So that's 49.9V / 15 = 3.32V per cell.
My new cells were still charging but were at 3.31V so I reckoned time to install them but the Growatts were at 56.16V so there was about a 3V difference. Not quite sure about doing the final connection, but will check with a fuse and measure the current with a clamp meter.

Tiny spark and fizzle but clamp meter showing over 100A so I have decided to use my EV as a dump load to drop the Growatt Battery stack to 53.22V which should match my Pylontech + extra cell at its current voltage.

At a 5kW discharge rate of the Growatt batteries, that's going to take a couple of hours.