That's the buckboard power supply professionaly cabletied to a bit of old board. Ran it up, tried the pot, all good.

Decided to check out the top voltage on the Pylontechs.
My batteries slowdown considerably after 88% soc, they can charge there for a long time then go quickly from 88% to 100%. Here's what I found.
88% SOC @ 51.3V
95% SOC @ 52.6V
100% SOC @ 52.9V
The above percentages are as indicated on the Goodwe hybrid inverter, there is lag so pinch of salt please.
Nonetheless, after it indicated 100%SOC the Victron continued to charge as did the grid and the solaredge, all of which I left doing their thing. At 53.3V the Victron shutdown and almost immediately the solaredge power was being exported. The grid charging had been off for about a minute by then as controlled by the Goodwe hybrid inverter.
Did another check after a few minutes and holding at 53.3V
Disconnected the can lead and the main feed leads to the stack and watched it self balance for about 6 minutes then all the Pylontech lights were out. A quick check of the voltage and it had fell back to 52.9V. Hooked it back up, reboot and all fine. I mention the change in voltage seen pre&post balancing to show that it does make a difference and is worth doing. I am choosing to do it on an annual basis even though its a small amount of power being redistributed (to be honest, I just like watching it do its thing).
The main thing I am taking away from this is that my particular Pylontech stack has a peak of 53.3V. Not sure what the rest of you guys top out at?
As each battery unit has 15 individual batteries within it in series I can take the 53.3V seen at 100%SOC and divide in by 15 which gives me a figure to stay below when balancing the new LF280 batteries on their Nov arrival.
3.553V being the figure.
That was fun.