Can I use CAT5e or CAT6 cable for a short extension of the RS485 cable from Meter to Inverter?
The included 5m cable with my new Solis inverter needs to be extend by about 8m. The inverters meter has a clamp so must be near the main meter and the inverter is in the loft.
I know RS485 should be screened but on such comparatively short run might it work?
The CAT5e & CAT6 cable I have is unscreened
Also what is considered the best way to physically connect the extension to the supplied cable, it ends in two separate prongs.
I realise most connectors wouldn't let the twist every ? cms to happen.
Strangely the Solis inverter comes with an RJ45 coupler which would allow easy extension of the batteries CAN cable but surely that would be very rare given how difficult extending the DC cable would be!
Use CAT5e or CAT6 cable to Extend RS485 cable from Meter to Inverter?
-
- Posts: 34
- Joined: Mon Sep 12, 2022 12:33 pm
- Location: Sussex coast
Use CAT5e or CAT6 cable to Extend RS485 cable from Meter to Inverter?
15 x JA SOLAR 385W JAM60S20MR (9 facing East 6 facing South)
Solis S5-EH1P6K-L Hybrid Inverter.
4 x Pylontech US3000
Solis S5-EH1P6K-L Hybrid Inverter.
4 x Pylontech US3000
-
- Posts: 1873
- Joined: Thu Sep 09, 2021 3:42 pm
- Location: North East Dorset
Re: Use CAT5e or CAT6 cable to Extend RS485 cable from Meter to Inverter?
Yes, it will be fine out to about 100ft. Just use one of the twisted pairs and ignore the rest, or join all the spares together and use them as a screen. Soldered joints and heatshrink sleeving is the neatest and most robust way to make the joints, I think, but RS485 is pretty tolerant.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
Re: Use CAT5e or CAT6 cable to Extend RS485 cable from Meter to Inverter?
__
Last edited by marshman on Sun Jun 11, 2023 2:12 pm, edited 1 time in total.
Re: Use CAT5e or CAT6 cable to Extend RS485 cable from Meter to Inverter?
Interesting, my Solis came with an Acrel meter that has a RJ45 socket on the bottom. It was easy for me to put the meter in a separate enclosure by the CU, clip the CT around the live trail and then CAT5e back to the garage inverter.
I'm guessing you were supplied with a different meter, perhaps an Eastron unit?
I'm guessing you were supplied with a different meter, perhaps an Eastron unit?
10x 405W JA Solar panels (4.05kWp) @ 5 degrees
3x 405W Longi panels (1.22kWp) @ 90 degrees
16.5kWh DIY LifePo4 battery
Solis inverter/charger
0.6kW Ripple WT
64kWh Kia E-Niro
3x 405W Longi panels (1.22kWp) @ 90 degrees
16.5kWh DIY LifePo4 battery
Solis inverter/charger
0.6kW Ripple WT
64kWh Kia E-Niro
-
- Posts: 34
- Joined: Mon Sep 12, 2022 12:33 pm
- Location: Sussex coast
Re: Use CAT5e or CAT6 cable to Extend RS485 cable from Meter to Inverter?
Yes it is an Estron SDM120CT.
Thanks for all the pointers they all sound good and fairly easy to do.
I have realised there is an alternative: Our power is overhead so I can fit the clamp to the power cable in the loft within 5m of the inverter.
I think clamps are Normally fitted after the meter but I can't see being before a problem.
I do though need to power the meter. There just happens to be a 13Amp socket in the loft any reason why I can't use that?
Fitting a fused spur to that circuit does seem a bit of overkill.
Thanks for all the pointers they all sound good and fairly easy to do.
I have realised there is an alternative: Our power is overhead so I can fit the clamp to the power cable in the loft within 5m of the inverter.
I think clamps are Normally fitted after the meter but I can't see being before a problem.
I do though need to power the meter. There just happens to be a 13Amp socket in the loft any reason why I can't use that?
Fitting a fused spur to that circuit does seem a bit of overkill.
15 x JA SOLAR 385W JAM60S20MR (9 facing East 6 facing South)
Solis S5-EH1P6K-L Hybrid Inverter.
4 x Pylontech US3000
Solis S5-EH1P6K-L Hybrid Inverter.
4 x Pylontech US3000
-
- Posts: 34
- Joined: Mon Sep 12, 2022 12:33 pm
- Location: Sussex coast
Re: Use CAT5e or CAT6 cable to Extend RS485 cable from Meter to Inverter?
Doh! I think I was being stupid about putting the clamp on the power cable in the loft. The cable is combined Live and Neutral and I believe clamps have to be round only the live cable? Is that correct?
15 x JA SOLAR 385W JAM60S20MR (9 facing East 6 facing South)
Solis S5-EH1P6K-L Hybrid Inverter.
4 x Pylontech US3000
Solis S5-EH1P6K-L Hybrid Inverter.
4 x Pylontech US3000
-
- Posts: 1873
- Joined: Thu Sep 09, 2021 3:42 pm
- Location: North East Dorset
Re: Use CAT5e or CAT6 cable to Extend RS485 cable from Meter to Inverter?
Yes, just around the live tail, or the neutral tail (they should both carry exactly the same current, although in different directions).ChrisJEvans wrote: ↑Wed Dec 14, 2022 9:44 am Doh! I think I was being stupid about putting the clamp on the power cable in the loft. The cable is combined Live and Neutral and I believe clamps have to be round only the live cable? Is that correct?
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
-
- Posts: 34
- Joined: Mon Sep 12, 2022 12:33 pm
- Location: Sussex coast
Re: Use CAT5e or CAT6 cable to Extend RS485 cable from Meter to Inverter?
Thanks that makes perfect sense.
15 x JA SOLAR 385W JAM60S20MR (9 facing East 6 facing South)
Solis S5-EH1P6K-L Hybrid Inverter.
4 x Pylontech US3000
Solis S5-EH1P6K-L Hybrid Inverter.
4 x Pylontech US3000