cojmh wrote: ↑Mon Oct 28, 2024 8:01 pm
I think I should qualify the above a bit which I will do below just to sense check that we are not overloading the system.
I am always happy to be corrected on things I have got wrong - as you say it is the way to learn - my only caveat is that it is done constructively without being condescending (which to be fair I have almost always found everything on the forum to be respectful and constructive)
Main Consumer Unit
- Shower 1 - 40A - This will be removed next year and I am pretty sure the shower is about 5KW - So this is closer to 22A real world use
- Shower 2 - 40A - This will be removed in a couple of years and I am pretty sure the shower is about 5KW - So this is closer to 22A real world use
- Kitchen/Cooker - 40A - This is probably accurate when we do celebratory meals (Christmas/Easter etc.)
- Outbuilding - 40A - At this point I don't know what I will have in the outbuilding. The plan is to run it as a workshop I don't foresee having more than 3KW (13A) running at the same time. Perhaps I should downsize this?
- PV - 32A - I consider this item to be pretty much zero as it is a generator rather than consumer. I understand there will be a little to keep it running when there is no sun but I think in the context we are assessing it that it will be negligible
- Zappi Charger - 32A - I currently don't have one so this is zero at the moment but will be in this Consumer unit when it is installed (after showers are removed)
- Eddi - 16A - I consider this item to be pretty much zero too as it is only there to consume surplus power from the PV system. Again there will be a little use to stay running when not diverting but again I consider it to be negligible
- AC 1 - 16A - This is a next year install - This is currently not installed and will not be until after showers removed
- AC 2 - 16A - This is an install probably 2-3 years down the line - Same as above
Based on the house at the moment this consumer unit will run 22+22+40 = 84A Maximum (everything on)
Based on where I will end up this consumer unit will run 40+13+32+16+16 = 117A Maximum (everything on)
Switchable Consumer Unit
- Ring Main Downstairs -32A - About the biggest thing we run is the vacuum cleaner ... which is max 2KW or 8.7A
- Ring Main Upstairs -32A - Nothing much upstairs maybe a couple of modern TVs and the hair dryer - so again assumer 2KW or 8.7A
- Ring Main Lofts - 32A - Server Gear up here so maybe 0.8KW or 3.5A
- Outbuilding- 16A - This is mainly to provide lights and CCTV in a power cut - This an estimate at 300W or 1.3A
- Front External Plug 16A - Very little we run outside - maybe the vacuum cleaner for the car or the pressure washer so 2KW or 8.7A
- Solar Thermal - 6A - To be added next year - This is just to run the pump so about 50W which is 0.25A
- Exterior lighting - 6A - I have a total of 6 outside lights (total of 60 Watts) so 0.26A
- Lighting Downstairs - 6A - There are probably 24 light fittings averaging about 5W per fitting - 120W which is 0.5A
- Lighting Upstairs - 6A - There are probably 12 light fittings averaging about 5W per fitting - 60W which is 0.25A
Based on where I will end up this consumer unit will run 32A Maximum (everything on) But this is extremely unlikely
We are currently on an 80A supply and three phase is not an option as I know they would need to run it across the road at high expense.
Whilst everything on will overload the supply - we have never got anywhere close so far.
I suppose the only thing we could do is move to gas for cooking but I think that would be a step backwards
I’ve never heard of a 5kW shower, the lowest I’ve seen are 7.5kW but they’re pretty rare, 9.5kW or 10.5kW are the most common. You’re supposed to go off of the breaker rating prima facie, because you’re supposed to be able to do max demand calcs simply by looking at the CU. You can do further investigations and modify your calculations but you need to have a good answer as to why a 20A device is protected by a 40A breaker it is doubtful that would comply with MIs!
You need to at least provide lip service to the formal method of calculating max demand! You can deviate from that with justification but it needs to be your starting point! What actually is connected to sockets circuits isn’t as relevant as what might be connected by another user. Therefore you need a very good reason if you’re going to deviate from the standard methods and should consider changing the breaker size.
Here goes!
Main Consumer Unit: DB1
- Cooker - 40A -10+9+5=24A (assuming a socket)
- Outbuilding - 40A - DB3 (circuits listed separately)
- PV - 32A - 0A (negligible demand (assuming no battery))
- Zappi - 32A - 0A if installed with wired CT and set to cap max demand
- Eddi - 16A - 0A if installed with wired CT and set up to cap max demand.
DB1 total: 136A
Basically you’re way over already, with two more DBs to consider! Once the showers are removed then DB1 drops to 56A.
Switchable Consumer Unit: DB2
- Downstairs Ring - 32A - 32A
- Upstairs Ring - 32A - 32*0.4=12.8A
- Loft Ring - 32A - 32*0.4=12.8A
- Outbuilding - 16A - 16*0.4=6.4
- Front External Plug -16A -16*0.4=6.4
- Solar Thermal - 6A - 0A (single hardwired device with negligible demand)
- Exterior lighting - 6A - 1A (to cover all lighting circuits)
- Lighting Downstairs - 6A - 0A
- Lighting Upstairs - 6A - 0A
DB2 Total: 71.4A
Outbuilding: DB3
- Sockets Ring - 32A - 32x0.4=12.8A
DB3 Total: 12.8A
GRAND TOTAL: 219.8A
So you’re way WAY over. If you’re taking out the 80A of showers then this drops to 139.8A (only after they’re out!) which is still over. And I’ve rated the 32A EV charging point and the 16A immersion at 0A because I’m assuming they are installed with a compliant method of max demand management. To do this they must be formally certified, have wired CTs, and there must be no method to override the max demand with a “boost” function or similar.
I’m also concerned that the outbuilding has its own DB but there is a circuit within the outbuilding that isn’t controlled by the DB. There needs to be very good signage on the DB and the non-DB3 accessories explaining such. It’d be easy for a future spark to get a shock incorrectly thinking that DB3 isolates the whole outbuilding.
How can you get this down?
What is the actual current draw of the AC units? A typical 3.5kW AC might be rated at 5A.
Does the outbuilding “switchable” circuit need to be 16A can it not be 6A? And you really, really should consider doing away with this. It is loads of added complexity and safety concerns to solve a problem that would be better solved with a UPS.
Does the attic sockets circuit need to be 32A? You could you downrate this to 16A? You could possibly justify, listing the actual devices and explaining that it is unlikely anything else will be powered by this circuit. Particularly if there is only a single double-socket up there and you clearly label it “computer equipment only” or similar.
Maybe you can scrape under the 100A but you really should consider getting a quote for a 3-phase supply.