two strings on same MPPTs, are they connected?

Post Reply
Gareth J
Posts: 173
Joined: Sun Oct 24, 2021 9:11 am

two strings on same MPPTs, are they connected?

#1

Post by Gareth J »

Am looking at buying a Solis 8kw single phase inverter but am wondering about the DC side of things. It's odd, as it has two MPPTs, one with one string at 12.5A and one with two strings at 25A total.

I want to simplify the wiring, particularly as I already have the right wire to do so and, if possible, run just two pairs of cables. There is no issue with shading.

So, will the strings on the dual stringed MPPT be connected inside the inverter you think? So I can effectively run the two strings down one pair of cables?

Not sure if there are terms I can search for that I'm missing.
MoSTiE
Posts: 71
Joined: Thu Sep 30, 2021 5:08 pm

Re: two strings on same MPPTs, are they connected?

#2

Post by MoSTiE »

i've just looked a 2 Solis 8K data sheets and they are both different, this one is probably your best bet :?: :?

https://www.itstechnologies.shop/produc ... r-inverter
User avatar
Stinsy
Posts: 2849
Joined: Wed Jun 02, 2021 1:09 pm

Re: two strings on same MPPTs, are they connected?

#3

Post by Stinsy »

Gareth J wrote: Tue Apr 18, 2023 10:08 pm Am looking at buying a Solis 8kw single phase inverter but am wondering about the DC side of things. It's odd, as it has two MPPTs, one with one string at 12.5A and one with two strings at 25A total.

I want to simplify the wiring, particularly as I already have the right wire to do so and, if possible, run just two pairs of cables. There is no issue with shading.

So, will the strings on the dual stringed MPPT be connected inside the inverter you think? So I can effectively run the two strings down one pair of cables?

Not sure if there are terms I can search for that I'm missing.
What panels are you installing and how many?
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Gareth J
Posts: 173
Joined: Sun Oct 24, 2021 9:11 am

Re: two strings on same MPPTs, are they connected?

#4

Post by Gareth J »

24x 415W Suntechs
Tinbum
Posts: 1118
Joined: Mon May 31, 2021 9:55 pm

Re: two strings on same MPPTs, are they connected?

#5

Post by Tinbum »

More importantly what are the voltages on the two strings?
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Gareth J
Posts: 173
Joined: Sun Oct 24, 2021 9:11 am

Re: two strings on same MPPTs, are they connected?

#6

Post by Gareth J »

Tinbum wrote: Wed Apr 19, 2023 10:16 am More importantly what are the voltages on the two strings?
Of course!

That will explain. I'm out at the minute but will check later. It's almost certainly going to be expecting separate strings of ~ 3300Wp. But whether or not the twin string MPPT can be fed with one string of ~6600Wp or can be connected in series, to split the load is I guess a question for solid. Would much prefer a simple one string per MPPT machine but finding one that's G100 at ~8kw is proving tricky.
User avatar
Stinsy
Posts: 2849
Joined: Wed Jun 02, 2021 1:09 pm

Re: two strings on same MPPTs, are they connected?

#7

Post by Stinsy »

Gareth J wrote: Wed Apr 19, 2023 6:46 am 24x 415W Suntechs
So Voc = 38.33V and Imp = 13.06A

If you put them all into a single string then you'd have a string voltage (Voc) of 919.92V and current (Imp) of 13.06A, the Voltage is in excess of the inverter's 600V max and you will definitely let the smoke out if you do that.

If you parallel up 2x strings of 12 panels you'd have a string voltage (Voc) of 459.96V and a string current (Imp) of 26.12A. This is what I'd recommend you do. Hook them up to the "25A" MPPT, don't worry about the current of the panels being higher than the inverter rating, it is a bit like plugging a 3A lamp into a 13A socket, you'll lose a smidge off the top in ideal conditions but only a teeny bit and ideal conditions don't occur very often.

You can leave the "12.5A" MPPT for future expansion.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Gareth J
Posts: 173
Joined: Sun Oct 24, 2021 9:11 am

Re: two strings on same MPPTs, are they connected?

#8

Post by Gareth J »

Stinsy wrote: Wed Apr 19, 2023 11:38 am
Gareth J wrote: Wed Apr 19, 2023 6:46 am 24x 415W Suntechs
So Voc = 38.33V and Imp = 13.06A

If you put them all into a single string then you'd have a string voltage (Voc) of 919.92V and current (Imp) of 13.06A, the Voltage is in excess of the inverter's 600V max and you will definitely let the smoke out if you do that.

If you parallel up 2x strings of 12 panels you'd have a string voltage (Voc) of 459.96V and a string current (Imp) of 26.12A. This is what I'd recommend you do. Hook them up to the "25A" MPPT, don't worry about the current of the panels being higher than the inverter rating, it is a bit like plugging a 3A lamp into a 13A socket, you'll lose a smidge off the top in ideal conditions but only a teeny bit and ideal conditions don't occur very often.

You can leave the "12.5A" MPPT for future expansion.
That's interesting. And better than than my idea, which was;
To split the 24 panels into 3x8 panel strings.
Give 12.5A MPPT one string.
Combine the other two strings at the roof (In series I guess - I imagine paralleling might to horrible things if there is a potential difference between "equal" strings)
Feed the 25A side with either just the one, combined string (which is, as you point out over voltage anyway) or series the two inputs so the voltage of the combined string is shared between the two inputs. But who knows if the inverter will like that.