AGT wrote: ↑Wed May 21, 2025 12:35 pm
It’s 20m away fed from 10mm2 Swa.
Youl'll be looking at c. 3.7V voltage-drop on that SWA. This means when your inverter is exporting at 9.7kW the Voltage at the inverter end will be 3.7V higher than the CU end. So if your grid voltage is borderline but within spec, your inverter will still trip it's over-Voltage protection.
Obviously, there will always be a voltage-drop on any cable. 16mm² SWA would be 2.4V for example and a shorter cable would be proportionally lower.
Some inverters trip off in an overvoltage condition and try again 5-mins later, others dynamically manage their output and throttle to stay within spec.
It is worth checking your grid voltage to see if you have a problem. I have a bazillion devices that record voltage! Eg this is what my hot water tap sees: