Sofar me3000sp

Tinbum
Posts: 1073
Joined: Mon May 31, 2021 9:55 pm

Re: Sofar me3000sp

#31

Post by Tinbum »

Have you got CAN communication between the battery and the inverter?

Are your inverters set to Pylon batteries in the battery setup?
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
GRUMPY
Posts: 43
Joined: Mon Jun 20, 2022 5:56 pm

Re: Sofar me3000sp

#32

Post by GRUMPY »

I have no communication between the batteries and the inverters
The battery is set at default battery in the settings not pylon
Tinbum
Posts: 1073
Joined: Mon May 31, 2021 9:55 pm

Re: Sofar me3000sp

#33

Post by Tinbum »

GRUMPY wrote: Sun Jan 14, 2024 4:13 am I have no communication between the batteries and the inverters
The battery is set at default battery in the settings not pylon
Thats probably the problem then. What are your battery settings?

Are you getting red lights on the batteries?

Your much better having communication as it takes care of all that, keeps the soc right, measures the actually battery voltage, and offers much better battery protection and system protection. I'd never not have battery inverter communication.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Tinbum
Posts: 1073
Joined: Mon May 31, 2021 9:55 pm

Re: Sofar me3000sp

#34

Post by Tinbum »

GRUMPY wrote: Sat Jan 13, 2024 5:16 pm I have two stacks of batteries on each inverter
Do you mean 2 batteries on each inverter?

No connection between the two stacks?
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
GRUMPY
Posts: 43
Joined: Mon Jun 20, 2022 5:56 pm

Re: Sofar me3000sp

#35

Post by GRUMPY »

I have two sets of 16s lifepo4 batteries on each inverter and a JK B2A24S20P BMS on each pack of 16s
hope this helps
ALAN/ALAN D

Re: Sofar me3000sp

#36

Post by ALAN/ALAN D »

Ref. “ Have you got CAN communication between the battery and the inverter? “

He has got
32 LiFeP04 3.2volt. 302 Ah cells
Each bank of 16 wired in series.
Both banks wired in parallel feeding the Solar ME300sp.
Each bank has got its own JK B2A24S20P B.M.S. System.

The B.M.S. Systems do not communicate with the ME300sp
Tinbum
Posts: 1073
Joined: Mon May 31, 2021 9:55 pm

Re: Sofar me3000sp

#37

Post by Tinbum »

Somehow I'd got it in my head he was on Pylontech. :roll:

I seems very strange that the inverter is seeing a battery over voltage when their is no communication with the battery and the battery bank is separate from the other inverter.

JK now do an active balance BMS that looks to be very good.

(Their is also a gizmo that someone is selling to give CAN communication to the older JK BMS's but he's selling it at an astronomical price, so much so a new BMS is cheaper.)
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
GRUMPY
Posts: 43
Joined: Mon Jun 20, 2022 5:56 pm

Re: Sofar me3000sp

#38

Post by GRUMPY »

Hi
The BMS units i got have the active balancer in them
is that the bit that balances each of the cells if so i have that
and on the app it gives you a reading of each cell voltage when balanced
User avatar
nowty
Posts: 5575
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Sofar me3000sp

#39

Post by nowty »

Do you have any other charging devices for the batteries apart from the Sofar units ?, like any DC charge controllers ?

On the Sofar battery settings, what are the settings for,

max protect voltage ?

max charge voltage ?

full charge voltage ?

You can get this info from the "System Information" page.
16.9kW PV > 107MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 22MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
GRUMPY
Posts: 43
Joined: Mon Jun 20, 2022 5:56 pm

Re: Sofar me3000sp

#40

Post by GRUMPY »

hi
max protection voltage which i presume is overvoltage protection is 58.5v
max charge voltage is 56.5v
full charge v is 55.0v
hope this helps
Post Reply