Not really solar related, but wondering if anyone has helpful suggestions.
Been at my in-laws this afternoon - they had a couple of power outages during & after the storm. After the first one their boiler sprung a leak, then after the 2nd one, one of the mcbs on the consumer unit will not reset. There is only 1 main rcd, which isn't tripped - see photo.
It feeds the boiler and most of the sockets in the older part of the house + the burglar alarm.
I went round & unplugged everything in every room to no avail.
The fuse on the boiler switch is OK, and also the burglar alarm fuse.
I thought I'd hit on something after asking them what they did differently between the 1st & 2nd powercut - to which the answer was - we boiled a kettle in the bedroom - as you do!
So a 3kw kettle plugged in via a fully wound in 10A Extension lead in the bedroom - oops.
I unscrewed the socket but there was nothing obviously wrong (metal back box not earthed, but has obviously always been like that).
They tried unsuccessfully to get a plumber for the boiler and an electrician - hoping for more success tomorrow.
Tripping mcb
Tripping mcb
Solar PV since July '22:
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W
-
- Posts: 649
- Joined: Mon May 31, 2021 7:16 pm
- Location: ville of spiky things
Re: Tripping mcb
When you try to reset the MCB does it make a big "splat" itself and fail to latch? if so obviously you do have a pretty serious short somewhere, if no splat but just fails to latch it might be a knackered MCB itself, fairly rare but not unknown. If you have unplugged and switched off everything it comes down to testing various bits of the circuit to home in on the fault.
Desp
Desp
Blah blah blah
Re: Tripping mcb
Just a thought (from a non electrician),
If you turn off the incoming power, then try to turn the MCB on will this show whether the MCB is faulty?
If the MCB fails to stay engaged it would indicate that the MCB is faulty as there is no power to be tripping it?
If the MCB engages then it would indicate that there is an electrical fault somewhere.
Just thinking of ways to try and focus in on where the problem is.
I could be wrong - so perhaps an electrician might have further insights?
Good Luck
If you turn off the incoming power, then try to turn the MCB on will this show whether the MCB is faulty?
If the MCB fails to stay engaged it would indicate that the MCB is faulty as there is no power to be tripping it?
If the MCB engages then it would indicate that there is an electrical fault somewhere.
Just thinking of ways to try and focus in on where the problem is.
I could be wrong - so perhaps an electrician might have further insights?
Good Luck
Re: Tripping mcb
was going to post this but he beat me too it, do this!cojmh wrote: ↑Sun Jan 26, 2025 7:28 pmJust a thought (from a non electrician),
If you turn off the incoming power, then try to turn the MCB on will this show whether the MCB is faulty?
If the MCB fails to stay engaged it would indicate that the MCB is faulty as there is no power to be tripping it?
If the MCB engages then it would indicate that there is an electrical fault somewhere.
Re: Tripping mcb
If everything was fine before the leak, there must be water stuck in a joint box, accessory , get the heating on/ dehumidifier/ window open and dry the leak area
Re: Tripping mcb
With the power off , disconnect the live wire from the mcb .spread-tee wrote: ↑Sun Jan 26, 2025 6:59 pm When you try to reset the MCB does it make a big "splat" itself and fail to latch? if so obviously you do have a pretty serious short somewhere, if no splat but just fails to latch it might be a knackered MCB itself, fairly rare but not unknown. If you have unplugged and switched off everything it comes down to testing various bits of the circuit to home in on the fault.
Desp
Reset mcb .
Power on.
If it wont reset then it's an mcb problem.
If it resets its a problem with that circuit.
reconnect wire.
Then .........
Unplug/disconnect (turning sockets off does NOT disconnect appliances unless a DP (double pole socket) -unusual .
Then try again and report back....
1750w Vertical PV micro inverters
3800w almost horizontal/south
Aarrow Becton 7 Woodburner
Dream 3kw ASHP only connected to summer Pool.
Allotment heavy clay.
1.784kw Kirk Hill
0.875kw Derril Water
0.2kwWhitelaw Brae
1kw Harlow Hydro.
3800w almost horizontal/south
Aarrow Becton 7 Woodburner
Dream 3kw ASHP only connected to summer Pool.
Allotment heavy clay.
1.784kw Kirk Hill
0.875kw Derril Water
0.2kwWhitelaw Brae
1kw Harlow Hydro.
Re: Tripping mcb
That board is decades old. Assuming you have removed the possibility of a defective appliance causing the issue by removing everything on that circuit then you either have a defective MCB or defective wiring. TBH, either way, you need a spark to come round a quote for a new all RCBO CU.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Re: Tripping mcb
Thanks all for the advice and suggestions. I will pass them on - I might have to go back again if they can't get hold of their usual electrician quickly (not surprisingly, was no answer yesterday, and I wouldn't be that surprised if they are rushed off their feet post storm)
Solar PV since July '22:
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W