Hello,
Just wondered if you'd sent your form off yet? I'm going through the same right now, and have downloaded the G99 fast track form from here, which appears slightly different to yours? -
https://www.westernpower.co.uk/connecti ... -connected
On that form I've downloaded, there are a couple of tables at the back which I think you can use to define the technology type section you were asking about.
I'm planning on using a similar diagram from the manual for the line diagram for export limitation they ask for. The next section though where they ask:-
Explanation / description of export limitation scheme operation including a description of the fail-safe functionality eg the response of the scheme following failure of a:
• Power monitoring unit
• Control unit
• Power Generating Module interface unit
• Demand control unit
• Communication equipment
Note, fail-safe tests are not required at installations where all Generating Units are EREC G83 or EREC G98 Type Tested, aggregated capacity is not more than 32 A per phase and export capacity is limited to 16 A per phase.
I'm not really sure what they want here? I have G98 and G100 cert for the inverter I want to use, so is that sufficient, or do WPD want actual sentences and descriptions of how the inverter will be fail safe? I saw you added a note saying the 3600ACS is G100 zero export cert, is that sufficient as far as you know? sharpener, if you could shed any light that would be great