Best PowerPoint skilzzz!!nowty wrote: ↑Wed Aug 17, 2022 9:44 amNice picture.NikoV6 wrote: ↑Wed Aug 17, 2022 6:07 am Thanks everybody for the replies, very helpful!
I should clarify, the AC from the inverter will be going to Tesla gateway.
Interesting about the voltage Nowty, my inverter has three inputs, I think I should reconfigure my panels for three string
https://www.segen.co.uk/product/solis-8 ... e-with-dc/
This is my wiring diagram, thoughts please
Regarding the input for 3 strings, there are only two MPPTs, so if doing 3 strings, the two going into the larger MPPT should be identically sized. I note the installation manual does not specifically say this.
So the panel configuration would need to be something like 8 + 8 / 6 or 7 + 7 / 8 configuration.
Cheers, the question about the strings into the MPPT was on my list!
Do you know if the DNO will be OK with a CT restricting export of the solars?