Central heating
Re: Central heating
I have the same problem occasionally with my Panasonic Aquarea 16kW A2W heat pump running UFH in Portugal.
It would throw either H62 - 'Water switch abnormality' indicating the flow rate is too low, or H12 - 'Indoor/Outdoor capacity unmatched'.
The H12 error is the most annoying - it basically means the unit has been unable to wind down the output capacity enough to maintain the flow temperature. It should have stopped the compressor, but these units are too clever for their own good.
I think the proper solution to all this is that there should be a buffer tank between the heat pump and the UFH. What I did was ensure there was a kitchen radiator always open in the loop, and use the low/normal/boost settings on the app which change the flow temp - 35C / 40C / 45C depending on the time of year.
When I installed a Kensa 25kW GSHP in the UK, I separated it from the UFH with an 800 litre thermal store. The Kensa units are also so simple that they are either on or off - no errors here.
It would throw either H62 - 'Water switch abnormality' indicating the flow rate is too low, or H12 - 'Indoor/Outdoor capacity unmatched'.
The H12 error is the most annoying - it basically means the unit has been unable to wind down the output capacity enough to maintain the flow temperature. It should have stopped the compressor, but these units are too clever for their own good.
I think the proper solution to all this is that there should be a buffer tank between the heat pump and the UFH. What I did was ensure there was a kitchen radiator always open in the loop, and use the low/normal/boost settings on the app which change the flow temp - 35C / 40C / 45C depending on the time of year.
When I installed a Kensa 25kW GSHP in the UK, I separated it from the UFH with an 800 litre thermal store. The Kensa units are also so simple that they are either on or off - no errors here.
-
- Posts: 1873
- Joined: Thu Sep 09, 2021 3:42 pm
- Location: North East Dorset
Re: Central heating
A low loss header is a sort of mini buffer designed specifically to get around this problem, although they were originally designed for use with boilers and multiple circulation pumps. Dead simple, just a fat bit of pipe with two pipe connections at the top and two at the bottom, that's connected inline with the flow and return. This is a good article describing them: https://www.heatgeek.com/low-loss-headers/
The big advantage over a buffer tank is that they don't take up anywhere near as much space.
The big advantage over a buffer tank is that they don't take up anywhere near as much space.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
Re: Central heating
House had crept down to 10 degs in.last few days so had a fair heatsoak to do. Ran most of the SH's while we were on our way home from Glasgow this morning( in front door at 03.30). It had taken the sting off but very glad to run up the WBS this morning. Big lounge where WBS lives is really nice now, over 20 degs and heat shove into rest of house ongoing. WBS storage bricks are up to temp and will keep emitting long into the night while we get the fabric back up to habited space.
It's pulled duty as kettle and also tumbledryer today for that no grid bonus it provides in these solar tightening months.
It's pulled duty as kettle and also tumbledryer today for that no grid bonus it provides in these solar tightening months.
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
-
- Posts: 1873
- Joined: Thu Sep 09, 2021 3:42 pm
- Location: North East Dorset
Re: Central heating
Still no heating at all here, this is the temperature in our hall as of a few minutes ago:
It's still relatively mild outside, too, although getting cooler. It's 11.4°C outside at the moment, but the sky's clear and I think we'll be in for a cooler night tonight.
It's still relatively mild outside, too, although getting cooler. It's 11.4°C outside at the moment, but the sky's clear and I think we'll be in for a cooler night tonight.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
Re: Central heating
You'll be needing that extra heat into the house tonight seeing it's down to 3C already.Joeboy wrote: ↑Thu Nov 03, 2022 4:20 pm House had crept down to 10 degs in.last few days so had a fair heatsoak to do. Ran most of the SH's while we were on our way home from Glasgow this morning( in front door at 03.30). It had taken the sting off but very glad to run up the WBS this morning. Big lounge where WBS lives is really nice now, over 20 degs and heat shove into rest of house ongoing. WBS storage bricks are up to temp and will keep emitting long into the night while we get the fabric back up to habited space.
It's pulled duty as kettle and also tumbledryer today for that no grid bonus it provides in these solar tightening months.
3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
Re: Central heating
I'm in my bed! Time difference and battery install caught up. 3C where's my 30C went?Fintray wrote: ↑Thu Nov 03, 2022 6:49 pmYou'll be needing that extra heat into the house tonight seeing it's down to 3C already.Joeboy wrote: ↑Thu Nov 03, 2022 4:20 pm House had crept down to 10 degs in.last few days so had a fair heatsoak to do. Ran most of the SH's while we were on our way home from Glasgow this morning( in front door at 03.30). It had taken the sting off but very glad to run up the WBS this morning. Big lounge where WBS lives is really nice now, over 20 degs and heat shove into rest of house ongoing. WBS storage bricks are up to temp and will keep emitting long into the night while we get the fabric back up to habited space.
It's pulled duty as kettle and also tumbledryer today for that no grid bonus it provides in these solar tightening months.
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Re: Central heating
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Re: Central heating
3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
Re: Central heating
Trying!
Last edited by Joeboy on Thu Nov 10, 2022 8:20 am, edited 2 times in total.
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
-
- Posts: 1873
- Joined: Thu Sep 09, 2021 3:42 pm
- Location: North East Dorset
Re: Central heating
Temperature in the house dipped down to 21.5°C last night, almost low enough for the heating to come on for the first time. However, today is bright and sunny, so we're getting a fair bit of solar gain, which I hope will delay the heating needing to come on for another day or two. Can't be far off the time when we need to run the heating overnight every now and again, though.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter