Ground Source Heat Pump at Nowty Towers

Air source, ground source and associated systems for heating homes
Bugtownboy
Posts: 967
Joined: Tue Jun 01, 2021 12:35 pm

Re: Ground Source Heat Pump at Nowty Towers

#11

Post by Bugtownboy »

Would that be a bit similar to this Joe ;)

User avatar
Joeboy
Posts: 8049
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: Ground Source Heat Pump at Nowty Towers

#12

Post by Joeboy »

Bugtownboy wrote: Sun Nov 28, 2021 12:46 pm Would that be a bit similar to this Joe ;)

That's the puppy! :)
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Bugtownboy
Posts: 967
Joined: Tue Jun 01, 2021 12:35 pm

Re: Ground Source Heat Pump at Nowty Towers

#13

Post by Bugtownboy »

Surf’s up 8-)
User avatar
nowty
Posts: 5754
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Ground Source Heat Pump at Nowty Towers

#14

Post by nowty »

Going off topic, but what the hell eh, :D

Back in the 90's when I did my Skydiving training we used to have a saying, "I love the smell of jet fuel in the morning", just at the time we were queuing up to board the Twin Otter aircraft and stood behind the exhaust of the Turboprop engines. :twisted:

Image

I did nearly 30 jumps and became qualified but gave it up quickly as the stress of leaving the aircraft on the last jump was as bad as the first.

This is my favourite photo of myself and I often look at it if I am having a bad day, "don't worry, as your situation could be much worse".
Image
Last edited by nowty on Mon Jan 03, 2022 5:23 pm, edited 5 times in total.
16.9kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 25MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
User avatar
nowty
Posts: 5754
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Ground Source Heat Pump at Nowty Towers

#15

Post by nowty »

Anyway, back to the boring stuff, :(

The next stage was done before my pressure testing of the cold circuit, sorry to get this out of order but I am going off a collection of my own notes.

The plumbing of the cold circuit (ground loop) included, full bore isolation valves, a small stainless steel expansion vessel, an air bleed valve and filling point with pressure gauge. I made an improvised fitting to connect a simple cheap pressure sprayer to pressure test the cold circuit.

Now I looked up quite a bit of data from various sources about flow rates and pressure drops using different sized pipes. It all gets quite complicated, but the relevant facts I came up with are,

Water velocities in copper pipe (general for heating systems) should be between 0.5 m/s (below which any suspended matter may settle out) and 2 m/s (above which erosion corrosion damage may occur). Also the heat carrying capacity of a pipe is limited by the maximum velocity that can be accepted for noise reasons and this is generally taken as 1.5 m/s. Also a high flow is recommended for ground loops in order to induce as much turbulence as possible to improve the heat transfer.

For a 1.5 m/s flow rate and a 5 degree temp drop, the heat carrying capacity of the main 22mm flow and return pipe is around 10 kW and a flow rate per hour of about 2000 litres per hour, both which exceed the design specs of the heatpump, so looked OK.


Image
16.9kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 25MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
AE-NMidlands
Posts: 2019
Joined: Wed Jun 02, 2021 6:10 pm

Re: Ground Source Heat Pump at Nowty Towers

#16

Post by AE-NMidlands »

Joeboy wrote: Sun Nov 28, 2021 12:29 pm
spread-tee wrote: Sun Nov 28, 2021 9:03 am Fittings are pretty variable in quality that's for sure, personally I solder all copper work,I only use compression if I cant use poly plumb or the pipework wont drain out enough for a solder joint.
Desp
Same here. Love a Yorkshire fitting and the smell of flux in the morning!
A friend convinced me to change to endfeed fittings: he said "If you can do a Yorkshire joint you can do endfeed, save a lot of money and space!"
I did and it has been OK. I was really surprised that when I disassembled one Yorkshire joint the inner end hadn't wetted / soldered the pipe at all, despite me being almost obsessive about cleaning both surfaces.
I have tried the "no need to clean" solder but didn't like it: it cleaned the copper perfectly but I couldn't assemble the joints. I put it down to the metal being so clean that it fused on first contact. I like the lubrication that you get with old-fashioned flux.
A
2.0 kW/4.62 MWh pa in Ripples, 4.5 kWp W-facing pv, 9.5 kWh batt
30 solar thermal tubes, 2MWh pa in Stockport, plus Congleton and Kinlochbervie Hydros,
Most travel by bike, walking or bus/train. Veg, fruit - and Bees!
Oliver90owner
Posts: 395
Joined: Wed Jun 16, 2021 3:48 pm

Re: Ground Source Heat Pump at Nowty Towers

#17

Post by Oliver90owner »

Going off topic, but what the hell eh, :D

It would be better(?) If other comments were posted on a different thread? It would make this most useful thread easier to follow if there were no interruptions to the flow. Personally, I’m very much enjoying the write-up - just not the bits that are ‘diluting’ it.
User avatar
Joeboy
Posts: 8049
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: Ground Source Heat Pump at Nowty Towers

#18

Post by Joeboy »

Oliver90owner wrote: Sun Nov 28, 2021 3:07 pm Going off topic, but what the hell eh, :D

It would be better(?) If other comments were posted on a different thread? It would make this most useful thread easier to follow if there were no interruptions to the flow. Personally, I’m very much enjoying the write-up - just not the bits that are ‘diluting’ it.
What a fun night out you must be pal. :roll:
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
User avatar
nowty
Posts: 5754
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Ground Source Heat Pump at Nowty Towers

#19

Post by nowty »

Then as my heatpump did not come with any built in water pumps, I had to work out what size of water pumps I needed. I found this graph from Yorkshire Pipes,

Image

The effective length of the pipe run was quite difficult to work out because of the different diameters of pipe and the numerous 90 degree bends and of course the heat exchanger in the evaporator also had to be added. Then the graph was for water at 13 degrees with no glycol in it. So after some more calculations I came to a pressure head value of 9 metres.

Well I had already bought a couple of standard 6m head pumps (cos their cheap) before even doing the calculations so had to press on trying them out. I tested it with a single pump and I measured a flow rate of 800 litres per hour. I was about to bite the bullet and purchase a more powerful pump but as I had two of the pumps I tried both in series and the flow rate improved to 1,200 litres per hour so decided to go with that.

I measured the flow rate by pumping from one bucket into another and measuring the time taken to fill the bucket.
Image
16.9kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 25MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
User avatar
nowty
Posts: 5754
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Ground Source Heat Pump at Nowty Towers

#20

Post by nowty »

So the actual testing time came, I connected the cold circuit with two water pumps and a couple of full bore flexible connection hoses and gate valves to the pumps for easy replacement. I filled the cold circuit with a 20% mixture of food grade glycol and pressurised it to around 1 bar. The glycol is required to lower the freezing temp of the liquid but it comes with an operational cost. The specific heat capacity of glycol is less than water and it makes the liquid more viscous, especially at low temperatures, so makes the flow rate drop and the pump work harder.

For experimental purposes, I simply connected the hot circuit with a single water pump running into a 35 litre builders bucket filled with water. I placed a thermometer in the bucket so I could measure the temperature over time and I also measured the power input to the heatpump.

I switched on the unit, first it did a system check, then the cold circuit pumps started up, followed a minute later by the hot circuit pumps. Soon after the compressor started up. Almost instantly the gauges on the exterior of the unit move in opposite directions, the evaporator is getting colder under the partial vacuum as the refrigerant gas boils as it turns from a liquid into a gas and the condenser is getting hotter under higher pressure as the refrigerant gas is compressed and turns from a gas back into a liquid thus giving up its latent heat. The hot water output feels slightly warm, with the cold circuit gets colder with condensation forming on the ground loop pipes.


Test setup
Image


Water temperature is rising
Image


Pressure gauges showing the high pressure condenser (hot) and the low pressure evaporator (cold) temperatures
Image


A constant increase of 2 degrees per minute in the 35 litre builders bucket, from 18 degrees all the way up to 58 degrees in 17 mins when the high temperature tripped out the compressor. I have calculated that equates to a constant 5.7kW of heat output. The electricity consumption gradually increases in line with the compressor pressure, thus reducing the COP value. The ground loop rapidly drops in temperature for the first 5 minutes, then becomes constant.

Image
Last edited by nowty on Sun Dec 05, 2021 3:37 pm, edited 1 time in total.
16.9kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 25MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Post Reply