The DNO has allowed you option 1 via the G99 fast track process.

Options 2 and 3 fall foul of,

The total aggregate capacity of the Power Generating Modules that are Electricity Storage devices do not exceed 16 A per phase and the total aggregate capacity of the Power Generating Modules that are not Electricity Storage devices do not exceed 16 A per phase.

The awkwardness is the hybrid inverter for option 2 being both an energy storage device and a non energy storage device. So in options 2 and 3 you exceed an aggregate capacity of 16 A per phase in the Power Generating Modules that are not Electricity Storage devices.

Of course what goes on the form and what eventually gets installed might be slightly different. The DNO might even OK a hybrid inverter by you ticking the boxes on the form.

I don't think a hybrid would easily charge from the existing array as they are generally DC coupled devices and some with an ability to charge from the grid but that is usually a timed affair for off peak import.
19.6kW PV > 117MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
User avatar
Joeboy
Posts: 9415
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: How to add batteries & more PV

#22

Post by Joeboy »

Getting too complicated for my wee brain. I'm away in the pool.
Last edited by Joeboy on Mon May 16, 2022 1:00 pm, edited 1 time in total.
17.55kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
Countrypaul
Posts: 663
Joined: Sun Jul 18, 2021 11:50 am

Re: How to add batteries & more PV

#23

Post by Countrypaul »

nowty wrote: Mon May 16, 2022 12:36 pm The DNO has allowed you option 1 via the G99 fast track process.

Options 2 and 3 fall foul of,

The total aggregate capacity of the Power Generating Modules that are Electricity Storage devices do not exceed 16 A per phase and the total aggregate capacity of the Power Generating Modules that are not Electricity Storage devices do not exceed 16 A per phase.

The awkwardness is the hybrid inverter for option 2 being both an energy storage device and a non energy storage device. So in options 2 and 3 you exceed an aggregate capacity of 16 A per phase in the Power Generating Modules that are not Electricity Storage devices.

Of course what goes on the form and what eventually gets installed might be slightly different. The DNO might even OK a hybrid inverter by you ticking the boxes on the form.

I don't think a hybrid would easily charge from the existing array as they are generally DC coupled devices and some with an ability to charge from the grid but that is usually a timed affair for off peak import.
Doesn't The total aggregate capacity of the Power Generating Modules that are Electricity Storage devices do not exceed 16 A per phase apply to the hybrid inverter and the total aggregate capacity of the Power Generating Modules that are not Electricity Storage devices do not exceed 16 A per phase. apply to the FITS system, or am I reading that wrongly?
pudding
Posts: 162
Joined: Sat Mar 26, 2022 7:01 pm
Location: Cornwall

Re: How to add batteries & more PV

#24

Post by pudding »

I don't think a hybrid would easily charge from the existing array as they are generally DC coupled devices and some with an ability to charge from the grid but that is usually a timed affair for off peak import.
That's what I was originally thinking with the hybrid inverters. Obviously it can sense and charge from it own DC connected solar array, but it would need CT clamps or some sensor to tell it when to charge from the AC connection when the other solar array is generating. Like you say, if it can only charge during set times for cheap overnight rates, and not when it detects export from the other solar array, then it's a non-started. Im trying to find a manual for that hybrid to see if it gets installed with a CT clamp to detect export. I suspect not unfortunately.
Last edited by pudding on Mon May 16, 2022 12:47 pm, edited 1 time in total.
4kWp -> Fronius 3.6kW | 3.51kWp & 3.28kWp -> Sunsynk 5kW hybrid | 1.8kWp -> Hoymiles 2000-4t | 2 x 15kWh Seplos DIY batts
8kW GSHP/MVHR/5kW A2A HP/ Ripple- KH & DW & WB :D now :|
User avatar
nowty
Posts: 6534
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: How to add batteries & more PV

#25

Post by nowty »

Countrypaul wrote: Mon May 16, 2022 12:40 pm
nowty wrote: Mon May 16, 2022 12:36 pm The DNO has allowed you option 1 via the G99 fast track process.

Options 2 and 3 fall foul of,

The total aggregate capacity of the Power Generating Modules that are Electricity Storage devices do not exceed 16 A per phase and the total aggregate capacity of the Power Generating Modules that are not Electricity Storage devices do not exceed 16 A per phase.

The awkwardness is the hybrid inverter for option 2 being both an energy storage device and a non energy storage device. So in options 2 and 3 you exceed an aggregate capacity of 16 A per phase in the Power Generating Modules that are not Electricity Storage devices.

Of course what goes on the form and what eventually gets installed might be slightly different. The DNO might even OK a hybrid inverter by you ticking the boxes on the form.

I don't think a hybrid would easily charge from the existing array as they are generally DC coupled devices and some with an ability to charge from the grid but that is usually a timed affair for off peak import.
Doesn't The total aggregate capacity of the Power Generating Modules that are Electricity Storage devices do not exceed 16 A per phase apply to the hybrid inverter and the total aggregate capacity of the Power Generating Modules that are not Electricity Storage devices do not exceed 16 A per phase. apply to the FITS system, or am I reading that wrongly?
It would apply to the hybrid and the original FIT system added together.
19.6kW PV > 117MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
User avatar
nowty
Posts: 6534
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: How to add batteries & more PV

#26

Post by nowty »

Interestingly on the ENA compliant database, the devices we are talking about are either classed as a "Generating Unit" or an "Energy Storage Device".

https://www.ena-eng.org/gen-ttr/

And I cannot find any hybrid types of devices under the class of "Energy Storage Device".
19.6kW PV > 117MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
User avatar
Stinsy
Posts: 3810
Joined: Wed Jun 02, 2021 1:09 pm

Re: How to add batteries & more PV

#27

Post by Stinsy »

Most hybrid inverters use a CT attached to the meter tails to measure current-flow in/out of the house. So if the main array is producing 2kW, the new array 1kW, and the house was using 500W then without any storage there'd be 1500W outflowing to the grid. However the hybrid inverter would target zero flowing out to the grid and would charge the batteries by 1500W irrelevant of which array is actually generating the power.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
6x 2.4kWh Pylontech batteries (14.4kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
pudding
Posts: 162
Joined: Sat Mar 26, 2022 7:01 pm
Location: Cornwall

Re: How to add batteries & more PV

#28

Post by pudding »

Excellent, I hope you're right Stinsy and Nowty not quite (sorry!), as that would make things simpler and easier, just need to check/confirm/arrange how it would work with the DNO if possible. Again it seems illogical if it cant be installed, as if the output of that hybrid inverter is 3.6kW, then it shouldn't matter what batteries or solar PV is connected to it, as it cant output more than that 13A.
4kWp -> Fronius 3.6kW | 3.51kWp & 3.28kWp -> Sunsynk 5kW hybrid | 1.8kWp -> Hoymiles 2000-4t | 2 x 15kWh Seplos DIY batts
8kW GSHP/MVHR/5kW A2A HP/ Ripple- KH & DW & WB :D now :|
User avatar
Stinsy
Posts: 3810
Joined: Wed Jun 02, 2021 1:09 pm

Re: How to add batteries & more PV

#29

Post by Stinsy »

All inverters have an option to limit outflow. You just need to chose an inverter that is "G100 compliant" meaning that the method of limiting outflow complies with UK regulations and it cannot "accidentally" start exporting at full whack.

DNOs are extremely conservative in this respect.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
6x 2.4kWh Pylontech batteries (14.4kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
User avatar
Joeboy
Posts: 9415
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: How to add batteries & more PV

#30

Post by Joeboy »

Stinsy wrote: Mon May 16, 2022 12:56 pm Most hybrid inverters use a CT attached to the meter tails to measure current-flow in/out of the house. So if the main array is producing 2kW, the new array 1kW, and the house was using 500W then without any storage there'd be 1500W outflowing to the grid. However the hybrid inverter would target zero flowing out to the grid and would charge the batteries by 1500W irrelevant of which array is actually generating the power.
This was my understanding too but as I'm 4,000miles from my system didn't want to say. Personally and it is personal I would be trying to drill down into that zero output/max discharge rate for a hybrid inverter while remaining compliant. My one regret is that discharge rate is limited to under 4kW on our hybrid, hence the personal. Also to be clear my knowledge is limited.
17.55kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit