Armoured cable for DC

Tinbum
Posts: 1115
Joined: Mon May 31, 2021 9:55 pm

Armoured cable for DC

#1

Post by Tinbum »

I have a company in redoing one set of my solar panels through an insurance company and in the conversation with them we talked about running the DC through armoured SWR cable as it is at present and they say it's not allowed. Something to do with it not being double insulated.

Anyone heard of this?
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
User avatar
Stinsy
Posts: 2834
Joined: Wed Jun 02, 2021 1:09 pm

Re: Armoured cable for DC

#2

Post by Stinsy »

Nonsense!

Armoured cable is indeed double-insulated and is perfectly fine for DC applications. Every rating table I've ever seen has made this clear.

Here is a document you can use for current ratings and voltage drop calculations: https://www.rm-electrical.com/wp-conten ... trical.pdf

SWA cable tends to be rated at 1000V between cores and 600V core-to-earth. Domestic PV installations tend not to exceed 500V so you shouldn't have a problem there either.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
User avatar
nowty
Posts: 5773
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Armoured cable for DC

#3

Post by nowty »

I agree Stinsy,

Armoured cable is double insulated anyway, in fact they are generally triple insulated. You could argue each conductor in the multicore cable would only be single insulated.

I recall looking at the spec of armoured cable I have used and it was well within the voltage capability of the cable in both DC or AC, so I don't have an issue of using it and I certainly would not use any other type underground.

Maybe its a general MCS recommendation for connected panels to an inverter ?, i.e, use double insulated solar cable with 1000v+ rating. And the company has interpreted it literally without taking any reasonable intelligence.

Or maybe its just cheaper not to use armoured cable !
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Tinbum
Posts: 1115
Joined: Mon May 31, 2021 9:55 pm

Re: Armoured cable for DC

#4

Post by Tinbum »

I was surprised as armoured is rated for AC and DC.

As the wall the inverter is on is due to be knocked down I asked if they could relocate the inverter in the process which they are happy to do. I'd already put in a new armoured cable for the DC but they say they can't use it as explained above. They have been pulled up for using it on a big project. They think it's possibly because the DC can't be isolated.

The other strange thing is the inverter has to be mounted on a fire board which is then mounted on a brick wall!!
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
User avatar
nowty
Posts: 5773
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Armoured cable for DC

#5

Post by nowty »

Tinbum wrote: Tue Oct 05, 2021 10:08 am I was surprised as armoured is rated for AC and DC.

As the wall the inverter is on is due to be knocked down I asked if they could relocate the inverter in the process which they are happy to do. I'd already put in a new armoured cable for the DC but they say they can't use it as explained above. They have been pulled up for using it on a big project. They think it's possibly because the DC can't be isolated.

The other strange thing is the inverter has to be mounted on a fire board which is then mounted on a brick wall!!
I can understand that they might not have wanted to use the SWA because you'd installed it so its not theirs. I do recall having a hell of an argument with a BT man when they installed my broadband 11 years ago. I wanted the main termination socket in the lounge next to my router and not in the hallway were the cable came in. He wanted to staple the cable along the skirting board and drill through an internal wall. But I already had laid a twisted pair cable under the floor so all he had to do was connect it up. He did not want to use it but in the end he agreed although he grumbled, "I'm not supposed to do this."
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
User avatar
Fintray
Posts: 1551
Joined: Mon May 31, 2021 6:37 pm
Location: Aberdeenshire

Re: Armoured cable for DC

#6

Post by Fintray »

My latest PV system was installed by a MCS installer and they had no problem with me supplying and running in the 4 core SWA cable between the panels and the inverters.
3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
User avatar
Stinsy
Posts: 2834
Joined: Wed Jun 02, 2021 1:09 pm

Re: Armoured cable for DC

#7

Post by Stinsy »

Tinbum wrote: Tue Oct 05, 2021 10:08 am The other strange thing is the inverter has to be mounted on a fire board which is then mounted on a brick wall!!
Mounting the inverter onto fireboard that is set away from the external wall is to reduce condensation. Because my inverter is in the attic attached to the gable-end wall, the installer who put my system in did as you describe.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Tinbum
Posts: 1115
Joined: Mon May 31, 2021 9:55 pm

Re: Armoured cable for DC

#8

Post by Tinbum »

I can see that is logical for some cases. This is actually mounted on the external brick leaf of a cavity wall that is inside a barn (so actually an internal wall) and the inverter is rated for external mounting.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Tinbum
Posts: 1115
Joined: Mon May 31, 2021 9:55 pm

Re: Armoured cable for DC

#9

Post by Tinbum »

nowty wrote: Tue Oct 05, 2021 10:46 am I can understand that they might not have wanted to use the SWA because you'd installed it so its not theirs. I do recall having a hell of an argument with a BT man when they installed my broadband 11 years ago. I wanted the main termination socket in the lounge next to my router and not in the hallway were the cable came in. He wanted to staple the cable along the skirting board and drill through an internal wall. But I already had laid a twisted pair cable under the floor so all he had to do was connect it up. He did not want to use it but in the end he agreed although he grumbled, "I'm not supposed to do this."
I hate cables surface mounted like that but can understand why someone may not want to use a cable someone else ha put in. This SWR is about 8m long brand new and visible from one end to the other. I don't mind if they want to run their own cable but it would be much better and much safer in armoured.
4 cores of single core solar cable won't have the same physical protection that armoured does inside a barn.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
User avatar
Stinsy
Posts: 2834
Joined: Wed Jun 02, 2021 1:09 pm

Re: Armoured cable for DC

#10

Post by Stinsy »

I can understand an electrician's reluctance to use a cable installed by someone else. But common sense has to be applied. Particularly with SWA. If you can see both ends and have a good idea where it goes, insulation resistance tests OK, R1+R2 and R1+RN both test in line with the estimated length, then they should be very confident in using it. If there was an iffy hidden or buried junction box or something, the above tests would show it...
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Post Reply