Ring the insulation where you want to remove it for the normal crimp and again closer to the end of the cable half way up.
Remove the rear portion, push the crimp onto cable and it will push insulation back, once crimp is half in remove the second bit of insulation
Remove the rear portion, push the crimp onto cable and it will push insulation back, once crimp is half in remove the second bit of insulation
Re: Solar PV advice
I read that as 6.42mm diameter. Which works out as 32.37mm². Given the cable looks a bit squished then it is deffo 35mm². Problem must be with the lugs!
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
6x 2.4kWh Pylontech batteries (14.4kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
6x 2.4kWh Pylontech batteries (14.4kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Re: Solar PV advice
Is the cable I have 50mm²??? 

Re: Solar PV advice
Get the scales out? Where was that post/thread with some of us weighing cables? 

4kW array w/Fronius | 3.51kW & 3.28kW arrays w/Sunsynk 5kW hybrid | 2 x 15kWh Seplos DIY batts
8kW GSHP/MVHR/5kW A2A HP/ Ripple- KH & DW & WB
8kW GSHP/MVHR/5kW A2A HP/ Ripple- KH & DW & WB

Re: Solar PV advice
1/0 AWG (American Wire Gauge) wire has a cross-sectional area of approximately 53.5 mm².

Why did I think I had 35mm² cable?



Why did I think I had 35mm² cable?