approx. 2080w).
The 4 panels east facing will be the first to be commissioned, followed by the South facings ones a few weeks/months later.
Anyone know if the Sunnyboy 3.0 can connect to the new solar panels as described above please?
Also any best practice for connecting the panels in such configurations please?
I assume the panels will be connected in series and the +ve and -ve MC4s will then connect to the A and B connections on the inverter.
Also to include the new generation from the new Sunnyboy I assume I will need to add the +ve cable from the Sunnyboy 3600TL21 to the CU in the CT Clamp for the SOFAR ME3000SP..... so both +ve cables from the 2 Sunnyboy inverters will be monitored by the SOFAR ME3000SP via the same CT clamp.
Many thanks
JC
I already have a SOFAR ME3000SP and batteries, and a SMA Sunnyboy 3600TL21 and 16 solar panels.
The SOFAR ME3000SP CT clamps monitor the solar generation from the solar installation and grid import export etc.
The CT Clamp is around the +ve cable from the Sunnyboy 3600TL21 to the CU.
I now want to add a SMA SunnyBoy 3.0 to my home installation.
I have 12 Solar panels each rated @ 260w == 3120w – max rating.
I would like to connect the panels as a set/string of 4 facing approx. East (approx. 1040w) and a set/string of 8 facing approx. South (approx. 2080w).
The 4 panels east facing will be the first to be commissioned, followed by the South facings ones a few weeks/months later.
Anyone know if the Sunnyboy 3.0 can connect to the new solar panels as described above please?
Also any best practice for connecting the panels in such configurations please?
I assume the panels will be connected in series and the +ve and -ve MC4s will then connect to the A and B connections on the inverter.
Also to include the new generation from the new Sunnyboy I assume I will need to add the +ve cable from the Sunnyboy 3600TL21 to the CU in the CT Clamp for the SOFAR ME3000SP..... so both +ve cables from the 2 Sunnyboy inverters will be monitored by the SOFAR ME3000SP via the same CT clamp.
Many thanks
JC