Hi all.
-
- Posts: 14
- Joined: Sun Oct 20, 2024 9:02 pm
Hi all.
Hi all, I am looking for advice on adding a inverter and linking it to a battery in our home.
Not sure what to ask an electrician to quote for and not sure if i will be able to find an electrician who will just supply the feed to the inverter location, or will need to find someone to supply and install the inverter as well. I also not sure if we want to supply the whole house and use the inverter / batteries when the kwh rate is at it highest, or have another circuit setup just for the inverter circuits such as my home office and a couple of new sockets in the kitchen,these will be used for airfryer etc . Looking at G98 certification., I have used victron before but if i go for a 48/5000 that will be a G99. We are in derbyshire.
Not sure what to ask an electrician to quote for and not sure if i will be able to find an electrician who will just supply the feed to the inverter location, or will need to find someone to supply and install the inverter as well. I also not sure if we want to supply the whole house and use the inverter / batteries when the kwh rate is at it highest, or have another circuit setup just for the inverter circuits such as my home office and a couple of new sockets in the kitchen,these will be used for airfryer etc . Looking at G98 certification., I have used victron before but if i go for a 48/5000 that will be a G99. We are in derbyshire.
Re: Hi all.
Hi there, welcome to the forum.
I'm sure you'll get lots of good advice here.
My thoughts as a non-expert are that if you're going to the trouble of fitting an inverter and batteries, it is worth feeding the whole house, and getting enough batteries to meet your usual daily needs, so you can have a cheap rate TOU tariff, eg. Octopus flux, to charge the batteries overnight & then use the stored energy during the day.
If you get the whole system fitted by a company, the whole system is vat free - on the other hand, lots of people on here have bought batteries from China for less and installed themselves.
Also, the mcs certification and g98 approval is easier if done by a registered company.
It's also good to get an idea of options for future expansion too, eg. Solar pv, EV charger, so you don't make life more complicated for your future self.
I know I wished I'd started out asking questiins here before I had my solar & battery system fitted!
I'm sure you'll get lots of good advice here.
My thoughts as a non-expert are that if you're going to the trouble of fitting an inverter and batteries, it is worth feeding the whole house, and getting enough batteries to meet your usual daily needs, so you can have a cheap rate TOU tariff, eg. Octopus flux, to charge the batteries overnight & then use the stored energy during the day.
If you get the whole system fitted by a company, the whole system is vat free - on the other hand, lots of people on here have bought batteries from China for less and installed themselves.
Also, the mcs certification and g98 approval is easier if done by a registered company.
It's also good to get an idea of options for future expansion too, eg. Solar pv, EV charger, so you don't make life more complicated for your future self.
I know I wished I'd started out asking questiins here before I had my solar & battery system fitted!
Solar PV since July '22:
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W
Re: Hi all.
Welcome to the forum Alfie.
I did a similar system to what you are considering with Victron Multiplus and batteries from China, the system runs the whole house.
I did a similar system to what you are considering with Victron Multiplus and batteries from China, the system runs the whole house.
3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
Re: Hi all.
Welcome.
Not much background detail there.
These days all what you require is fitted in one box-inverter,batteries, switch to islanding and charging on TOU (Time of Use) tariff. The Tesla powerwall does this but there is cheaper alternatives i am sure.
Not much background detail there.
These days all what you require is fitted in one box-inverter,batteries, switch to islanding and charging on TOU (Time of Use) tariff. The Tesla powerwall does this but there is cheaper alternatives i am sure.
Re: Hi all.
electric-alfie, I am reading your email as if you don't currently have any Solar PV, are not looking to add any Solar PV and just want a Inverter and battery function to take advantage of TOU tariffs ?
If so, several on here have done just that, but if your thinking of adding some Solar PV in the future then fitting a Hybrid inverter would be advised as they can take either or both Solar PV and Batteries.
If so, several on here have done just that, but if your thinking of adding some Solar PV in the future then fitting a Hybrid inverter would be advised as they can take either or both Solar PV and Batteries.
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
-
- Posts: 14
- Joined: Sun Oct 20, 2024 9:02 pm
Re: Hi all.
Hi all, re the solar, we have a southeast facing rear garden that gets loads of sun, the only issue is the gable end of the house faces in that direction, I have thought about getting a few panels on a pergola facing south. ATM I have a small workshop that face south east and that has 2 400W Perlight All Black Mono Perc Panels, then on my greenhouse I have another 2 of the same, these feed into a victron mppt, then onto a seplos mason battery, it powers my home office during the summer but winter is crap, i picked up a second hand victron pheonix ( no charger ) in a swap. All the cables are sized according to victron and i use a t class fuse before the inverter and mersen dc disconnected between the batteries and theother stuff, its all controlled by a cerbo gx. I aslo have a victron distributor - thats a bit like a big buss bar, this houses the mega fuses for the mppt etc. After living with this stuff for 2 years i honestly dont think that we would have enough solar so i am looking to charge when the kwh rate is low and use that stored power when the rate is higher, on something lile octopus agile. I must admit that i think the victron stuff is vgood, i recently looked at a sunsynch system and it looks much neater, as the mppt etc is all housed in 1 unit
-
- Posts: 2061
- Joined: Wed Jun 02, 2021 6:10 pm
Re: Hi all.
Don't discount roof aspects which don't face south. I have E, S and W but because the first 2 need major work before the pv goes on I hadn't done anything. Then I got fed up waiting/not being in the game and had just the W roof done... I have been delighted by how it has performed and what it has delivered. Fitted this last January, 2.7 megaWatt-hours generated so far and 1.6 exported.
Others here have been pleased with what vertical panels can deliver too...
A
Others here have been pleased with what vertical panels can deliver too...
A
2.0 kW/4.62 MWh pa in Ripples, 4.5 kWp W-facing pv, 9.5 kWh batt
30 solar thermal tubes, 2MWh pa in Stockport, plus Congleton and Kinlochbervie Hydros,
Most travel by bike, walking or bus/train. Veg, fruit - and Bees!
30 solar thermal tubes, 2MWh pa in Stockport, plus Congleton and Kinlochbervie Hydros,
Most travel by bike, walking or bus/train. Veg, fruit - and Bees!
Re: Hi all.
No need for panels to face South! In fact North-facing will generate an economically viable amount of power (about 50% of a similar south-facing array).electric-alfie wrote: ↑Tue Oct 22, 2024 7:34 am Hi all, re the solar, we have a southeast facing rear garden that gets loads of sun, the only issue is the gable end of the house faces in that direction, I have thought about getting a few panels on a pergola facing south. ATM I have a small workshop that face south east and that has 2 400W Perlight All Black Mono Perc Panels, then on my greenhouse I have another 2 of the same, these feed into a victron mppt, then onto a seplos mason battery, it powers my home office during the summer but winter is crap, i picked up a second hand victron pheonix ( no charger ) in a swap. All the cables are sized according to victron and i use a t class fuse before the inverter and mersen dc disconnected between the batteries and theother stuff, its all controlled by a cerbo gx. I aslo have a victron distributor - thats a bit like a big buss bar, this houses the mega fuses for the mppt etc. After living with this stuff for 2 years i honestly dont think that we would have enough solar so i am looking to charge when the kwh rate is low and use that stored power when the rate is higher, on something lile octopus agile. I must admit that i think the victron stuff is vgood, i recently looked at a sunsynch system and it looks much neater, as the mppt etc is all housed in 1 unit
The logic of a north-south ridge precluding solar was rife a couple of decades ago. But is simply isn't true!
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
-
- Posts: 2061
- Joined: Wed Jun 02, 2021 6:10 pm
Re: Hi all.
Definitely!
shows the W-facing pv generating from 8 am onwards,filling the battery through the afternoon and supplying my 3.6kW permitted export until the sun went in, when the battery took over through the rest of the peak period. That month I exported £68 worth, net bill -£38!2.0 kW/4.62 MWh pa in Ripples, 4.5 kWp W-facing pv, 9.5 kWh batt
30 solar thermal tubes, 2MWh pa in Stockport, plus Congleton and Kinlochbervie Hydros,
Most travel by bike, walking or bus/train. Veg, fruit - and Bees!
30 solar thermal tubes, 2MWh pa in Stockport, plus Congleton and Kinlochbervie Hydros,
Most travel by bike, walking or bus/train. Veg, fruit - and Bees!
-
- Posts: 14
- Joined: Sun Oct 20, 2024 9:02 pm
Re: Hi all.
Due to our roof design the west side isnt big enough for more than a couple of panels (we have an extension sticking out of the side) , the eastside is no use as there are conifers that are higher than the roof, that would be the best side as its about 35ft long and it would get the sun from sunrise to about 13.00. The shed does ok, this is my data from victron for past 24hrs, the gable is flat.