generator over voltage

If there is a foul wind a blowin' then drop by for a chat - about coconuts of anything else off topic.
Justme
Posts: 15
Joined: Fri Jul 15, 2022 6:24 am

generator over voltage

#1

Post by Justme »

Currently struggling through a head fog of illness with a 11kw genny that is giving me an over voltage of 333v ac.
Its a single phase unit.
Tried new AVR's all still give same voltage.
Removing avr & output drops to 30v ac.
Tested all joints & windings for shorts & cant find any but dont have a megga to do a high voltage leak test.
My super cheap scope goes crazy & I cant get any sensible readings, but it does read from the inverter fine.

All googling points to over rpm (its not) faulty avr (unlikely 3 are faulty) or loose connections or high resistance which I cant find any.

I just cant find whats up with it.
Westie
Posts: 15
Joined: Fri Jul 23, 2021 8:31 pm

Re: generator over voltage

#2

Post by Westie »

Justme wrote: Sun Jul 31, 2022 1:46 pm Currently struggling through a head fog of illness with a 11kw genny that is giving me an over voltage of 333v ac.
Its a single phase unit.
Tried new AVR's all still give same voltage.
Removing avr & output drops to 30v ac.
Tested all joints & windings for shorts & cant find any but dont have a megga to do a high voltage leak test.
My super cheap scope goes crazy & I cant get any sensible readings, but it does read from the inverter fine.

All googling points to over rpm (its not) faulty avr (unlikely 3 are faulty) or loose connections or high resistance which I cant find any.

I just cant find whats up with it.
Need a bit more info mate, is it brushed or brushless, if brushed how many sliprings 2 or 3?
Tinbum
Posts: 1285
Joined: Mon May 31, 2021 9:55 pm

Re: generator over voltage

#3

Post by Tinbum »

Justme wrote: Sun Jul 31, 2022 1:46 pm All googling points to over rpm
That would just effect frequency.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 135kWh Rolls batteries, 52kWh Growatt storage GBLI 6532, 66kWh Pylontech US3000C, 43kWh DIY, Sofar ME3000's, Brosley wood burner and 250lt DHW
rogeriko
Posts: 30
Joined: Sat Jun 12, 2021 10:57 pm

Re: generator over voltage

#4

Post by rogeriko »

Put a load on it, like an electric heater 2-3kw and then measure it.
newtoallthis
Posts: 26
Joined: Fri Jul 22, 2022 8:10 pm

Re: generator over voltage

#5

Post by newtoallthis »

I am a mere Mechanical Engineer, but from my distant memory I have to ask A=are you measuring RMS voltage or Peak voltage.

RMS x √2 = Peak.

So, if you are measuring 230 V and your meter is set to Peak then it will indicate 325V. 240V would indicate 339V.
Multiplus II 5000VA 48V
4 x Pylontec US3000
3.68 KW AC coupled roof mounted PV
1.38 KW DC coupled roof mounted PV
3.68 KW DC coupled ground mounted PV
4KW Air 2 Air Heat Pump.
billi

Re: generator over voltage

#6

Post by billi »

rogeriko wrote: Sun Jul 31, 2022 9:30 pm Put a load on it, like an electric heater 2-3kw and then measure it.
my first thought , too
Hermit
Posts: 21
Joined: Sat Oct 16, 2021 8:39 am

Re: generator over voltage

#7

Post by Hermit »

Hi Justme, sounds like a dud meter or something to me as you say "it reads OK at the inverter". I am thinking that if the inverter accepts the voltage then it must be OK :?:
Justme
Posts: 15
Joined: Fri Jul 15, 2022 6:24 am

Re: generator over voltage

#8

Post by Justme »

Hermit wrote: Mon Aug 01, 2022 8:26 am Hi Justme, sounds like a dud meter or something to me as you say "it reads OK at the inverter". I am thinking that if the inverter accepts the voltage then it must be OK :?:
When did I say that?
The scope reads inverter fine.
Meter reads inverter fine.
Westie
Posts: 15
Joined: Fri Jul 23, 2021 8:31 pm

Re: generator over voltage

#9

Post by Westie »

newtoallthis wrote: Sun Jul 31, 2022 10:01 pm I am a mere Mechanical Engineer, but from my distant memory I have to ask A=are you measuring RMS voltage or Peak voltage.

RMS x √2 = Peak.

So, if you are measuring 230 V and your meter is set to Peak then it will indicate 325V. 240V would indicate 339V.
Good point, many cheap multimeters have a peak hold function now... Make sure its not peak holding!
Justme
Posts: 15
Joined: Fri Jul 15, 2022 6:24 am

Re: generator over voltage

#10

Post by Justme »

Westie wrote: Sun Jul 31, 2022 7:45 pm
Need a bit more info mate, is it brushed or brushless, if brushed how many sliprings 2 or 3?

Brushless.
Post Reply