Doubts about attic location for the Pylon batts.

SporranMcDonald
Posts: 57
Joined: Thu Feb 16, 2023 10:29 am
Location: East Hampshire

Doubts about attic location for the Pylon batts.

#1

Post by SporranMcDonald »

Well, in general the PV system is achieving great results - i.e. only using about 1 kWh per week of grid elec. since the install ( 7 weeks ago )

However there is a persistent and sporadic Alarm being reported by the Solis Inverter
BMS 2015 . . . . . described as a "Hint Alarm"
It self-corrects after some variable period of time.
Below is the lower-level error - presumably passed up from the battery . . . . . .
InnerErr.BMS(33293) & Low.Temp.BMS(33293)

I have asked the Installer to notify and get advice from Pylontech. ( I have expectations of a very slow response, )

Anyhow, I have read about various ways of creating a less-hostile environment for the batteries in the loft & remember previously asking the installer if I could locate them in the "electrics corner" in the kitchen. This was dismissed because of "lack of air-flow".

Distance between Inverter and Batts would then need 4 or 5 metres for new cables . . . . . Wha'dya think ?
. . .
230326ElectricsCorner_1.jpg
230326ElectricsCorner_1.jpg (126.91 KiB) Viewed 2070 times
4 kWp Solar PV : 50%/50% SE/SW : Solis Hybrid 3.6 : Pylontec 9.6 kWh
5 kW & 4kW Air-to-Air Mitsubishi Heat Pumps
Ripple : Graig Fatha & Kirk Hill . . . . plus various other renewable projects.
No Car : bicycles : bus & train
Mr Gus
Posts: 3813
Joined: Sun Jun 13, 2021 9:42 pm
Location: Tofu eaters paradise (harrumph)

Re: Doubts about attic location for the Pylon batts.

#2

Post by Mr Gus »

What are the loft temperature highs & lows in your house? (how does that tie in with kits operating parameters? ..any de-rating occurring from gusty winds taking it below regular design limits?
What options to increasing airflow are there now it is already installed (minimising more disruption & cost potential)

Did the installer have much experience with batteries, pylontech especially?

I'm really wary of the extremes lofts can cycle through, dust etc, maintenance & removal / upgrade access every time I hear of it chosen as a site of install.

Whats the problem re airflow in the kitchen he cited? ..didnt want to spend time creating some extra if needed through what look like they could be solid walls?

Have you got a temp sensor up there that transmits the temp to you so you can log when it go's off & what temperatures kick it off?
Is it boarded out & dust free up there? (anything clogged with 100 yrs loft dust) ?

Have you checked solis website error code list?

is "hint" actually High Internal Temp ?
https://usservice.solisinverters.com/su ... lete-list-

Joeboy has his pylons in the garage, so I'm sure can set you at ease there, if only to get a broader perspective.

Is ned yu (pylontech) still around on the victron boards?
1906 ripplewatts @wind Turb-ine-erry
It's the wifes Tesla 3 (she lets me wash it)
Leaf 24
Celotex type insulation stuffed most places
Skip diver to the gentry
Austroflamm WBS
A finger of solar + shed full more
User avatar
Stinsy
Posts: 2947
Joined: Wed Jun 02, 2021 1:09 pm

Re: Doubts about attic location for the Pylon batts.

#3

Post by Stinsy »

1) You have to move the inverter and the batteries. You can't shift just the batteries. Keeping the distance between inverter and batteries as small as possible trumps all other design considerations.

2) The Pylontechs are happy in a wide range of environments. An attic is a perfectly reasonable place for them. If the cell temperature get's below 0℃ then the charge rate will drop. However this is cell temperature not ambient temperature. The cells will be warmer than ambient if they're in use (charging or discharging) and will take a long time to cool down thereafter. Even if the low-temp is triggered they soon warm up while being charged at the lower rate and allow full-rate charging.

3) A far simpler option is to put some insulation around the batteries in winter to help them stay warm.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Tinbum
Posts: 1130
Joined: Mon May 31, 2021 9:55 pm

Re: Doubts about attic location for the Pylon batts.

#4

Post by Tinbum »

Only thing i would say is that kitchens can be humid and a corner like that could be cold so think about condensation.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
AGT
Posts: 1006
Joined: Sat Jan 29, 2022 11:26 am

Re: Doubts about attic location for the Pylon batts.

#5

Post by AGT »

What’s under the floor?
Do you have suspended timber floor with depth?

My long term plan is to do this under my hallway where I have about 1.5m depth, tidy up a bit down there, and have a heater on a frost stat for any chilly days….
User avatar
nowty
Posts: 5887
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Doubts about attic location for the Pylon batts.

#6

Post by nowty »

AGT wrote: Sun Mar 26, 2023 6:31 pm What’s under the floor?
Do you have suspended timber floor with depth?

My long term plan is to do this under my hallway where I have about 1.5m depth, tidy up a bit down there, and have a heater on a frost stat for any chilly days….
Thats where mine are and I have less than 0.5m depth, nicely out of the way and the temperature is very stable, typically 10 degrees in winter and 15 degrees in summer.
Image
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 27MWh generated
6 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Lincs Robert
Posts: 214
Joined: Fri Mar 11, 2022 7:48 pm
Location: Lincolnshire

Re: Doubts about attic location for the Pylon batts.

#7

Post by Lincs Robert »

Mine are in my roof - with the inverter/chargers that drive them. The cables are no longer than 2m each, I could probably shorten them if I really wanted to.

There’s no issue with airflow, but temperature is an issue especially as I went down from a stack of 5 to a stack of 3. If the attic is less than 10c then they charge at a lower rate. This was masked when there were 5. The discharge rate isn’t an issue, but the charge rate is. As we have come out of winter things have improved- but I’ll be adding a 4th battery to the stack when funds permit. I have two stacks of 3, so will need to go to two stacks of 4. Hope that make sense.
bxman

Re: Doubts about attic location for the Pylon batts.

#8

Post by bxman »

I would be more worried about them getting to hot in summer in the loft
As Stinsy says move both inverter and batteries doubt they will overheat the kitchen
Lincs Robert
Posts: 214
Joined: Fri Mar 11, 2022 7:48 pm
Location: Lincolnshire

Re: Doubts about attic location for the Pylon batts.

#9

Post by Lincs Robert »

Mine have been in the roof since 2019 with no problems at all, until I went from 5 x 2 to 3 x 2 batteries & got the cold problem I outlined before …
SporranMcDonald
Posts: 57
Joined: Thu Feb 16, 2023 10:29 am
Location: East Hampshire

Re: Doubts about attic location for the Pylon batts.

#10

Post by SporranMcDonald »

Thanks to all for your contributions. Comments noted. I'll concentrate on this one :-
Stinsy wrote: Sun Mar 26, 2023 5:33 pm 1) You have to move the inverter and the batteries. You can't shift just the batteries. Keeping the distance between inverter and batteries as small as possible trumps all other design considerations.
Thanks : This is the critical info. I'll waste no more time on the "electrics corner" plan.
2) The Pylontechs are happy in a wide range of environments. An attic is a perfectly reasonable place for them. If the cell temperature get's below 0℃ then the charge rate will drop. However this is cell temperature not ambient temperature. The cells will be warmer than ambient if they're in use (charging or discharging) and will take a long time to cool down thereafter. Even if the low-temp is triggered they soon warm up while being charged at the lower rate and allow full-rate charging.
This is important for managing my expectations. { I would prefer my expensive, shiny, new, toy to NOT produce Alarm messages }.
3) A far simpler option is to put some insulation around the batteries in winter to help them stay warm.
Stage 1 :
Methinks I need to get a remote Temperature sensor up in the attic, with a DayHigh & DayLow recording - as a minimum.
Better still if I can store regular, periodic readings in a data store for plotting / analysis.

Stage 2 :
Anticipate possible cooling requirement in summer & a mild heating facility in winter . . . e.g. typical reptile / fish tank controls . . . .
4 kWp Solar PV : 50%/50% SE/SW : Solis Hybrid 3.6 : Pylontec 9.6 kWh
5 kW & 4kW Air-to-Air Mitsubishi Heat Pumps
Ripple : Graig Fatha & Kirk Hill . . . . plus various other renewable projects.
No Car : bicycles : bus & train
Post Reply