Mine was a DIY install, but was a new build, so duct runs were easy, all done before the walls and ceiling were plasterboarded. I got some things right straight off, like mounting the MVHR on anti-vibration mounts to reduce fan noise transmission to the floor it's mounted on, and I got the flow calculations right, so the system wasn't that difficult to balance.ducabi wrote: ↑Thu Dec 01, 2022 2:02 pm That's not sort of help I was hoping for. I thought you would convince me to go with extraction fans
Have you guys done it yourself of used someone for installation/calibration. I'm happy to pay but I don't have any positive experience recently with delegating work I'm afraid, so I guess I would need to do it myself.
Perhaps there is a good online shop doing lots of work to workout what the client needs to supply a proper DIY kit.
The one thing I got wrong was omitting silencers on the MVHR room supply and extract ducts. They made a big difference to the noise level and made the system effectively inaudible unless it's boosting.
Nothing about the installation is at all difficult, easier with two pairs of hands, perhaps, as feeding ducting around on your own can be a bit tiresome. Hardest bit was flow balancing. I used a hot wire anemometer to measure the flow rate, poking it into a bit of 150mm pipe held tight to each ceiling fitting. Balancing was still a lengthy process though. It's very iterative, adjust one fitting a lot and that changes the back pressure and throws all the others out.