Re: ASHP & triple glazing

#821

Post by Stinsy »

Joeboy wrote: Mon Jan 13, 2025 5:03 pm
Fintray wrote: Mon Jan 13, 2025 12:43 pm That's a fair bit of work to fill that cavity but you will get the benefit from it for years to come.

You need to get that air in the system sorted out, decide what mode to run the heat pump in, set a heat curve and see what it's like over a longer period. Probably start off with a higher heat curve (don't want Mrs I feeling the cold :fight: ) and take it from there.
Like I said mine is set at inactive, no night setback and the heat curve at 0.4 (was at 0.35 before the cold weather arrived).
Aye on the air. Still not sure it is though. I've dropped the dhw flow rate to 53% for tonight. I'll see what it does. Heat curve currently at 0.45. 0.6 is my freeze goto setting. If the air alarms continue I'll get them back out to bleed.
Have you checked your expansion vessel? If it isn;t pumped up correctly or isn't big enough then when the water in the system warms up it expands and a bit seeps out of the PRV, then when the system cools it sucks a bit of air in through the PRV.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
User avatar
Joeboy
Posts: 8421
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: ASHP & triple glazing

#822

Post by Joeboy »

Stinsy wrote: Mon Jan 13, 2025 5:25 pm
Joeboy wrote: Mon Jan 13, 2025 5:03 pm
Fintray wrote: Mon Jan 13, 2025 12:43 pm That's a fair bit of work to fill that cavity but you will get the benefit from it for years to come.

You need to get that air in the system sorted out, decide what mode to run the heat pump in, set a heat curve and see what it's like over a longer period. Probably start off with a higher heat curve (don't want Mrs I feeling the cold :fight: ) and take it from there.
Like I said mine is set at inactive, no night setback and the heat curve at 0.4 (was at 0.35 before the cold weather arrived).
Aye on the air. Still not sure it is though. I've dropped the dhw flow rate to 53% for tonight. I'll see what it does. Heat curve currently at 0.45. 0.6 is my freeze goto setting. If the air alarms continue I'll get them back out to bleed.
Have you checked your expansion vessel? If it isn;t pumped up correctly or isn't big enough then when the water in the system warms up it expands and a bit seeps out of the PRV, then when the system cools it sucks a bit of air in through the PRV.
Haven't checked that. Tbh, if it keeps throwing data errors I'll get the installers back. It's only the 3rd party monitoring not the HP itself.

The black cold patches are in full retreat.

Before 1
Image

After 1
Image

Before 2
Image

After 2
Image
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
7kW ASHP
200ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit trees
User avatar
Joeboy
Posts: 8421
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: ASHP & triple glazing

#823

Post by Joeboy »

Upcycled the front lounge skirting boards (ogee) via the part solar operated tablesaw to simple boards. All went in well along with some thin insulation sheet to match heights with existing floor.

Image

Image

Temperatures in that room are now absolutely excellent. :) Plastering tomorrow if floor cures ok overnight.

Managed a sub 30kWh day so far. Exporting at the moment too. It's January, right? :twisted:

I like the idea that our 1.5kWh per day saved can be exported. Just another way to ensure that we work from as close to source in our RE as possible. Generated a couple of kWhs too off the PV.

Image

Image
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
7kW ASHP
200ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit trees
User avatar
Joeboy
Posts: 8421
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: ASHP & triple glazing

#824

Post by Joeboy »

Stinsy wrote: Mon Jan 13, 2025 5:25 pm
Joeboy wrote: Mon Jan 13, 2025 5:03 pm
Fintray wrote: Mon Jan 13, 2025 12:43 pm That's a fair bit of work to fill that cavity but you will get the benefit from it for years to come.

You need to get that air in the system sorted out, decide what mode to run the heat pump in, set a heat curve and see what it's like over a longer period. Probably start off with a higher heat curve (don't want Mrs I feeling the cold :fight: ) and take it from there.
Like I said mine is set at inactive, no night setback and the heat curve at 0.4 (was at 0.35 before the cold weather arrived).
Aye on the air. Still not sure it is though. I've dropped the dhw flow rate to 53% for tonight. I'll see what it does. Heat curve currently at 0.45. 0.6 is my freeze goto setting. If the air alarms continue I'll get them back out to bleed.
Have you checked your expansion vessel? If it isn;t pumped up correctly or isn't big enough then when the water in the system warms up it expands and a bit seeps out of the PRV, then when the system cools it sucks a bit of air in through the PRV.
I have asked the question yesterday on errors continuing and also on expansion vessel this morning. :xl:

Looks like hp system is learning, a much steadier temp this morning. Power use overnight lowest seen so far.

Image

Image
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
7kW ASHP
200ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit trees
User avatar
Joeboy
Posts: 8421
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: ASHP & triple glazing

#825

Post by Joeboy »

Strange how things can appear linked. Also as a caveat for buyers of HP's and their ancillary monitor systems.

"I have a level 3 HP monitoring system (order no *****) fitted at my home by Aberdeen Air Source. The system went live on 13th Dec 2024. The system has been bled and all air removed and is fitted with AAV's. We continue to see data error alarms when the dhw cycle is running, although only up to now on the 1.5hr cycle through the night. This morning we had a new wrinkle with data errors showing outside the dhw cycle. I.E, when the home heating was running. Since we woke this morning the COP and heat output values within the OEM software are blank. Energy used is present as is circuit temp.

I am assuming a component failure? I have power cycled the blue box and it has re established comms with my home network. No joy with heat output or cop. I am now running a boost HW cycle and there is a 30 min cop showing of 0.06, that's not right!

I am looking to get this sorted asap but I am aware that this is 3rd party equipment and Aberdeen Air Source are a small growing company with limited personnel and hours in the day. I wanted to raise this fault as early as possible so the system remains in warranty for repair. Where do we go from here?"


So the company who fitted it shouldn't really be on the hook for the repair/replacement? I think they should do the replacement and bill OEM for the hour rate to change it out?

How will OEM respond? Let's wait and find out. :D
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
7kW ASHP
200ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit trees
User avatar
Fintray
Posts: 1655
Joined: Mon May 31, 2021 6:37 pm
Location: Aberdeenshire

Re: ASHP & triple glazing

#826

Post by Fintray »

I'm wondering if a bit of debris has got stuck in the heat meter?

Have you tried asking OEM for advice as they may be able to point you to a solution?
3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
User avatar
Joeboy
Posts: 8421
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: ASHP & triple glazing

#827

Post by Joeboy »

Fintray wrote: Wed Jan 15, 2025 10:40 am I'm wondering if a bit of debris has got stuck in the heat meter?

Have you tried asking OEM for advice as they may be able to point you to a solution?
That thought crossed my mind too. I found a tiny leak on a compression fitting earlier this morning, since topped up circuit. I'll run a Purge cycle then that's me kind of done for end user fault finding. Weirdly the meter kicked in again for cop & heat. We'll see what oem say...

They are cc'd in the mail along with Aberdeen Air Source. To be clear, the HP itself is absolutely fantastic but I feel slightly let down by the set up of the oem gear on install and potential to be caught in the middle for who fixes it. I'll update as we go. Hopefully a Purge and repressurise will get it done. Robbie suggested there might need to be another AAV installed close to the heat meter. I have no doubts it will be resolved but thought to highlight the potential gap between supplier of monitoring gear and installers for those going for an HP.


Image

That set of 3 data errors hours after the dhw cycle this morning is a first.
Image
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
7kW ASHP
200ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit trees
Ronski
Posts: 95
Joined: Mon Feb 20, 2023 9:11 pm
Location: Kent

Re: ASHP & triple glazing

#828

Post by Ronski »

Always a complication with things like this, be interesting to see what OEM come back with.

OEM always throws me, in the motor trade it stands for Original Equipment Manufacturer.
User avatar
Joeboy
Posts: 8421
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: ASHP & triple glazing

#829

Post by Joeboy »

Ronski wrote: Wed Jan 15, 2025 1:13 pm Always a complication with things like this, be interesting to see what OEM come back with.

OEM always throws me, in the motor trade it stands for Original Equipment Manufacturer.
I know, I was a mechanic back the day, pattern.parts and all that. :D

OEM got back to me quickly,


"Looking at your data, I can see the heat meter is having issues reading the flow rate. This is often due to air in the system, but can be caused by a number of issues. Could you send over photos showing the indoor part of the heat pump installation, showing the:
location of heat meter and general pipework layout around the cylinder
Location of the automatic air valves (AAVs), I'm assuming the AAVS are open, little plastic screw is loose on top?
Pressure gauge showing the pressure in the system? This should be between 1-2 bar, keeping the pressure high around 2 bar should help with the air issue
All the best,"
"
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
7kW ASHP
200ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit trees
User avatar
Joeboy
Posts: 8421
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: ASHP & triple glazing

#830

Post by Joeboy »

Regardless of the air in system issue, we are running well. System has been running off PV for 4 hours today (11 to 3).

A combination of good outdoor temps, low flow rates at the HP, the sun being incrementally higher and improved insulation.

I swear that wall work has made a tangible difference to stabilising the house.

Image

Image

Image

Still running in active with heat curve at 0.4.

Image
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
7kW ASHP
200ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
WBSx2