Monitoring Battery Capacity

cycling_mike
Posts: 25
Joined: Mon Nov 28, 2022 5:50 pm
Location: Wirral

Monitoring Battery Capacity

#1

Post by cycling_mike »

A newbie question so go easy.

So how do you guys (and others) measure the capacity of your batteries. I appreciate the cells lose storage over time but not sure how to measure the current storage capacity of my batteries.

I have a LuxAC3600 invertor and (nominally at least) 9.6kWh of battery storage (3* HanchuEss 3.2kWh units).
I could wait until the batteries fully discharge and see how much power they take in a charging cycle - the Luxpower app tells me this. This seems a bit empirical but I don't see another way.
The app tells me I have battery capacity of 151Ah but this does not seem to relate to the nominal kWh rating in any way that I can see. Am I missing something?

My supplemental is does battery temperature effect storage total capacity or just charging/discharging rate?

Thanks.. :xx:
3.2kW PV, Goodwe invertor
9.6kWh Li batteries, Lux invertor
110kWh Heater storage
Allotment Veg patch
User avatar
Stinsy
Posts: 2850
Joined: Wed Jun 02, 2021 1:09 pm

Re: Monitoring Battery Capacity

#2

Post by Stinsy »

The Ah figure is what the batteries tell Lux over the data connection. Whether this is the same as the marketing goon wrote on the box is for you to figure out!

You might be able to connect a raspberry pi to the batteries and get a SoH figure. You could also use a clamp meter or data from your inverter to guess capacity.

As far as I am able to measure the capacity of my Pylontechs is the same as new and they’re in their 5th year.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
User avatar
Krill
Posts: 387
Joined: Fri Sep 02, 2022 4:38 pm

Re: Monitoring Battery Capacity

#3

Post by Krill »

Given entropy, your proposed method doesn't actually work. The amount of energy in is not the same as the most of energy out.

If I was going to test, I'd disconnect the batteries from a house load and then run a standard 1kW heater and see how long the inverter lasted for (even then you would have to account for the inverter inefficiency but this is reported in the technical specification).

To be clear: I've had my house stack for 9 months now and I have no cloue exactly how much they hold, but this doesn't matter to me. What matters is that I know how long it lasts with general household use.

I'm sure nowty will come along and explain the point that storage capacity and discharge rates are inherently linked due to the electrochemistry (the coler it is, the less power is produced for each part of hte chemical reaction, and "storage capacity" could be defined in terms of the amount of molecules that are yet to react and release energy, but we can't measure for this without destructive testing of hte batteries).
Solar PV: 6.4kW solar PV (Eurener MEPV 400W*16)
PV Inverter: Solis 6kW inverter
Batteries: 14.4kWh LiFePO4 batteries (Pylontech US5000*3)
Battery Inverter: LuxPowertek 3600 ACS*2 battery inverter
WBS: 8kW Hunter Avalon 6 Multifuel burner (wood only)
marshman
Posts: 614
Joined: Thu Jun 17, 2021 7:58 pm

Re: Monitoring Battery Capacity

#4

Post by marshman »

151Ah @ a nominal 50V = 7550Wh or 7.55kWh

Only real way is to "coulomb count" or fully charge and then measure how much energy you can extract when discharging form full charge to your lower limit.
User avatar
AlBargey
Posts: 187
Joined: Mon Oct 11, 2021 8:41 pm

Re: Monitoring Battery Capacity

#5

Post by AlBargey »

Well if each battery is 3.2kWh:

3200Wh / 51.2v = 62.5Ah x 3 batteries = 187.5Ah Total storage capacity 48v to 57.6v

If they're meant to be 187.5Ah and are now 151Ah, you have 36.5Ah missing, or 19.5% reduction in capacity.

What is the discharge limit 48v or 49.6v etc, higher voltage limit would mean a little less capacity.

Are they cycled hard daily, and then kept at 57.6v for extended periods, maybe SOH isn't great? It could just be they are unbalanced and need a decent charge to give them time to balance properly.

I have a Victron SmartShunt, so I can do a discharge test after fully charging and just see how much I can discharge from them over a few hours until the inverter or BMS shut off.

Does the software not show a rough kWh out as well as in if you don't have a shunt?
38m Barge, Solar (10.6 kWp), 26 kWh of LFP, Victron Quattro 8 kVA, CerboGX, 3,500L STP, 57kVa Perkins
Our live data: https://vrm.victronenergy.com/installat ... e/c76c4bf6
User avatar
nowty
Posts: 5792
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Monitoring Battery Capacity

#6

Post by nowty »

Krill wrote: Wed Jan 24, 2024 3:59 pm I'm sure nowty will come along and explain the point that storage capacity and discharge rates are inherently linked due to the electrochemistry (the coler it is, the less power is produced for each part of hte chemical reaction, and "storage capacity" could be defined in terms of the amount of molecules that are yet to react and release energy, but we can't measure for this without destructive testing of hte batteries).
No, I use a spreadsheet and read off the stack voltage. :fight:
if I'm heavily charging / discharging I add or subtract a bit based on my experience.
NOTE - No one else should use these numbers as you won't have a battery bank like mine.
Image

And I have a voltage monitor in my lounge so I can easily see it.
Image
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
User avatar
AlBargey
Posts: 187
Joined: Mon Oct 11, 2021 8:41 pm

Re: Monitoring Battery Capacity

#7

Post by AlBargey »

Just as a side not to Nowty's voltage reference spreadsheet, knowing 100% SOC or the risk of overcharging gets complicated with absorption times and end amps, tail current, termination current, whatever you want to call it. LiFePO4 can be charged to 100% with a charge voltage @ 3.4v per cell or up to 3.65v per cell, depending on the tail current at the end of charge, it just takes longer with a lower absorption voltage and the necessary lower tail current.

Good article here on Lithium charging:

*Edit - broken link

https://nordkyndesign.com/charging-mari ... ery-banks/
Last edited by AlBargey on Wed Jan 24, 2024 6:43 pm, edited 1 time in total.
38m Barge, Solar (10.6 kWp), 26 kWh of LFP, Victron Quattro 8 kVA, CerboGX, 3,500L STP, 57kVa Perkins
Our live data: https://vrm.victronenergy.com/installat ... e/c76c4bf6
cycling_mike
Posts: 25
Joined: Mon Nov 28, 2022 5:50 pm
Location: Wirral

Re: Monitoring Battery Capacity

#8

Post by cycling_mike »

Thanks all

Feel like I am going down a bit of a rabbit hole here, as ever answers come at multiple levels of complexity.

Krill makes a valid point,
Krill wrote: Wed Jan 24, 2024 3:59 pm To be clear: I've had my house stack for 9 months now and I have no cloue exactly how much they hold, but this doesn't matter to me. What matters is that I know how long it lasts with general household use.
My batteries do cover our general household use so why worry. But the apps reporting of Ah did fall from 160Ah to 151Ah some while back and this has got me concerned.
AlBargey wrote: Wed Jan 24, 2024 4:43 pm Well if each battery is 3.2kWh:

3200Wh / 51.2v = 62.5Ah x 3 batteries = 187.5Ah Total storage capacity 48v to 57.6v

If they're meant to be 187.5Ah and are now 151Ah, you have 36.5Ah missing, or 19.5% reduction in capacity.

What is the discharge limit 48v or 49.6v etc, higher voltage limit would mean a little less capacity.
The discharge limit is 40v, that seems OK
AlBargey wrote: Wed Jan 24, 2024 4:43 pm Are they cycled hard daily, and then kept at 57.6v for extended periods, maybe SOH isn't great? It could just be they are unbalanced and need a decent charge to give them time to balance properly.
At this time of year they are cycled each day, a daily charge to 100% at cheap rate, this is consumed over the day to about 10%. In the summer my panels supply all I need so no need so no AC charging.
At the time of writing my three batteries are discharging and showing
SOC 61.1% 52.9v
SOC 62.9% 52.9v
SOC 64.7% 52.9v
do these look in balance?
AlBargey wrote: Wed Jan 24, 2024 4:43 pm Does the software not show a rough kWh out as well as in if you don't have a shunt?
Not that I have spotted.
3.2kW PV, Goodwe invertor
9.6kWh Li batteries, Lux invertor
110kWh Heater storage
Allotment Veg patch
User avatar
Fintray
Posts: 1558
Joined: Mon May 31, 2021 6:37 pm
Location: Aberdeenshire

Re: Monitoring Battery Capacity

#9

Post by Fintray »

AlBargey wrote: Wed Jan 24, 2024 5:09 pm Good article here on Lithium charging:
https://nordkyndesign.com/charging-marine-lithium-battery-banks/
Hi Al, went to look at the article but you have linked back to this thread, think the one you meant is below.
https://nordkyndesign.com/charging-mari ... ery-banks/
3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
User avatar
AlBargey
Posts: 187
Joined: Mon Oct 11, 2021 8:41 pm

Re: Monitoring Battery Capacity

#10

Post by AlBargey »

cycling_mike wrote: Wed Jan 24, 2024 6:23 pm

The discharge limit is 40v, that seems OK
40v = 2.5v per cell - The absolute minimum you should ever take an LFP cell down to, if you can increase to 3v or 3.1v (48-49.6V) your batteries will last longer, there's also very little capacity in that small lower voltage knee.

*Edit - Just to clarify, is that your charge settings or BMS settings - it's fine for the battery BMS but not ideal for charge settings, same for the voltages I mention below.
cycling_mike wrote: Wed Jan 24, 2024 6:23 pm At the time of writing my three batteries are discharging and showing
SOC 61.1% 52.9v
SOC 62.9% 52.9v
SOC 64.7% 52.9v
do these look in balance?
That's just how the batteries are 'balanced' to each other and shows their SOC algorithms accuracy or lack of (But could be a sign of weaker cells in the lower two) , but not how the individual battery cells are balanced to each other in the individual batteries, which you can only see in the upper voltage knee when charging above 3.42v per cell. Can you see cell level readings? What is the deviation in voltage of the cells when they are close or at 100%? It should be less than 30mV difference between the lowest and highest cells if they are well balanced.

If you're leaving 10% SOC then that should be OK, but running them really hard everyday down to 2.5v per cell would definitely lower the SOH more quickly, and if they are also charging up to 2.65v per cell that will also help wear them out more quickly. It seems general consensus for longevity is charging up to 3.45-3.50v per cell with the appropriate tail current, or absorption time to get the same outcome, all assuming they are LFP not NMC, liPO or something else.

If you can log in online or connect to a laptop to get more info somehow, it's probably a good idea.
Last edited by AlBargey on Wed Jan 24, 2024 9:12 pm, edited 3 times in total.
38m Barge, Solar (10.6 kWp), 26 kWh of LFP, Victron Quattro 8 kVA, CerboGX, 3,500L STP, 57kVa Perkins