Armoured cable for DC
Re: Armoured cable for DC
Now not allowed to use Swa for DC cabling according to new rules as it doesn’t have enough insulation between conductors double /reinforced insulation. Is required
cabling like PV ultra seems to meet the requirements..
https://www.expertelectrical.co.uk/pv-u ... uff-sheath
Just as a wire up a future string with Swa
cabling like PV ultra seems to meet the requirements..
https://www.expertelectrical.co.uk/pv-u ... uff-sheath
Just as a wire up a future string with Swa
Re: Armoured cable for DC
WTF, great, ain't going to stop a spade or similar slicing into a non armoured cable no matter how much insulation it has.
I'll stick to my BS 6724 armoured cables thank you.
Seriously would you prefer an armoured or non armoured ?
New non armoured Sh1t
Nowty Towers BS 6724 armoured SWA
I'll stick to my BS 6724 armoured cables thank you.
Seriously would you prefer an armoured or non armoured ?
New non armoured Sh1t
Nowty Towers BS 6724 armoured SWA
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 27MWh generated
6 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Ripple 6.6kW Wind + 4.5kW PV > 27MWh generated
6 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Re: Armoured cable for DC
Yep in full agreement with you…..
Just cause the Swa manufacturers don’t test the bedding between the cores or something
Just cause the Swa manufacturers don’t test the bedding between the cores or something
Re: Armoured cable for DC
My second PV system has 4 core SWA and never had a problem with it and doubt I will have, 6 years so far so good.
3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!) Now likely to be removed for more PV.
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
Re: Armoured cable for DC
90% of mine is and has been in 10 years. The only bit that isn't is the bit mentioned at the first post.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: Armoured cable for DC
Imagine grandfather rights will apply
Re: Armoured cable for DC
I don’t get it!
If SWA is rated for 1000V DC between cores what possible reason could there be not to use it for a solar array that is probably 400-500V?
If SWA is rated for 1000V DC between cores what possible reason could there be not to use it for a solar array that is probably 400-500V?
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Re: Armoured cable for DC
Here are the actual figures from the BS standard for SWA…
The maximum permitted DC volts between conductors is 1800 Vdc
I’ve worked with plenty of SWA, larger stuff generally and some of the inner insulation is so thin it’s translucent but it all states to comply with BS standards. Mechanically the internal insulation is pretty poor, once in a cableway or machine I’m always wary of the insulation but HO7 for example, comes through the gland fully intact until the termination and is much more robust. Common to have to sleeve SWA internals once exposed. Not really relevant here but still.
The maximum permitted DC volts between conductors is 1800 Vdc
I’ve worked with plenty of SWA, larger stuff generally and some of the inner insulation is so thin it’s translucent but it all states to comply with BS standards. Mechanically the internal insulation is pretty poor, once in a cableway or machine I’m always wary of the insulation but HO7 for example, comes through the gland fully intact until the termination and is much more robust. Common to have to sleeve SWA internals once exposed. Not really relevant here but still.
-
- Posts: 577
- Joined: Sun Jul 18, 2021 11:50 am
Re: Armoured cable for DC
That new cablw is also available in an armoured version: https://www.doncastercables.com/uploads ... sheet_.pdf
Best of both?
Best of both?
Re: Armoured cable for DC
I wonder if this is a case of regulation lagging behind technological advances:
Some of the earlier pv systems used single string inverters which could have >800v on the string. If there have been any failures on those older systems they might have prompted this decision without considering the fact that most modern systems use multiple lower-voltage strings anyway.
Some of the earlier pv systems used single string inverters which could have >800v on the string. If there have been any failures on those older systems they might have prompted this decision without considering the fact that most modern systems use multiple lower-voltage strings anyway.
450W hydro-electric
5110W pv
1.3kw Wt2 - not yet producing
6kWh lead acid - maybe 1kwh useable
LiMnCo battery made from 2nd hand hybrid car modules 3.6kwh nominal 24v.
300lt hot water tank and two storage heaters
ASHP Grant Aerona 3 10.5kw and UFH
5110W pv
1.3kw Wt2 - not yet producing
6kWh lead acid - maybe 1kwh useable
LiMnCo battery made from 2nd hand hybrid car modules 3.6kwh nominal 24v.
300lt hot water tank and two storage heaters
ASHP Grant Aerona 3 10.5kw and UFH