Bignose2 wrote: ↑Sun Apr 02, 2023 9:15 am
I had hoped I had made it clear, the pictures show the isolation switch etc. as it was all professionally installed & commission & DNO paper work etc.
I cannot image that the inverter sold into mainstream the UK does not have those protections build in on the backup circuit.
In the case of power failure from what I read it immediately isolates just that one circuit so no way it can feed back to the grid.
Its not as if trying to do the whole house on UPS.
Looks to me that the isolator shown in post #15 pictured upthread is the isolator required for the connection from the PV inverter, it is not the same as the isolator required between the battery system and the CU, you need both. A lockable double pole mcb is arguably sufficient for the latter (though IMO is not really the intent of the IET CoP) and in practice many ppl fit another rotary one right next to the battery charger/inverter.
Are you going to change the wiring between the meter pictured and the isolator to avoid AC power derived from the battery showing on the meter? Or have I misunderstood the topology?
Yes it is explained there but the key point is that for the RCDs to provide the protection but not nuisance trip there needs to be one and only one neutral-earth bond in the system. So when the mains is present the bond relay in the invert must be open, and if not then closed.openspaceman wrote: ↑Sun Apr 02, 2023 1:08 pm
I am going to read Nowty's link but from my current position of ignorance I cannot see how a live to earth leak would affect an RCD by having two bonded earths.
You are now allowed to have your earth electrode wired in parallel with the PME earth provided by the DNO but it does not change the position regarding the neutral-earth bonding.