Ongoing Work at Nowty Towers
Posted: Mon Jun 21, 2021 8:23 pm
(nowtyproject for searching)
Well, as its a new forum, we will have to have a short recap of where I was up to with my battery system.
Over the past few years I was buying up mostly faulty 5kWh lithium Growatt Battery packs from the SP2000 controller range which I believe are no longer manufactured as they are pretty old technology now, compared with the Sofar and Lux, etc. And Growatt seem to have a new unit now, no idea how good the new one is. So unfortunately not many old units seem to come up for sale anymore.
So although each battery unit was somehow faulty with a red light (or no light), I found it was always, very low charge level, or a cell imbalance or the protection board had expired in some way. It was never the actual lithium cells. Even one with practically zero volts came back to life and accepted the correct amount of kWh's charge.
Feb 2018
So I ripped out the cell modules (which were in handy 24V modules) and ran them first with my old 24v Off Grid SMA Sunny Island. No cell balancing seemed necessary as they worked OK for a full season with ALL cells paralleled up with fused links.
April 2018
But then I upgraded to a 48v SMA On Grid Sunny Island with full house backup system with G100 compliant export limitation.
So I had to reconfigure 24v modules into 48v modules by connecting each original 24v pair together with a heavy duty string fuse so each 48v battery pack is from the original 5kWh pack and is individually fused. I ended up buying several more faulty battery packs until I had 10 of them.
But being lazy and reusing the fused links, I only paralleled up every two or 3 cells, hoping that any drift between two or three adjacent cells would be minimal.
April 2019
Occasionally I checked the cells manually for imbalance but there were too many of them to do the job properly and after about a year I had several cells which ran very low. So I had to install some sort of automatic balancing system. Some were quite expensive, others were too small or too complicated. In the end I found some cheap Chinese sourced active balancers which could be cascaded to work with any number of cells and could shift up to 5A from each adjacent cell proportional to the imbalance.
Balancing Board Specification
Operating voltage: 3.0V - 4.2V
Working power drain 15mA
Termination voltage: 2.9V (into under voltage sleep state <1mA)
Maximum Balance current: The Cell difference V / Balance current 0.1V/1A 0.5V/3.5A 1.0V/5.5A
Balance accuracy: < 5mv
No external power supply is required, internal energy in each high cell is transferred to the lower adjacent cell in the pack to balance the entire battery pack.
Front Side
Back Side
Remote Test Point with the Balance Boards - Aug 2020
I split the 1 bank of 10 batteries into 2 banks of 5 batteries, each capable of full 6kW charge / discharge. I connected the balance boards remotely to ONLY the middle battery of each 5 battery banks and relied on the parallel fused links to trickle down the balancing to the other batteries. I added a few more fused links so apart from the middle battery with ALL its cells on the balancer, only each pair cells were paralleled up on the adjacent batteries.
This worked very well indeed but it made me even more lazy to check any imbalance in the cell pairs. After another 6 months or so I was randomly checking the odd cell and found a significant cell imbalance on a pair. Which meant I needed to do a full check on ALL 140 cells.
The battery balancers are on Battery 3 (yellow) on each bank which is connected to all 14 cells.
The bold vertical lines show which cells have the parallel fused interconnects.
The red numbers are pair's of cells which I found as unacceptably imbalanced.
Feb 2021
So my conclusion was I had to parallel up ALL cells, that meant I had to make up another 48 fused leads and install. Well that was back in Feb this year and although I bought the bits and pieces early on, its been on the "TO DO" list until very recently. Finally I've pulled my finger out and made them up and I have now installed them. So now finally, ALL cells are now paralleled up and therefore ALL cells are now connected to the balancing boards.
June 2021
In a week or so I will report back with another full table of cell voltages to see if my full paralleling up of the cells on the balancing boards has worked.
Well, as its a new forum, we will have to have a short recap of where I was up to with my battery system.
Over the past few years I was buying up mostly faulty 5kWh lithium Growatt Battery packs from the SP2000 controller range which I believe are no longer manufactured as they are pretty old technology now, compared with the Sofar and Lux, etc. And Growatt seem to have a new unit now, no idea how good the new one is. So unfortunately not many old units seem to come up for sale anymore.
So although each battery unit was somehow faulty with a red light (or no light), I found it was always, very low charge level, or a cell imbalance or the protection board had expired in some way. It was never the actual lithium cells. Even one with practically zero volts came back to life and accepted the correct amount of kWh's charge.
Feb 2018
So I ripped out the cell modules (which were in handy 24V modules) and ran them first with my old 24v Off Grid SMA Sunny Island. No cell balancing seemed necessary as they worked OK for a full season with ALL cells paralleled up with fused links.
April 2018
But then I upgraded to a 48v SMA On Grid Sunny Island with full house backup system with G100 compliant export limitation.
So I had to reconfigure 24v modules into 48v modules by connecting each original 24v pair together with a heavy duty string fuse so each 48v battery pack is from the original 5kWh pack and is individually fused. I ended up buying several more faulty battery packs until I had 10 of them.
But being lazy and reusing the fused links, I only paralleled up every two or 3 cells, hoping that any drift between two or three adjacent cells would be minimal.
April 2019
Occasionally I checked the cells manually for imbalance but there were too many of them to do the job properly and after about a year I had several cells which ran very low. So I had to install some sort of automatic balancing system. Some were quite expensive, others were too small or too complicated. In the end I found some cheap Chinese sourced active balancers which could be cascaded to work with any number of cells and could shift up to 5A from each adjacent cell proportional to the imbalance.
Balancing Board Specification
Operating voltage: 3.0V - 4.2V
Working power drain 15mA
Termination voltage: 2.9V (into under voltage sleep state <1mA)
Maximum Balance current: The Cell difference V / Balance current 0.1V/1A 0.5V/3.5A 1.0V/5.5A
Balance accuracy: < 5mv
No external power supply is required, internal energy in each high cell is transferred to the lower adjacent cell in the pack to balance the entire battery pack.
Front Side
Back Side
Remote Test Point with the Balance Boards - Aug 2020
I split the 1 bank of 10 batteries into 2 banks of 5 batteries, each capable of full 6kW charge / discharge. I connected the balance boards remotely to ONLY the middle battery of each 5 battery banks and relied on the parallel fused links to trickle down the balancing to the other batteries. I added a few more fused links so apart from the middle battery with ALL its cells on the balancer, only each pair cells were paralleled up on the adjacent batteries.
This worked very well indeed but it made me even more lazy to check any imbalance in the cell pairs. After another 6 months or so I was randomly checking the odd cell and found a significant cell imbalance on a pair. Which meant I needed to do a full check on ALL 140 cells.
The battery balancers are on Battery 3 (yellow) on each bank which is connected to all 14 cells.
The bold vertical lines show which cells have the parallel fused interconnects.
The red numbers are pair's of cells which I found as unacceptably imbalanced.
Feb 2021
So my conclusion was I had to parallel up ALL cells, that meant I had to make up another 48 fused leads and install. Well that was back in Feb this year and although I bought the bits and pieces early on, its been on the "TO DO" list until very recently. Finally I've pulled my finger out and made them up and I have now installed them. So now finally, ALL cells are now paralleled up and therefore ALL cells are now connected to the balancing boards.
June 2021
In a week or so I will report back with another full table of cell voltages to see if my full paralleling up of the cells on the balancing boards has worked.