Minimum number of batteries for Victron inverter
Minimum number of batteries for Victron inverter
I’m slowly researching my system and would prefer not to put down money for 6 pylontech paired with a Victron MultiPlus 8000 just yet. The link https://www.victronenergy.com/live/batt ... ch_phantom suggests it needs 6 batteries at a minimum but I keep hearing about soft start functionality in the us3000c batteries. Would that mean I can reduce the number required to say 3?
Re: Minimum number of batteries for Victron inverter
The minimum number of batteries is 1.
However the batteries form a “stack” and the “master” reports to the inverter the allowable charge/discharge current. For the US2000 batteries this is 25A per battery. So you are restricted to 1200W per battery. You’d not be getting he most out of your very expensive inverter with 3 batteries and 3600W but if that is what you want to do, go ahead!
However the batteries form a “stack” and the “master” reports to the inverter the allowable charge/discharge current. For the US2000 batteries this is 25A per battery. So you are restricted to 1200W per battery. You’d not be getting he most out of your very expensive inverter with 3 batteries and 3600W but if that is what you want to do, go ahead!
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
6x 2.4kWh Pylontech batteries (14.4kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
6x 2.4kWh Pylontech batteries (14.4kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Re: Minimum number of batteries for Victron inverter
A single us3000c battery isn't enough to soft start a single Sunny Island inverter, it takes 2 goes and the inverter doesn't always like that and has to have the capacitors totally discharged to restart.Andy wrote: ↑Fri Oct 08, 2021 1:32 pm I’m slowly researching my system and would prefer not to put down money for 6 pylontech paired with a Victron MultiPlus 8000 just yet. The link https://www.victronenergy.com/live/batt ... ch_phantom suggests it needs 6 batteries at a minimum but I keep hearing about soft start functionality in the us3000c batteries. Would that mean I can reduce the number required to say 3?
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 135kWh Rolls batteries, 52kWh Growatt storage GBLI 6532, 66kWh Pylontech US3000C, 43kWh DIY, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: Minimum number of batteries for Victron inverter
I'd say 4 of them as a minimum and I would recommend fitting them as 2 x 2 in parallel as in the picture from the link you sent.
Recommended continuous charge / discharge rate is 37A per US3000 battery pack.
That 8000 Victron is similar in spec to my SMA 8.0 Sunny Island which has a max continuous discharge from its battery pack of 140A.
140A / 37A = 3.8 battery packs.
If your going to limit the max continuous output to say 110A / 120A, around 5kW after inefficiencies, you could get away with a single stack of 3.
Recommended continuous charge / discharge rate is 37A per US3000 battery pack.
That 8000 Victron is similar in spec to my SMA 8.0 Sunny Island which has a max continuous discharge from its battery pack of 140A.
140A / 37A = 3.8 battery packs.
If your going to limit the max continuous output to say 110A / 120A, around 5kW after inefficiencies, you could get away with a single stack of 3.
18.7kW PV > 110MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 33MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
Ripple 6.6kW Wind + 4.5kW PV > 33MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3