Starting from scratch, new design for grid-tied PV system, 8.5kW panels, 14.5kWh storage, 8kW inverter. G99 Form

sharpener
Posts: 432
Joined: Fri May 20, 2022 10:42 am

Re: Starting from scratch, new design for grid-tied PV system, 8.5kW panels, 14.5kWh storage, 8kW inverter. G99 Form

#21

Post by sharpener »

Krill wrote: Mon May 08, 2023 9:32 pm
Personally I'd have a look at the Sunsynk 3.6kW hybrid inverters, they don't look that expensive and have greater inverting power then the name suggests. It's probably worth considering to just get two (or even three if you really want to be paranoid about ability to not cap total production) installed by a professional and get them to do the paper work, and then connect up additional battery banks and PV arrays as any when needed. That way everything is legit and can be sold on if needed.
Yes, 2 x3.6kW would do it, they would have a combined passthrough of 70A so you could have the whole house on the UPS side leaving just the EV chargers on the grid side. I am assuming @Smallholder has all the circuits accessible in the one place, but some ppl on here have the panels 10s of m from the house or like me a garage across the driveway, now is the time to tell us!

The 8.5 kW of PV makes the inverters a bit over-panelled but by an acceptable amount, there is just enough to supply the 7kW EV charger, and the curtailment at the height of summer is when there will mostly likely be a surplus anyway.

According to the instructions https://cdn.shopify.com/s/files/1/0257/ ... 1672913323 the Sunsynks will work without a battery attached, which prompts the thought of getting a single one installed under MCS and adding the second one and the batteries later.

There doesn't seem to be any setting for export power limit (p 49), it's either ON or OFF. So it's not clear if with a master-slave setup you can set them to be different in order to limit the combined export power to 3.6kW. But you could just forget aboout export.

To comply with UK regs you need to install an external neutral-earth bonding relay but at least there is a signal to drive it (p23. I think the word "not" is missing from the description!)
16 x 230W Upsolar panels S Devon, 4kW Steca, 3.9 MWh FITs/yr
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP
richbee
Posts: 604
Joined: Tue Apr 19, 2022 3:39 pm
Location: Northumberland

Re: Starting from scratch, new design for grid-tied PV system, 8.5kW panels, 14.5kWh storage, 8kW inverter. G99 Form

#22

Post by richbee »

sharpener wrote: Tue May 09, 2023 9:58 am
Krill wrote: Mon May 08, 2023 9:32 pm
Personally I'd have a look at the Sunsynk 3.6kW hybrid inverters, they don't look that expensive and have greater inverting power then the name suggests. It's probably worth considering to just get two (or even three if you really want to be paranoid about ability to not cap total production) installed by a professional and get them to do the paper work, and then connect up additional battery banks and PV arrays as any when needed. That way everything is legit and can be sold on if needed.
Yes, 2 x3.6kW would do it, they would have a combined passthrough of 70A so you could have the whole house on the UPS side leaving just the EV chargers on the grid side. I am assuming @Smallholder has all the circuits accessible in the one place, but some ppl on here have the panels 10s of m from the house or like me a garage across the driveway, now is the time to tell us!

The 8.5 kW of PV makes the inverters a bit over-panelled but by an acceptable amount, there is just enough to supply the 7kW EV charger, and the curtailment at the height of summer is when there will mostly likely be a surplus anyway.

According to the instructions https://cdn.shopify.com/s/files/1/0257/ ... 1672913323 the Sunsynks will work without a battery attached, which prompts the thought of getting a single one installed under MCS and adding the second one and the batteries later.

There doesn't seem to be any setting for export power limit (p 49), it's either ON or OFF. So it's not clear if with a master-slave setup you can set them to be different in order to limit the combined export power to 3.6kW. But you could just forget aboout export.

To comply with UK regs you need to install an external neutral-earth bonding relay but at least there is a signal to drive it (p23. I think the word "not" is missing from the description!)
I have the Sunsynk 3.6kW hybrid inverter - looking at the settings > system mode: you can control the export mode, solar export, and there is a control for 'maximum sell power' (set at 3600W) - which I assume allows you to control the amount of export. I've never tried changing that setting, as there is no need with the 3.6kW version.
Solar PV since July '22:
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W
NikoV6
Posts: 218
Joined: Thu Aug 11, 2022 6:42 am

Re: Starting from scratch, new design for grid-tied PV system, 8.5kW panels, 14.5kWh storage, 8kW inverter. G99 Form

#23

Post by NikoV6 »

I spoke to Scottish Power and they were happy for G98 certification as I limit my export to 3.6kW using Solis G99 and G100 compatible inverter (CT clamp)

Belt and braces, I have subsequently applied G99 in the slim hope that Octopus will eventually cave and allow DNO approval to export suitable for SEG payment.

MCS requirement grips me! :evil: :evil: :evil:
14Kw Mitsubishi Ecodan ASHP
22 x JA Solar 455W Mono Perc Half Cell Silvers
Solis 8.0Kw 5G Dual MPPT Inverter
13.5Kw Tesla Powerwall
Zappi 2 Charger
iBoost