Pylontech - Servtec console software

Tinbum
Posts: 1194
Joined: Mon May 31, 2021 9:55 pm

Re: Pylontech - Servtec console software

#61

Post by Tinbum »

Victron have a thread on this where they have altered their algorithm to use the read max cell voltage in the pack and adjust the charge voltage down to keep any max cell voltage below 3.5v (recalling value from memory).

I now have incorporated this into my Teensy setup to do the same.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
User avatar
Stinsy
Posts: 3201
Joined: Wed Jun 02, 2021 1:09 pm

Re: Pylontech - Servtec console software

#62

Post by Stinsy »

BTW any link to an idiot’s guide to getting this set up and ideally accessible from HA would be much appreciated!
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Tinbum
Posts: 1194
Joined: Mon May 31, 2021 9:55 pm

Re: Pylontech - Servtec console software

#63

Post by Tinbum »

Stinsy wrote: Sun Jan 26, 2025 7:51 pm BTW any link to an idiot’s guide to getting this set up and ideally accessible from HA would be much appreciated!
Not that I know of.

I incorporated it into my setup where I directly read the CAN messages from the batteries, alter them as required and then send them on to the inverter.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
greentangerine
Posts: 75
Joined: Mon Aug 23, 2021 12:31 pm

Re: Pylontech - Servtec console software

#64

Post by greentangerine »

Is there any way of checking the SOH of individual packs?

I've clearly got a major problem when over 19kWh of battery packs now take less than two hours to go from 20% to 100% via a 3kW inverter!
65 x Ø58mm SunnPro/Gledhill 450l
Solis Mini 4G 3kW/Sharp ND210/2.94kWp
SB1600/Sharp ND220/1.76kWp
SB1600/Kinve 235/2.115kWp
Dean Forge Croft Clearburn 11kW
SoFar ME3000/Pylontech US2000/19.2kWh
Ecodan 11kW HP
MG4
PVOutput
SporranMcDonald
Posts: 62
Joined: Thu Feb 16, 2023 10:29 am
Location: East Hampshire

Re: Pylontech - Servtec console software

#65

Post by SporranMcDonald »

greentangerine wrote: Mon Jan 27, 2025 3:10 pm Is there any way of checking the SOH of individual packs?

I've clearly got a major problem when over 19kWh of battery packs now take less than two hours to go from 20% to 100% via a 3kW inverter!
You don't say whether you got the minicom working . . . . . but if you did .. . . . . there is the "stat" command which shows more detailed BMS statistics.

In theory stat [n] should give you the SOH for the individual units . . . . . [ Servtech documentation ]

On my system I can only get a non-zero SOH value for the Master battery ( i.e. where the console lead is plugged ).

While Console cable in Master Battery - stat 2 / stat 3 / stat 4 . . . . . all show zero values for SOH . . . . although the values of other stat parameters vary between the four units. [ I don't understand what is going on here. ]

Maybe moving the Console cable to specific units would show the SOH for that specific unit .
4 kWp Solar PV : 50%/50% SE/SW : Solis Hybrid 3.6 : Pylontec 9.6 kWh
5 kW & 4kW Air-to-Air Mitsubishi Heat Pumps
Ripple : Graig Fatha & Kirk Hill . . . . plus various other renewable projects.
No Car : bicycles : bus & train
Tinbum
Posts: 1194
Joined: Mon May 31, 2021 9:55 pm

Re: Pylontech - Servtec console software

#66

Post by Tinbum »

greentangerine wrote: Mon Jan 27, 2025 3:10 pm Is there any way of checking the SOH of individual packs?

I've clearly got a major problem when over 19kWh of battery packs now take less than two hours to go from 20% to 100% via a 3kW inverter!
Yes, pretty sure you should be able to see them in BatteryView. An overall SOH is transmitted over CAN as well.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
greentangerine
Posts: 75
Joined: Mon Aug 23, 2021 12:31 pm

Re: Pylontech - Servtec console software

#67

Post by greentangerine »

Which value is SOH in the stat output?

This is my master battery ...

pylon_debug>stat 1
@
Device address 1
Data Items : 1918
HisData Items : 2044
MiscData Items : 121
Charge Cnt. : 252
Discharge Cnt. : 0
Charge Times : 34151
Status Cnt. : 125
Idle Times : 36049
COC Times : 0
DOC Times : 0
COCA Times : 0
DOCA Times : 0
SC Times : 0
Bat OV Times : 2501
Bat HV Times : 906
Bat LV Times : 50
Bat UV Times : 9
Bat SLP Times : 0
Pwr OV Times : 0
Pwr HV Times : 0
Pwr LV Times : 0
Pwr UV Times : 0
Pwr SLP Times : 0
COT Times : 0
CUT Times : 0
DOT Times : 0
DUT Times : 0
CHT Times : 0
CLT Times : 0
DHT Times : 0
DLT Times : 0
Shut Times : 1036
Reset Times : 699
RV Times : 0
Input OV Times : 0
SOH Times : 2559
BMICERR Times : 0
CYCLE Times : 1124
Pwr Percent : 8
Pwr Coulomb : 13860000
Dsg Cap : 56239334
HT@0.5C Cnt : 0
LT@0.5C Cnt : 0
HT Cnt : 0
LT Cnt : 0
LV Cnt : 0
LifeWarn Times : 0
LifeAlarm Times : 0
Command completed successfully
$$
pylon_debug>
65 x Ø58mm SunnPro/Gledhill 450l
Solis Mini 4G 3kW/Sharp ND210/2.94kWp
SB1600/Sharp ND220/1.76kWp
SB1600/Kinve 235/2.115kWp
Dean Forge Croft Clearburn 11kW
SoFar ME3000/Pylontech US2000/19.2kWh
Ecodan 11kW HP
MG4
PVOutput
SporranMcDonald
Posts: 62
Joined: Thu Feb 16, 2023 10:29 am
Location: East Hampshire

Re: Pylontech - Servtec console software

#68

Post by SporranMcDonald »

Sorry, it looks like I have misled you. I'm guessing that your battery is an older model than my 2000C.
EDIT : I see that you have 2000B . . . . .

If you see below, my 2000C Master battery has an explicit "SOH" value of 99. ( All others have a SOH of zero. )

I'm guessing that the SOH is a calculated value that is only presented at specific points on the various interfaces.
I can also see a SOH of 99 using the minicom "pwrsys" command. . . . i.e. calculated for the whole battery stack.
I cannot find SOH anywhere in BatteryView.
ServTech doc does NOT show SOH in as minicom "stat" output. ( I'm guessing it's from an older battery model, than 2000C. )

I better fall silent now before I waste you time any further. I suggest that you contact Pylontech UK support, so that you (eventually) get some formal assistance . . . while possible informal support elsewhere e.g. Facebook Pylontech Battery group

Code: Select all

stat 1
@
Device address           1
Data Items      :        0
HisData Items   :     1793
Charge Cnt.     :        0
Discharge Cnt.  :      446
Charge Times    :    27182
Status Cnt.     :      445
Idle Times      :    41161
COC Times       :        0
COC2 Times      :        0
DOC Times       :        0
DOC2 Times      :        0
COCA Times      :        0
DOCA Times      :        0
SC Times        :        0
Bat OV Times    :        0
Bat HV Times    :        0
Bat LV Times    :        0
Bat UV Times    :        0
Bat SLP Times   :        0
Pwr OV Times    :        0
Pwr HV Times    :        0
Pwr LV Times    :        0
Pwr UV Times    :        0
Pwr SLP Times   :        0
COT Times       :        0
CUT Times       :        0
DOT Times       :        0
DUT Times       :        0
CHT Times       :        0
CLT Times       :        0
DHT Times       :        0
DLT Times       :        0
Shut Times      :       33
Reset Times     :       36
RV Times        :        0
Input OV Times  :        0
SOH Times       :        0
BMICERR Times   :        0
CYCLE Times     :      187
SOH             :       99
Pwr Percent     :       86
Pwr Coulomb     : 152322560
Dsg Cap         :  9362795
HT@0.5C Cnt     :        0
LT@0.5C Cnt     :        0
HT Cnt          :        0
LT Cnt          :        0
LV Cnt          :        0
LifeWarn Times  :        0
LifeAlarm Times :        0
Command completed successfully

4 kWp Solar PV : 50%/50% SE/SW : Solis Hybrid 3.6 : Pylontec 9.6 kWh
5 kW & 4kW Air-to-Air Mitsubishi Heat Pumps
Ripple : Graig Fatha & Kirk Hill . . . . plus various other renewable projects.
No Car : bicycles : bus & train
User avatar
nowty
Posts: 6007
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Pylontech - Servtec console software

#69

Post by nowty »

There is a guy on EBay who does repairs, cell replacements and other repairs, plenty of good feedback. Having seen a tear down video of one it’s something that I would not attempt myself, except maybe a simple cell rebalance.
https://www.ebay.co.uk/itm/276770956771
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 30MWh generated
6 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 520 m3
Tinbum
Posts: 1194
Joined: Mon May 31, 2021 9:55 pm

Re: Pylontech - Servtec console software

#70

Post by Tinbum »

I would have a look at the log files for the battery that is playing up. If you can see that it hasn't been subjected to over voltage (of the battery not cell) then contact pylontech themselves and try for a warranty replacement. They are very good if it's not user error.