DC disconnects/isolators.
Posted: Sun Apr 13, 2025 12:21 pm
Hi Gents.
We have some upcoming projects this summer to extend our solar capability.
The larger arrays will go through the sunsynk mppts just fine,
But we are planning 2 strings, which would not hit the start up voltage and even if could, would be woefully inefficient if run through the sunsynk.
As a result ive bought a 45A Victron SmartSolar 150-45 -150 Voc, PV Charge Controller to run these strings with.
But i will need a solar disconnect, especially as the cables will be underground for 10m (planned swa)
As space is a precious commodity, i was thinking about a 2 string isolator, but i am just coming up confused with what will do the job
Strings will be 3 panels of 440W.
Voc 38.9V so 38.9x3, x1.2 = 140.04V
Isc 14.31A so 14.31x 1.25 = 17. 89A
So i am looking for something that can handle 18A or 20A and 150V per string.
Some 4 pole switches ive looked at last night have a 20A rating, but their specs say only do a max of 8A per string, which suggests the max Amps is split between the two strings evenly with some buffer room
Another ive looked at is 25A and does 18A per string, which clearly is not splitting the main number evenly between the two, but suggests the strings are both able to take the max amperage.
And the majority just have a table that doesnt make clear if the values are per string or not.
Can anyone help?
We have some upcoming projects this summer to extend our solar capability.
The larger arrays will go through the sunsynk mppts just fine,
But we are planning 2 strings, which would not hit the start up voltage and even if could, would be woefully inefficient if run through the sunsynk.
As a result ive bought a 45A Victron SmartSolar 150-45 -150 Voc, PV Charge Controller to run these strings with.
But i will need a solar disconnect, especially as the cables will be underground for 10m (planned swa)
As space is a precious commodity, i was thinking about a 2 string isolator, but i am just coming up confused with what will do the job
Strings will be 3 panels of 440W.
Voc 38.9V so 38.9x3, x1.2 = 140.04V
Isc 14.31A so 14.31x 1.25 = 17. 89A
So i am looking for something that can handle 18A or 20A and 150V per string.
Some 4 pole switches ive looked at last night have a 20A rating, but their specs say only do a max of 8A per string, which suggests the max Amps is split between the two strings evenly with some buffer room
Another ive looked at is 25A and does 18A per string, which clearly is not splitting the main number evenly between the two, but suggests the strings are both able to take the max amperage.
And the majority just have a table that doesnt make clear if the values are per string or not.
Can anyone help?