ducabi wrote: ↑Wed Nov 02, 2022 1:29 pm
Now when everything is working I want to understand what's wrong in general starting with the new mini CU.
1) The spec was to include RCD + MCB curve C. Am i right that there is no RCD at all and MCB is actually curve B?
What are my options? Adding RCD + replacing MCB with curve C or do i need RCBO? I guess I need RCD not only for inverter but for lights and socket as well.
2)
Oldgreybeard wrote: ↑Tue Nov 01, 2022 5:30 pm
Easy to fix, the MCB (circled in red below) just needs to be swapped for an RCBO (at the same time the cable rating needs to be checked - 32A is too high to protect any cable under 4mm²):
Shall I check what cables I have or change RCBO/MCB for a different one?
3) If there are so many safety issues related to it shall i report it somewhere?
You could try and report it to whichever part P body the electrician is a member of, but TBH I'm not convinced that's the best route to go down. They would almost certainly just get the electrician that did the work to try and put it right, and if I'm honest I would be concerned that this still may not make things safe. As there are obvious major safety issue visible from the photos, who knows what else might be lurking unseen? For example, are the terminals all torqued up correctly, or was the installation properly safety tested?
A B curve over current device is fine for an inverter, safer than a C curve, really. C curve devices are very slow to operate when overloaded and are intended for protection for things that have a very high initial current demand, like big electric motors and pumps, so they won't nuisance trip if there is an overload for a few seconds.
You are right, there is no RCD protection at all on the inverter circuit, it's been connected via that 32A MCB to the incoming supply at the main switch.
Swapping the MCB for an RCBO is very quick and easy and a suitable Fusebox RCBO is around £16, so not that expensive. It's a ten minute job to swap this and test it.
The lights and sockets have RCBOs already, so have RCD protection.
The cable size needs to be checked, specifically the cable running to the inverter. The cable size determines the over current protection requirement. 1.5mm² flex can carry 16A maximum, so needs a 16A RCBO, 2.5mm² flex can carry 25A, so needs a 20A RCBO. 4mm² flex can carry 32A, so needs a 32A RCBO. I doubt 4mm² flex will actually fit the terminals in the inverter, though, so I doubt that's what's been used.
The consumer unit needs two blanks fitting at the left to block the hole and prevent anyone being able to poke a finger in and touch the live busbar at the bottom. Very quick and easy to fix, and cheap.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter