Pylontech Batteries

DavB275
Posts: 18
Joined: Fri Jul 09, 2021 7:23 am

Re: Pylontech Batteries

#41

Post by DavB275 »

Thanks everyone. Appreciate all the input.

Yes I'm running 24v system. Had to import these from Italy - none in UK.

Tinbums explanation of the 28.4v is what I believed it to be.

Re. the cable connections - I originally had them connected to top and bottom units of the stack, but it seemed it was the top and bottom units that were giving high voltage alarms first each time. Tried the current config. to see if it made any difference. Effectively I now have + & - to two stacks of three.
Off Grid home
3.5kW PV panels 2kW wind turbine
Solar thermal tubes 2500L thermal store
Perge log boiler
6 x Pylontech batteries
9kVa Lister generator
Tinbum
Posts: 1027
Joined: Mon May 31, 2021 9:55 pm

Re: Pylontech Batteries

#42

Post by Tinbum »

The thing is with the pylontech their are so many different versions and the documentation doesn't always keep up. The 24v have different communication to the inverter depending on age and I have seen different charge voltages in the pylon documentation.

Some docs show 28.2 - 28.5v and others 28.2 -28.8v
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
User avatar
Stinsy
Posts: 2640
Joined: Wed Jun 02, 2021 1:09 pm

Re: Pylontech Batteries

#43

Post by Stinsy »

Tinbum wrote: Sat Sep 25, 2021 7:50 pm The thing is with the pylontech their are so many different versions and the documentation doesn't always keep up. The 24v have different communication to the inverter depending on age and I have seen different charge voltages in the pylon documentation.

Some docs show 28.2 - 28.5v and others 28.2 -28.8v
Either way 28.4V is good to go!
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
User avatar
Joeboy
Posts: 7109
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: Pylontech Batteries

#44

Post by Joeboy »

You were not balanced as you know, please redo your cables too. 1 in 6 out. Keep balancing. Batteries are one of the few representations of Not Just plug & play although appearing to be. All the best, cheers!
16.6kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 11MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
DavB275
Posts: 18
Joined: Fri Jul 09, 2021 7:23 am

Re: Pylontech Batteries

#45

Post by DavB275 »

Joeboy wrote: Sun Sep 26, 2021 12:37 am You were not balanced as you know, please redo your cables too. 1 in 6 out. Keep balancing. Batteries are one of the few representations of Not Just plug & play although appearing to be. All the best, cheers!
Thanks Joeboy. Yes, I intend to re-balance again at some point. Have already re-configured the cables. Now have 1 in, 3 out, and 4 in, 6 out. Both ins and outs feeding from common bus bars, as I read somewhere that it's not good to run a stack of more than 4 from a single set of the Pylontech long cables. Trust this will work ok. All advice is welcome. Cheers. Dave
Off Grid home
3.5kW PV panels 2kW wind turbine
Solar thermal tubes 2500L thermal store
Perge log boiler
6 x Pylontech batteries
9kVa Lister generator
User avatar
Joeboy
Posts: 7109
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: Pylontech Batteries

#46

Post by Joeboy »

DavB275 wrote: Sun Sep 26, 2021 8:50 am
Joeboy wrote: Sun Sep 26, 2021 12:37 am You were not balanced as you know, please redo your cables too. 1 in 6 out. Keep balancing. Batteries are one of the few representations of Not Just plug & play although appearing to be. All the best, cheers!
Thanks Joeboy. Yes, I intend to re-balance again at some point. Have already re-configured the cables. Now have 1 in, 3 out, and 4 in, 6 out. Both ins and outs feeding from common bus bars, as I read somewhere that it's not good to run a stack of more than 4 from a single set of the Pylontech long cables. Trust this will work ok. All advice is welcome. Cheers. Dave
No worries, glad to help. Had not heard about 4+ being an issue? I run 6 US2000's and have not had any problems or even felt heat in the cables. Good to know though.
16.6kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 11MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Tinbum
Posts: 1027
Joined: Mon May 31, 2021 9:55 pm

Re: Pylontech Batteries

#47

Post by Tinbum »

The cables are limited to about 120A so for more than 4 units you should run 2 sets of cables from the pack to the inverter. (I guess it really depends on the max current your going to pull or charge).


Image
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
User avatar
nowty
Posts: 5139
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Pylontech Batteries

#48

Post by nowty »

@DavB275, sorry for not replying to my question about your max charge voltage as I missed it, but I think its all been correctly covered by the reply's from Tinbum and Joeboy.

I first thought 28.4v, thats high for a 24v system !, but as the 48v Pylontechs have 15 cells, the 24v ones must have 8 so when I cross checked on my own tables, 100% on an 8 cell Pylontech would be about 28.3v.

Others have found some low cell alarms when they are first installed, it seems that sometimes, especially if you are using the whole capacity you need to do a few cycles for all the cells to balance up.

For your reference I knocked up this table for an 8 cell Pylontech battery for voltage vs SOC
Image

Cells are damaged if you go above 3.7v per cell so 29.6v with the pack, or below 2.65v per cell or 21.2v with the pack.
15.2kW PV > 100MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 19MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 490 m3
Post Reply