One last question...
What happens if the battery is already above the SOC target when entering the scheduled period?
Does it discharge down to that target, then stop discharging? Or is it just a case of scheduled period = using grid power no matter what?
Is it possible to set the maximum battery charge when charging from grid?
Re: Is it possible to set the maximum battery charge when charging from grid?
10x 405W JA Solar panels (4.05kWp) @ 5 degrees
3x 405W Longi panels (1.22kWp) @ 90 degrees
16.5kWh DIY LifePo4 battery
Solis inverter/charger
0.6kW Ripple WT
64kWh Kia E-Niro
3x 405W Longi panels (1.22kWp) @ 90 degrees
16.5kWh DIY LifePo4 battery
Solis inverter/charger
0.6kW Ripple WT
64kWh Kia E-Niro
Re: Is it possible to set the maximum battery charge when charging from grid?
On my inverter it does nothing.
I set my inverter to charge to 50% in summer however it is usually above this so does nothing.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Re: Is it possible to set the maximum battery charge when charging from grid?
In this situation Victrons neither charge nor discharge during the scheduled period. Many users have said it would be better if there was an option to discharge down to the target level to avoid it using the grid unnecessarily.
But the good news is they automatically use any PV generation there is to supply the loads, any surplus then charges the battery, only when it is full will it export. Which is exactly what most people want, without any programming.
You can also set an SoC floor level which is like a reserve tank for power cuts.
16 x 230W Upsolar panels S Devon, 4kW Steca, 3.9 MWh FITs/yr
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP