DC connections and specs
Posted: Sat Nov 23, 2024 10:42 pm
I need to extend one of my PV cable pairs about 4m, which leads to the question "what is the right way to join a DC PV cable"? Given the requirement for double-insulation can I just use a copper butt crimp to join the two ends and then put two layers of heat-shrink over it? Or maybe better heat-shrink, some physical protection and a bit more heatshrink? I could just use a pair of MC4s, which are designed for this application, but they don't have a great rep, so I thought an insulated butt-crimp would actually be a more reliable, lower-resistance connection. Max current (Iscmax@60C) is 14.5A Thoughts?
It's 4mm cable.
And another thing I don't really understand. All the specs for DC isolators tell you to get one rated to to 125% of the short-circuit current. So the 16A DC isolator I have for a circuit with an Iscmax of 14.3A which you might think would be adequate, officially isn't. It should be > 17.9A, which in practice means a 20A one.
Does anyone know where this +25% comes from? Is it the wiring regs or some random safety factor everone uses, or an MCS recommendation? Or is this a simple-minded way of allowing for the thermal co-efficients? My panels string Isc is 14.07A, and the temp coefficient for Isc is 0.050%/C, so at 60C that's ~1.5% change in current, (i.e. 14.3A). Which is a long way from 25%.
I found this, written circa 2010 here (http://eco-nomical.co.uk/pv_install.htm)
"all DC equipment including cabling must have a minimum rating of:
Voltage: Voc x 1.15
Current Isc x 1.25 .
Voc and Isc are provided by module manufacturers. Obviously they must be summed appropriately for strings (connections in series add voltage only, connections in parallel add current only). These safety factors must be applied because under certain conditions differing from standard test conditions the values can exceed those stated. Any DC installations exceeding 120Voc require double insulation for all their components including cabling."
Is that summarising from the wiring regs?
In practice if I have 4 poles in a high-quality switch (so each cable is through 2 switches) is an 11% margin as opposed to a 25% margin a really bad idea, or not? I am well aware that DC switches are prone to catching fire if you actually try to use them and the quality or ratings are insufficient (and the latest regs tell you to avoid them if possible). More switches in series appears to give you a higher voltage you can switch the rated current at, not a higher current.
It's 4mm cable.
And another thing I don't really understand. All the specs for DC isolators tell you to get one rated to to 125% of the short-circuit current. So the 16A DC isolator I have for a circuit with an Iscmax of 14.3A which you might think would be adequate, officially isn't. It should be > 17.9A, which in practice means a 20A one.
Does anyone know where this +25% comes from? Is it the wiring regs or some random safety factor everone uses, or an MCS recommendation? Or is this a simple-minded way of allowing for the thermal co-efficients? My panels string Isc is 14.07A, and the temp coefficient for Isc is 0.050%/C, so at 60C that's ~1.5% change in current, (i.e. 14.3A). Which is a long way from 25%.
I found this, written circa 2010 here (http://eco-nomical.co.uk/pv_install.htm)
"all DC equipment including cabling must have a minimum rating of:
Voltage: Voc x 1.15
Current Isc x 1.25 .
Voc and Isc are provided by module manufacturers. Obviously they must be summed appropriately for strings (connections in series add voltage only, connections in parallel add current only). These safety factors must be applied because under certain conditions differing from standard test conditions the values can exceed those stated. Any DC installations exceeding 120Voc require double insulation for all their components including cabling."
Is that summarising from the wiring regs?
In practice if I have 4 poles in a high-quality switch (so each cable is through 2 switches) is an 11% margin as opposed to a 25% margin a really bad idea, or not? I am well aware that DC switches are prone to catching fire if you actually try to use them and the quality or ratings are insufficient (and the latest regs tell you to avoid them if possible). More switches in series appears to give you a higher voltage you can switch the rated current at, not a higher current.