Re: Battery-inverter cables upgrade
Yep.
Think of it like this, assume copper is 9/cm3 and he thinks he has 250 cm3 so 9x250=2250g oe 2.25kg.
However, 25mm2 is 0.25cm2 so 0.25 x 100 = 25cm3, 9 x 25 = 225g
If it does weigh 2.25kg/m where do you get it?
Think of it like this, assume copper is 9/cm3 and he thinks he has 250 cm3 so 9x250=2250g oe 2.25kg.
However, 25mm2 is 0.25cm2 so 0.25 x 100 = 25cm3, 9 x 25 = 225g
If it does weigh 2.25kg/m where do you get it?
Re: Battery-inverter cables upgrade
I think you're right. There are 100mm² in 1cm²...
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Re: Battery-inverter cables upgrade
K.I.S.S.
Re: Battery-inverter cables upgrade
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 30MWh generated
6 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 520 m3
Ripple 6.6kW Wind + 4.5kW PV > 30MWh generated
6 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 520 m3
Re: Battery-inverter cables upgrade
How much does the insulating jacket weigh?
btw that's the "hi-flex" cable Nowty it's 40mm² > 45mm²
Dodgey cable dot com linky
PM me for the "I know what you did last Summer" hotline
Free cable or class action lawsuit; you choose...'Split Charge's' defense was "even the NHS buys it!"
btw that's the "hi-flex" cable Nowty it's 40mm² > 45mm²
Dodgey cable dot com linky
PM me for the "I know what you did last Summer" hotline
Free cable or class action lawsuit; you choose...'Split Charge's' defense was "even the NHS buys it!"
Re: Battery-inverter cables upgrade
I think your right as my 50mm² hydraulic die would not adequately crimp it, I had to use a 35mm² die but not compress all the way.Saladin wrote: ↑Thu Jan 16, 2025 12:31 am How much does the insulating jacket weigh?
btw that's the "hi-flex" cable Nowty it's 40mm² > 45mm²
Dodgey cable dot com linky
PM me for the "I know what you did last Summer" hotline
Free cable or class action lawsuit; you choose...'Split Charge's' defense was "even the NHS buys it!"
However, even 35mm² cable would have been adequate for my upgrade needs anyway.
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 30MWh generated
6 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 520 m3
Ripple 6.6kW Wind + 4.5kW PV > 30MWh generated
6 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 520 m3
Re: Battery-inverter cables upgrade
The gauge being down is one thing but so is the price hence my acceptance of the back-hander. Sure it's dishonest but it's effin' hard to get honest cable or any at all in a red jacket over 50mm², if the price per gram of copper is fair then ignore the numbers and oversize the oversize is my logic.
Easiest way to tell is push 200A through it and see if the voltage drop is consistent with rated for that gauge, length and voltage. After that if the bonnet bee is bothersome have it tested in an independant lab then choose your adventure from there
I'm sure they've covered their bottoms it took me a month to get compensation. When you look at the data sheet the CSA of their 35mm² is 30mm² when you пr² all the strands (but in reality it's less again), the ampacity is at a reduced duty cycle and the jacket gets thinner every year to help the heat dissipation.
I pulled 10 year old hi-flex outtov a boat and it was noticeably more substantial than the "same gauge" new hi-flex I was replacing it with.
In the grand scheme of things the planet's vibrating...we need tuning forks not cables....
Easiest way to tell is push 200A through it and see if the voltage drop is consistent with rated for that gauge, length and voltage. After that if the bonnet bee is bothersome have it tested in an independant lab then choose your adventure from there
I'm sure they've covered their bottoms it took me a month to get compensation. When you look at the data sheet the CSA of their 35mm² is 30mm² when you пr² all the strands (but in reality it's less again), the ampacity is at a reduced duty cycle and the jacket gets thinner every year to help the heat dissipation.
I pulled 10 year old hi-flex outtov a boat and it was noticeably more substantial than the "same gauge" new hi-flex I was replacing it with.
In the grand scheme of things the planet's vibrating...we need tuning forks not cables....
Re: Battery-inverter cables upgrade
Blimey, this has developed. Ok, so I was thinking of this 50mm cable between inverter and disconnect/connector block - https://www.superlecdirect.com/superlec ... -6381ef50/ Anything wrong with it or problem using this flexible cable?
4kW array w/Fronius | 3.51kW & 3.28kW arrays w/Sunsynk 5kW hybrid | 6 x Pylon US3000C
8kW GSHP/MVHR/5kW A2A HP/ Ripple- KH & DW & WB
8kW GSHP/MVHR/5kW A2A HP/ Ripple- KH & DW & WB
Re: Battery-inverter cables upgrade
Why have you chosen H07RN-F? That is for harsh environments such as outdoors, building sites, or marine applications. Sure it'll do the job but it is the wrong tool for a short run between Disconnect and inverter.pudding wrote: ↑Thu Jan 16, 2025 8:25 am Blimey, this has developed. Ok, so I was thinking of this 50mm cable between inverter and disconnect/connector block - https://www.superlecdirect.com/superlec ... -6381ef50/ Anything wrong with it or problem using this flexible cable?
Look for "welding cable".
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)