Island Mode N-E Bond Relay, How do inverters manage this?

Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: Island Mode N-E Bond Relay, How do inverters manage this?

#31

Post by Oldgreybeard »

Swwils wrote: Wed Nov 09, 2022 8:13 am Middle OFF seems very sensible to me and I don't like those 4 module changeovers with no mid position.
Stipulated in the manuals for some inverters, too, as mentioned in this post in another thread: https://camelot-forum.co.uk/phpBB3/view ... 200#p21768

Sofar HYD3600 manual EPS switching.jpg
Sofar HYD3600 manual EPS switching.jpg (83.04 KiB) Viewed 981 times
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
Swwils
Posts: 530
Joined: Sat Feb 26, 2022 12:58 pm

Re: Island Mode N-E Bond Relay, How do inverters manage this?

#32

Post by Swwils »

So what are people's thoughts of just bonding N+E with the island mode isolator?

A 4 pole changeover switch with middile off could make this quite easy rather than have the additional complexity of a relay.
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: Island Mode N-E Bond Relay, How do inverters manage this?

#33

Post by Oldgreybeard »

Swwils wrote: Wed Nov 09, 2022 6:20 pm So what are people's thoughts of just bonding N+E with the island mode isolator?

A 4 pole changeover switch with middile off could make this quite easy rather than have the additional complexity of a relay.
Makes a great deal of sense for a manual changeover, IMHO. My only concern would be the case where the inverter manufacturer seems averse to making an N to PE connection in EPS mode, although for the life of me I can't understand why this could be a concern, given that N to PE will most probably be linked when the inverter is running in grid connected mode.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
Swwils
Posts: 530
Joined: Sat Feb 26, 2022 12:58 pm

Re: Island Mode N-E Bond Relay, How do inverters manage this?

#34

Post by Swwils »

I've not seen any indication of this for lux.

Not that I think what they sent is even able to be done within regulations:

Image

Can't see this being sensible at all.
User avatar
Stinsy
Posts: 2640
Joined: Wed Jun 02, 2021 1:09 pm

Re: Island Mode N-E Bond Relay, How do inverters manage this?

#35

Post by Stinsy »

By far the simplest solution is for E-N to be linked out when running off-grid. If your inverter has a UPS output then all is good. If your inverter has an EPS output then you need the link only to be active in grid-down condition. However some inverters seem to have circuitry that wouldn’t like an E-N link, and the point of an E-N link is to ensure that if an earthed casing become live it would immediately trip the overcurrent protective device and that is far form certain with many inverters…
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
ducabi
Posts: 172
Joined: Sat Sep 10, 2022 5:32 pm

Re: Island Mode N-E Bond Relay, How do inverters manage this?

#36

Post by ducabi »

I'm now worried what to do with my Sofar HYD3600ES. I'm in a not-old estate (late 80s), so being 5-10 away from the house means I'm outside my plot. I need TT for EPS and also for commando socket (for EV charging). I could use PEN protection like matt:e for commando but it won't help with EPS for inverter.
My worry comes from watching John Ward on YT which says it's not easy to do good TT on TNCS whereas by (other) electrician says it's a simple £100 job.
User avatar
Stinsy
Posts: 2640
Joined: Wed Jun 02, 2021 1:09 pm

Re: Island Mode N-E Bond Relay, How do inverters manage this?

#37

Post by Stinsy »

ducabi wrote: Wed Nov 09, 2022 10:59 pm I'm now worried what to do with my Sofar HYD3600ES. I'm in a not-old estate (late 80s), so being 5-10 away from the house means I'm outside my plot. I need TT for EPS and also for commando socket (for EV charging). I could use PEN protection like matt:e for commando but it won't help with EPS for inverter.
My worry comes from watching John Ward on YT which says it's not easy to do good TT on TNCS whereas by (other) electrician says it's a simple £100 job.
The “easiness” of a TT depends where you live and how much you care about a good result. The whole reason you’re now allowed (questionable in some cases) PEN-fault detection in stead of an earth rod is that in some areas earth rods are problematic. EG around Bristol you’re on solid rock, in London the risk of hitting something (sewer, gas main, someone’s basement, etc. is too high).

If you’re more rural and have a convenient flowerbed you can wallop a rod into then you’re good. You might need a 2nd or 3rd rod if you don’t get a decent reading off the first though.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
ducabi
Posts: 172
Joined: Sat Sep 10, 2022 5:32 pm

Re: Island Mode N-E Bond Relay, How do inverters manage this?

#38

Post by ducabi »

Stinsy wrote: Thu Nov 10, 2022 6:00 am The “easiness” of a TT depends where you live and how much you care about a good result. The whole reason you’re now allowed (questionable in some cases) PEN-fault detection in stead of an earth rod is that in some areas earth rods are problematic. EG around Bristol you’re on solid rock, in London the risk of hitting something (sewer, gas main, someone’s basement, etc. is too high).

If you’re more rural and have a convenient flowerbed you can wallop a rod into then you’re good. You might need a 2nd or 3rd rod if you don’t get a decent reading off the first though.
I'm Bristol area. 99.5% of the time the house will be using grid earthing, so I don't want to move from TNCS to TT in case TT earthing is questionable.
So, the issue is a good earthing for EPS + good earthing for commando socket. I could probably do a PEN protection for commando socket, TT for inverter and leave TNCS for normal use. Question is if it makes sense.
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: Island Mode N-E Bond Relay, How do inverters manage this?

#39

Post by Oldgreybeard »

It takes maybe ten to fifteen minutes to bang in an earth rod and see what value of Ra you can get. My experience has been that it's really unusual to not be able to get below 200 ohms. When I put in a rod for our garage supply the value of Ra measured was 26 ohms, when the charger installer checked our main earth rod Ra was 24 ohms (there's about 40m between the garage rod and the incoming supply rod).

A 3/8" earth rod without the enclosure etc costs less than a fiver, so it might be worth just banging one in (in a safe location away from other services) as a test, then asking an electrician to come around and measure the test electrode Ra for you (will take minutes to do). That way you would know whether TT for the whole supply is a viable option or not. If it turns out that Ra is OK (under 200 ohms) then you're good to go with a proper TT installation. If it's a bit marginal you can try swapping the 3/8" rod for a 5/8" one, or joining two together with a coupler and driving it down deeper.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
Post Reply