Island Mode N-E Bond Relay, How do inverters manage this?
Posted: Sat Oct 22, 2022 12:28 pm
When I was installing my Luxpower inverter and batteries, my electrician came across an issue where the system doesn't behave correctly in island mode, ie when the grid is out and we're running from batteries. Rather than try and explain it myself, he's written it out in detail because we need to forward it on to Luxpower. I thought there's bound to be someone on here who's come across this issue before and might be able to either shed light on how to fix it.
Hi J
As per our conversation today, I believe there is an issue with the inverter switching between Connected Mode and Island Mode (switching between on and off-grid).
When in connected mode the voltages at the incoming terminals of the Critical Supplies consumer's unit connected to the UPS output are L-N 230V, L-PE 230V and N-PE 0V. This is as expected.
When simulating mains power failure, the inverter switches into UPS mode. My understanding is that the inverter includes an internal "Island Mode Isolator" that isolates the incoming grid L & N from the outgoing UPS L & N within the inverter when running in Island Mode. This is as required by UK Regulations when any generator runs in Island Mode.
In Island Mode I obtained readings of 230V between L & N, but the voltage between L and PE and N and PE varies wildly and I measured as much as 90V N to PE at one point.
Below is a link to the IET website (Institution of Engineering and Technology, the organisation that writes the Wiring Regulations and other electrical publications). It links to excerpts from their Code of Practice for Electrical Energy Storage Systems and details the connection requirements for Connected Mode and Island Mode and specific requirements for switching between them.
Reference is made to the need for a N-E Bond Relay. This relay contact switches a link between the N and PE of the UPS output dependent on the status of the Island Mode Isolator; as the Island Mode Isolator throws open (under grid power loss), the N-E contact closes thus grounding the N of the UPS supply from the inverter and preventing a "floating neutral". When the Island Mode Isolator makes again (on restoration of the grid supply), the N-E contact opens thus removing what would be detected as a N-PE fault by any upstream RCD and preventing it from tipping.
I can find no reference to a N-E Bond Relay in the documentation for the inverter. There is no reference to an internal one nor a reference for the need for one to be installed externally, however, it is clear from the document in the link that one is required.
From the voltages I have obtained I believe there is no N-E Bond relay present within the inverter.
Due to the requirement for the relay contact to close after the isolator has opened, but open before the isolator closes I believe the relay needs to be controlled by the inverter; the inverter is in charge of when switching takes place.
The questions I would put to Lux Power are:
Is there a N-E Bond Relay integral to the inverter and if so why am I obtaining the readings detailed above?
If there is not a N-E Bond Relay integral to the inverter, how can one be installed and connected externally?
Depending on the answers to 1 and 2, why is there no reference to the need to install a N-E Bond Relay or instruction on how to connect one to the inverter within the manual.
https://electrical.theiet.org/wiring-ma ... e-systems/
Hopefully I have provided sufficient information for Lux Power to understand the nature of the issue and the query, but if they require any further information I would be happy for them to contact me.
Hopefully they will be able to provide us with a solution to this problem.
Regards
Martyn
Hi J
As per our conversation today, I believe there is an issue with the inverter switching between Connected Mode and Island Mode (switching between on and off-grid).
When in connected mode the voltages at the incoming terminals of the Critical Supplies consumer's unit connected to the UPS output are L-N 230V, L-PE 230V and N-PE 0V. This is as expected.
When simulating mains power failure, the inverter switches into UPS mode. My understanding is that the inverter includes an internal "Island Mode Isolator" that isolates the incoming grid L & N from the outgoing UPS L & N within the inverter when running in Island Mode. This is as required by UK Regulations when any generator runs in Island Mode.
In Island Mode I obtained readings of 230V between L & N, but the voltage between L and PE and N and PE varies wildly and I measured as much as 90V N to PE at one point.
Below is a link to the IET website (Institution of Engineering and Technology, the organisation that writes the Wiring Regulations and other electrical publications). It links to excerpts from their Code of Practice for Electrical Energy Storage Systems and details the connection requirements for Connected Mode and Island Mode and specific requirements for switching between them.
Reference is made to the need for a N-E Bond Relay. This relay contact switches a link between the N and PE of the UPS output dependent on the status of the Island Mode Isolator; as the Island Mode Isolator throws open (under grid power loss), the N-E contact closes thus grounding the N of the UPS supply from the inverter and preventing a "floating neutral". When the Island Mode Isolator makes again (on restoration of the grid supply), the N-E contact opens thus removing what would be detected as a N-PE fault by any upstream RCD and preventing it from tipping.
I can find no reference to a N-E Bond Relay in the documentation for the inverter. There is no reference to an internal one nor a reference for the need for one to be installed externally, however, it is clear from the document in the link that one is required.
From the voltages I have obtained I believe there is no N-E Bond relay present within the inverter.
Due to the requirement for the relay contact to close after the isolator has opened, but open before the isolator closes I believe the relay needs to be controlled by the inverter; the inverter is in charge of when switching takes place.
The questions I would put to Lux Power are:
Is there a N-E Bond Relay integral to the inverter and if so why am I obtaining the readings detailed above?
If there is not a N-E Bond Relay integral to the inverter, how can one be installed and connected externally?
Depending on the answers to 1 and 2, why is there no reference to the need to install a N-E Bond Relay or instruction on how to connect one to the inverter within the manual.
https://electrical.theiet.org/wiring-ma ... e-systems/
Hopefully I have provided sufficient information for Lux Power to understand the nature of the issue and the query, but if they require any further information I would be happy for them to contact me.
Hopefully they will be able to provide us with a solution to this problem.
Regards
Martyn