Mm2

User avatar
Joeboy
Posts: 7916
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Mm2

#1

Post by Joeboy »

Just wondering, hypothetically speaking.. Let's say I had a Jim Cracknell run of cable carrying 240V or so @ 1kW?

What would the V drop (resistance) be going from 1.5mm sq copper to the also off the shelf.2.5mm sq copper conductor? Say over a 20 mtr run?

Is it literally a 40% drop in resistance? Please consider this a teaching moment. I can find it out tomorrow but I thought it would be a nice opportunity for someone to teach the forum?

Cheers
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
AGT
Posts: 923
Joined: Sat Jan 29, 2022 11:26 am

Re: Mm2

#2

Post by AGT »

Download the Megger app, has a nice handy cable calculator all free
Last edited by AGT on Sat Sep 21, 2024 11:27 pm, edited 1 time in total.
AGT
Posts: 923
Joined: Sat Jan 29, 2022 11:26 am

Re: Mm2

#3

Post by AGT »

Image
ecogeorge
Posts: 397
Joined: Sun Oct 31, 2021 7:23 pm
Location: Gloucestershire

Re: Mm2

#4

Post by ecogeorge »

TLC have a good calculator too.....
https://www.tlc-direct.co.uk/Technical/ ... 759dccbd35
1750w Vertical PV micro inverters
3800w almost horizontal/south
Aarrow Becton 7 Woodburner
Dream 3kw ASHP only connected to summer Pool.
Allotment heavy clay.
1.784kw Kirk Hill
0.875kw Derril Water
0.2kwWhitelaw Brae
1kw Harlow Hydro.
resybaby
Posts: 268
Joined: Thu Aug 17, 2023 3:33 pm
Location: Cornwalls North Coast

Re: Mm2

#5

Post by resybaby »

Am i missing something with this?

Have Used both calculators and obtained different answers for similar situation.
One says 1.0mm the other says 1.5mm.

By coincidence the same length/loads as my a2a installation the other day.
I used 2.5mm which i had lying around, knowing it more than capable. at least my cable wont be getting warm then.

Image
4.0kw FIT PV solar Sunnyboy 4000tl & 7 x 570w JA solar panels
7.08kw JA Solar panels & Sunsynk ECCO 3.6kw.
7 x US5000 Pylontechs.
4500l RWH
Full Biomass heating system
iBoost HW divertor
Full house internal walls insulation
600min Loft insulation
User avatar
Joeboy
Posts: 7916
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: Mm2

#6

Post by Joeboy »

resybaby wrote: Mon Sep 23, 2024 12:17 am Am i missing something with this?

Have Used both calculators and obtained different answers for similar situation.
One says 1.0mm the other says 1.5mm.

By coincidence the same length/loads as my a2a installation the other day.
I used 2.5mm which i had lying around, knowing it more than capable. at least my cable wont be getting warm then.

Image
That looks good! Once back from Germany I'll try the Bongo power cable cobbled temporarily together to get power from workshop up to hot tub where the outdoor CU is. Just need to catch one or two pieces of late Autumn sunshine and I'll know from the Ketotek meter if its worth trenching in a cable. I hope so as it would be great to not hit the 253V trip and reset limit on the garage Hoymiles unit from the shove of the Enphase to get the power through..

If I do a suicide lead and remain fully aware I can switch that run on & off while seeing the change on the meter.

Immediate disassembled and back to commando sockets after though.
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Countrypaul
Posts: 535
Joined: Sun Jul 18, 2021 11:50 am

Re: Mm2

#7

Post by Countrypaul »

resybaby wrote: Mon Sep 23, 2024 12:17 am Am i missing something with this?

Have Used both calculators and obtained different answers for similar situation.
One says 1.0mm the other says 1.5mm.

By coincidence the same length/loads as my a2a installation the other day.
I used 2.5mm which i had lying around, knowing it more than capable. at least my cable wont be getting warm then.

Image
I notice one uses SWA and the other uses T&E, if you change the latter to SWA it also coes out with 1.5
AGT
Posts: 923
Joined: Sat Jan 29, 2022 11:26 am

Re: Mm2

#8

Post by AGT »

The online calculators are rough and ready, don’t give all the correction factors for proper design but are handy.
Differ me in cable might be that I picked SWA, clipped direct, the other might default to something else.

Personally I wouldn’t use 1mm2 for external supplies in Swa.
MrPablo
Posts: 272
Joined: Mon Oct 17, 2022 1:26 pm

Re: Mm2

#9

Post by MrPablo »

Agreed, it's nothing but a pain in the arse if future demands require a bigger cable.
Oversized is good, as long as you don't go crazy.
10x 405W JA Solar panels (4.05kWp) @ 5 degrees
3x 405W Longi panels (1.22kWp) @ 90 degrees
16.5kWh DIY LifePo4 battery
Solis inverter/charger
0.6kW Ripple WT
64kWh Kia E-Niro
Oliver90owner
Posts: 385
Joined: Wed Jun 16, 2021 3:48 pm

Re: Mm2

#10

Post by Oliver90owner »

Joeboy,

If I want to check the reality of a result, I compare doubling or halving one or both.

To halve the resistance, one would need to double the cross sectional area, which would double the current carrying ability (and power) at constant voltage.

The analogy would be of having two conductors in parallel, each carrying the same current and delivering the same power. However this may not always quite hold, for calculators/tables, simply because conductors come in standard incremental increases, and the conductor size has to always be rounded up! (ie minus zero, plus to the next higher size).

Also some calculators may not include every possible scenario. Perfect insulation of the conductor would mean the only heat loss could be at the ends, so the temperature at the centre of the run would continue to rise - likely past the maximum permissible (where the resistance will rise and the insulation sheaths will degrade).

So yes, the resistance would fall by 40%. A graph of resistance v cross sectional area is a straight line, so a proportional relationship (double one, halve the other in this case). We have not doubled the cross sectional area so the resistance has been reduced, but not by half.

Imagine three 0.5mm^2 conductors (equivalent to one 1.5mm^2 conductor), each carrying 333W. 5 of those 0.5mm^2 conductors will be able to carry 5*1/3kW = 1 2/3kW = 1.67kW

The relationship between parallel resistors and actual overall resistance is the sum of the reciprocals (whereas for the total of resistors in series is the sum of those resistors).

Without setting out all the Ohm’s Law related maths, increasing the cross sectional area from 1.5mm^2 to 2.5mm^2 conductors is a 67% increase of the former to the latter. The reciprocal of the 1.667 is 0.60 which is 60% of the original - a 40% decrease in resistance.

Someone else could likely explain it better than I can….
Post Reply