Sofar ME3000SP 'Check Charge' cycle
Re: Sofar ME3000SP 'Check Charge' cycle
Welcome to the forum.
3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
10.24kWp PV SolarEdge system
Tesla Powerwall 2
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
-
- Posts: 86
- Joined: Mon Aug 23, 2021 12:31 pm
- Location: Dorset
Re: Sofar ME3000SP 'Check Charge' cycle
I don't have this problem.
I run under control during the four hour Octopus Go period from a Pi but Auto for the remaining time and it works fine without any pauses.
I do have a clamp on my PV feed though and the firmware is 2.something.
I run under control during the four hour Octopus Go period from a Pi but Auto for the remaining time and it works fine without any pauses.
I do have a clamp on my PV feed though and the firmware is 2.something.
65 x Ø58mm SunnPro/Gledhill 450l
Solis Mini 4G 3kW/Sharp ND210/2.94kWp
SB1600/Sharp ND220/1.76kWp
SB1600/Kinve 235/2.115kWp
Dean Forge Croft Clearburn 11kW
SoFar ME3000/Pylontech 42.4kWh
Ecodan 14kW HP
MG4
PVOutput
Solis Mini 4G 3kW/Sharp ND210/2.94kWp
SB1600/Sharp ND220/1.76kWp
SB1600/Kinve 235/2.115kWp
Dean Forge Croft Clearburn 11kW
SoFar ME3000/Pylontech 42.4kWh
Ecodan 14kW HP
MG4
PVOutput
Re: Sofar ME3000SP 'Check Charge' cycle
Well spotted. I can confirm installing the CTpv on a PV circuit stops the 'check charge' cycle. This is something Sofar Technical support failed to disclose! Just installing the CT but not clamping a wire has no effect.MikeHen wrote: ↑Fri Sep 08, 2023 5:09 pm I am in the process of a Sofar ME3000SP install, and I experienced exactly this issue while operating in Auto with only CTa clamp connected. I am using firmware 3.30 (latest as of today).
* Charge 30s (inc. 3s ramp-up)
* Wait 2s
* Standby 2s
* Check charge 2s
* Ramp-up charge ?s..
As soon as I connected the CT PV clamp to my PV inverter the issue disappears. It now charges without any cycling.
I suspect the software is detecting the "export > PV generation" condition as an error condition (even though we all think the PV clamp is only for logging), hence the cycling.
Tested on V3.30.