BMS communication issues
Re: BMS communication issues
I completely agree .... assume nothing and test everything!
A bit of an update.
I decided to leave the batteries online (I normally turn them of as I don't like the idea of them being on if I don't know they are working properly)
It would seem they are now willing to discharge - the only problem is that the inverter is discharging them to the grid (which is the opposite of what I want to see!)
So I have now seen that the batteries will discharge, but not correctly (and at the maximum discharge rate which seems to have reset itself to 50A)
I will have to see if I can get hold of the manufacturers.
A bit of an update.
I decided to leave the batteries online (I normally turn them of as I don't like the idea of them being on if I don't know they are working properly)
It would seem they are now willing to discharge - the only problem is that the inverter is discharging them to the grid (which is the opposite of what I want to see!)
So I have now seen that the batteries will discharge, but not correctly (and at the maximum discharge rate which seems to have reset itself to 50A)
I will have to see if I can get hold of the manufacturers.
Re: BMS communication issues
The calibration (i.e the direction) f your grid CT clamp may be wrong.
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Re: BMS communication issues
I didn't realise there was a direction.
It is very possible - just before I installed the batteries, I had a new smart metre installed by British Gas which included a an isolator switch - so I know they had to disconnect the grid clamp and they might have put it back wrong.
I will have a look at that .... is there any directional markings on the clamp?
Thanks,
It is very possible - just before I installed the batteries, I had a new smart metre installed by British Gas which included a an isolator switch - so I know they had to disconnect the grid clamp and they might have put it back wrong.
I will have a look at that .... is there any directional markings on the clamp?
Thanks,
Re: BMS communication issues
There should be.
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Re: BMS communication issues
Can you post a photo?
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Re: BMS communication issues
OK,
I have just had a look and referenced the Solax documentation and it is indeed pointing in the wrong direction. There is an arrow on it that is supposed to point to the public grid .... mine points to the consumer units.
Before I start fiddling with the CT sensor do I need to turn off the power or turn off the inverter?
Or can I simply unclip the CT sensor and clip it back on the correct way around without doing anything to the inverter?
Thanks - I would never have thought to look at that!
I have just had a look and referenced the Solax documentation and it is indeed pointing in the wrong direction. There is an arrow on it that is supposed to point to the public grid .... mine points to the consumer units.
Before I start fiddling with the CT sensor do I need to turn off the power or turn off the inverter?
Or can I simply unclip the CT sensor and clip it back on the correct way around without doing anything to the inverter?
Thanks - I would never have thought to look at that!
Re: BMS communication issues
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Re: BMS communication issues
Unclip.cojmh wrote: ↑Sat Apr 02, 2022 4:06 pm OK,
I have just had a look and referenced the Solax documentation and it is indeed pointing in the wrong direction. There is an arrow on it that is supposed to point to the public grid .... mine points to the consumer units.
Before I start fiddling with the CT sensor do I need to turn off the power or turn off the inverter?
Or can I simply unclip the CT sensor and clip it back on the correct way around without doing anything to the inverter?
Thanks - I would never have thought to look at that!
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Re: BMS communication issues
I sincerely hope it has been a CT clamp and wrongly wired bms lead. Fingers x'd.
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Re: BMS communication issues
Your cable certainly seems ok at the battery end and from what you have said the inverter end looks ok.
I would drop the Voltage down to 53.2v as that is the max the battery will every request. Their are many warnings not to over volt the batteries as it can easily lead to a new bms being needed.
I think you are going to have to go back to Solis and ask them to confirm the pinouts and that their protocol is ok for the USx000C and if not they need to bring a new firmware out.
Have you tried using a different one of your batteries as the master, just to rule out a battery fault?
I would drop the Voltage down to 53.2v as that is the max the battery will every request. Their are many warnings not to over volt the batteries as it can easily lead to a new bms being needed.
I think you are going to have to go back to Solis and ask them to confirm the pinouts and that their protocol is ok for the USx000C and if not they need to bring a new firmware out.
Have you tried using a different one of your batteries as the master, just to rule out a battery fault?
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW