I didn't want to say the other day but you might have blocked the injector with tank debris when it ran dry.
I'd go paperspill (big one), easy start, then both. Then mechanic.

24v x 70A is 1.7 kW allowing for inefficiency it could easily draw significantly more, especially at startup so 2VA might well be somewhat light.
I'd have ordered a recon injector and had the old one serviced and gone on the shelf along with a spare fuel filter. While it's offline I'd dump the fuel tank, inspect internally for rust/scale/sludge then reinstall/replace/clean as required along with new fuel filter and purge all through again before fitting the recon injector. But that's just me. I do respect the offgrid life that relies on gensets for back up. Often wondered the running cost difference between diesel & LPG in the say 10 day per year running scenario?Sunrisemike wrote: ↑Sat Nov 09, 2024 5:00 pm OK, so removed the injector and connected to the fuel line, and no spray. Took it to Asher in Southampton who will test it next week. Meanwhile, i ordered a stand by generator from Amazon. Says 3.8 kw, but when i wired it in to the charger, it trips. It's a Victron Centaur, 24v 70 amp. According to the blogs, 3 kw should charge it.(the Lister is rated at 3). Any ideas? the sockets on the generator are pretty micky mouse, but thought as an emergency generator, should be OK. This is generator number 5 in 23 years. The joy of being off grid! I do have number 1 generator still running, it's a pramac, but 20 years old. This grey cloud is not helping at all!
Mike
![]()