Sofar me3000sp
Re: Sofar me3000sp
Have you got CAN communication between the battery and the inverter?
Are your inverters set to Pylon batteries in the battery setup?
Are your inverters set to Pylon batteries in the battery setup?
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: Sofar me3000sp
I have no communication between the batteries and the inverters
The battery is set at default battery in the settings not pylon
The battery is set at default battery in the settings not pylon
Re: Sofar me3000sp
Thats probably the problem then. What are your battery settings?
Are you getting red lights on the batteries?
Your much better having communication as it takes care of all that, keeps the soc right, measures the actually battery voltage, and offers much better battery protection and system protection. I'd never not have battery inverter communication.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: Sofar me3000sp
Do you mean 2 batteries on each inverter?
No connection between the two stacks?
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: Sofar me3000sp
I have two sets of 16s lifepo4 batteries on each inverter and a JK B2A24S20P BMS on each pack of 16s
hope this helps
hope this helps
Re: Sofar me3000sp
Ref. “ Have you got CAN communication between the battery and the inverter? “
He has got
32 LiFeP04 3.2volt. 302 Ah cells
Each bank of 16 wired in series.
Both banks wired in parallel feeding the Solar ME300sp.
Each bank has got its own JK B2A24S20P B.M.S. System.
The B.M.S. Systems do not communicate with the ME300sp
He has got
32 LiFeP04 3.2volt. 302 Ah cells
Each bank of 16 wired in series.
Both banks wired in parallel feeding the Solar ME300sp.
Each bank has got its own JK B2A24S20P B.M.S. System.
The B.M.S. Systems do not communicate with the ME300sp
Re: Sofar me3000sp
Somehow I'd got it in my head he was on Pylontech.
I seems very strange that the inverter is seeing a battery over voltage when their is no communication with the battery and the battery bank is separate from the other inverter.
JK now do an active balance BMS that looks to be very good.
(Their is also a gizmo that someone is selling to give CAN communication to the older JK BMS's but he's selling it at an astronomical price, so much so a new BMS is cheaper.)
I seems very strange that the inverter is seeing a battery over voltage when their is no communication with the battery and the battery bank is separate from the other inverter.
JK now do an active balance BMS that looks to be very good.
(Their is also a gizmo that someone is selling to give CAN communication to the older JK BMS's but he's selling it at an astronomical price, so much so a new BMS is cheaper.)
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: Sofar me3000sp
Hi
The BMS units i got have the active balancer in them
is that the bit that balances each of the cells if so i have that
and on the app it gives you a reading of each cell voltage when balanced
The BMS units i got have the active balancer in them
is that the bit that balances each of the cells if so i have that
and on the app it gives you a reading of each cell voltage when balanced
Re: Sofar me3000sp
Do you have any other charging devices for the batteries apart from the Sofar units ?, like any DC charge controllers ?
On the Sofar battery settings, what are the settings for,
max protect voltage ?
max charge voltage ?
full charge voltage ?
You can get this info from the "System Information" page.
On the Sofar battery settings, what are the settings for,
max protect voltage ?
max charge voltage ?
full charge voltage ?
You can get this info from the "System Information" page.
16.9kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 25MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Ripple 6.6kW Wind + 4.5kW PV > 25MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Re: Sofar me3000sp
hi
max protection voltage which i presume is overvoltage protection is 58.5v
max charge voltage is 56.5v
full charge v is 55.0v
hope this helps
max protection voltage which i presume is overvoltage protection is 58.5v
max charge voltage is 56.5v
full charge v is 55.0v
hope this helps