Commissioning & Testing G98 and G100 via G99 Fast Track For Battery Storage
Posted: Mon Oct 24, 2022 7:30 am
Hi all,
Been approved for G99 Fast Track for Battery Storage utilising Solax X1-AC-3.6kw inverter, and at the moment one Solax Triple Power LFP 5.8kw Master battery
by SP Energy which is great (filled in the forms myself) just need a Competent Person Scheme Electrician for the installing and Signing Off as per email from SP Energy
Commissioning & Testing out G98 and G100.
Forms are: To Be Completed within 28 days of installation, informing the SP Energy so they can update their records as Fully Installed.
G98 Form B: Installation Document for Connection under G98 ENA EREC G98 Issue 1 Amendment 6 2021
G99 Form B3: Installation and Commissioning Confirmation Form ENA EREC G99 Issue 1Amendment 6 20220
My Battery turned up last week, Delivery Paper stated the Solax Master Battery, but infact was delivered a Slave Battery, which cannot connect directly to the inverter,
wrong size cables, short ones 650mm and most importantly no BMS on Slave, and not the Master Battery size 200 cm long... with BMS attached.
Telephoned the Supplier and told them and filled out their online website Contact Form about the Wrong Battery being delivered and attached file of picture of the outer
cardboard packaging showing the Details of the Slave Battery. Awaiting Reply
Now that I have a 3 month period to install from energy company, No Master Battery on install date as per Application G99 Form A1-2.
Now without a Master Battery, The Big Question is can you still Install, Commission and Test just the Solax X1-AC-3.6kw inverter with the Eastron SDM 230 MID Meter (for limiting Export Control to a Max of 3.68kW (16A) stated by SP Energy in Confirmation email) I will set to 0 Watts for maximum home use. Or has the AC Inverter to be connected to a Battery for the above forms Install, Commissioning and Tests to be Confirmed as Fully Installed as required by SP Energy Confirmation email within 28 days of being installed.
I know that battery is just that, So can you install the inverter alone without a battery.?
Been approved for G99 Fast Track for Battery Storage utilising Solax X1-AC-3.6kw inverter, and at the moment one Solax Triple Power LFP 5.8kw Master battery
by SP Energy which is great (filled in the forms myself) just need a Competent Person Scheme Electrician for the installing and Signing Off as per email from SP Energy
Commissioning & Testing out G98 and G100.
Forms are: To Be Completed within 28 days of installation, informing the SP Energy so they can update their records as Fully Installed.
G98 Form B: Installation Document for Connection under G98 ENA EREC G98 Issue 1 Amendment 6 2021
G99 Form B3: Installation and Commissioning Confirmation Form ENA EREC G99 Issue 1Amendment 6 20220
My Battery turned up last week, Delivery Paper stated the Solax Master Battery, but infact was delivered a Slave Battery, which cannot connect directly to the inverter,
wrong size cables, short ones 650mm and most importantly no BMS on Slave, and not the Master Battery size 200 cm long... with BMS attached.
Telephoned the Supplier and told them and filled out their online website Contact Form about the Wrong Battery being delivered and attached file of picture of the outer
cardboard packaging showing the Details of the Slave Battery. Awaiting Reply
Now that I have a 3 month period to install from energy company, No Master Battery on install date as per Application G99 Form A1-2.
Now without a Master Battery, The Big Question is can you still Install, Commission and Test just the Solax X1-AC-3.6kw inverter with the Eastron SDM 230 MID Meter (for limiting Export Control to a Max of 3.68kW (16A) stated by SP Energy in Confirmation email) I will set to 0 Watts for maximum home use. Or has the AC Inverter to be connected to a Battery for the above forms Install, Commissioning and Tests to be Confirmed as Fully Installed as required by SP Energy Confirmation email within 28 days of being installed.
I know that battery is just that, So can you install the inverter alone without a battery.?